[Equest-users] Modeling 62.1 Ventilation Requirements

Paul Diglio paul.diglio at sbcglobal.net
Fri Apr 19 05:19:21 PDT 2013


Folks:

I was looking for a way to write a user-defined expression to calculate the 62.1 
ventilation requirements based on type of area and type of occupancy.
I posted a question to eSimForums.com and Charlie (cgronek) replied with the 
following:


Paul,
You could write a switch statement that  calculates the OA flow based on area 
and occupancy for different  activity descriptions. This would go in the OA-CFM 
entry of the zone:

switch(#LR("SPACE","C-ACTIVITY-DESC"))
case "Offi" : #LR("SPACE","AREA")*0.06+#LR("SPACE","NUMBER-OF-PEOPLE")*5
case "Corr" : #LR("SPACE","AREA")*0.06+#LR("SPACE","NUMBER-OF-PEOPLE")*0
default : no_default
endswitch

This  doesn't take into account anything like distribution efficiency or  system 
ventilation efficiency, so it may not be fully representative of  the ASHRAE 62 
requirements, depending on what system you're modeling. 


Also,  you mention that the number of occupants vary depending on the occupied  
schedule of the area - this is true from a loads standpoint, but will  not have 
any affect on the outside air flow. You'd have to model demand  control 
ventilation (DCV) to account for occupancy variations.

-Charlie
Using this information, I wrote the following expression for a recent project:


In Outdoor Air under Airside HVAC Zone Parameters enter 0 in the Flow per 
Person, the Air Changes and Flow per Area.  Then right click on Airflow, click 
on Edit/View user default.  Choose User-defined default expression and enter 
your expression using the format below.  The length of the input string is 
limited so if you try to enter too many space types an error will occur.  
 
After the CASE enter up to the first 4 characters of the space type as defined 
in the Building Shell/Space Properties Description tab. 

 
The first part of each expression calculates the ventilation requirement based 
on the area.  In the first CASE below, I want .06 CFM/Ft2 for the offices.  The 
second part of the expression calculates the ventilation requirement per 
person.  In the example below, it is 5 CFM per person.
 
The formula needs to be input only once.  You can then select each zone and 
choose the User Default expression by right clicking on the Airflow field as 
described above and the formula will appear.
 
You can also enter the distribution efficiency by dividing the entire expression 
by the applicable efficiency if the expression is not too long.  Or you can 
divide each factor (the .06 and 5 for the first example) by the applicable 
efficiency, which is usually .8 for the type systems I work on and enter .075 
and 6.25 for this example.
 
switch (#LR("SPACE","C-ACTIVITY-DESC"))
    CASE "OFC": #LR("SPACE", "AREA")*.06+#LR("SPACE","NUMBER-OF-PEOPLE")*5
    CASE "FITN": #LR("SPACE", "AREA")*.06+#LR("SPACE","NUMBER-OF-PEOPLE")*20
    CASE "TECH": #LR("SPACE", "AREA")*.12+#LR("SPACE","NUMBER-OF-PEOPLE")*10
    CASE "DAYC": #LR("SPACE", "AREA")*.18+#LR("SPACE","NUMBER-OF-PEOPLE")*10
    CASE "GAME": #LR("SPACE", "AREA")*.18+#LR("SPACE","NUMBER-OF-PEOPLE")*7.5
    CASE "RR": #LR("SPACE", "AREA")*.06+#LR("SPACE","NUMBER-OF-PEOPLE")*5
    CASE "MECH": #LR("SPACE", "AREA")*.06
    CASE "STOR": #LR("SPACE", "AREA")*.12
    CASE "CORR": #LR("SPACE", "AREA")*.06
    CASE "ELEV": #LR("SPACE", "AREA")*.12
    CASE "GYM": #LR("SPACE", "AREA")*.30
default : no_default
   endswitch

 Paul Diglio, CEM, CBCP


87 Fairmont Avenue
New Haven, CT  06513
203-415-0082


www.pdigliollc.com