Robin,
I did this a while back, but think I remember the essentials.
In the DOE text, remove the zone OA requirement by adding a "$" in front of each "OA-CFM/PER" line for all zones served by the system.
Next, I recall adding a keyword to the system: MIN-OA-FRAC = 1.0 (I think). I think you might want to comment out the MIN-OUTSIDE-AIR keyword in your system as well.
I might not have it exactly right but generally this was the method. It lets your system modulate with VAV boxes and just maintains a 100% OA fraction.
Good luck,
Riley Beise, P.Eng., BEMP, LEED Green Associate
Energy Analyst
AME Consulting Group
721 Johnson Street
Victoria, BC, V8W 1M8
p. 250-382-5999
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of equest-users-request at lists.onebuilding.org
Sent: Thursday, April 18, 2013 1:03 PM
To: equest-users at lists.onebuilding.org
Subject: Equest-users Digest, Vol 61, Issue 17
Send Equest-users mailing list submissions to
equest-users at lists.onebuilding.org
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
or, via email, send a message with subject or body 'help' to
equest-users-request at lists.onebuilding.org
You can reach the person managing the list at
equest-users-owner at lists.onebuilding.org
When replying, please edit your Subject line so it is more specific than "Re: Contents of Equest-users digest..."
More information about the Equest-users
mailing list