[Equest-users] Baseline fan curve
Nick Caton
ncaton at smithboucher.com
Tue Apr 2 08:51:58 PDT 2013
Hi Sambhav,
The part-load curve referenced in the last passage of Appendix G (both 2004 and 2007), applies to baseline systems 5 through 8: both VAV and Packaged VAV systems.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sambhav Tiwari
Sent: Tuesday, April 02, 2013 4:26 AM
To: equest-users
Subject: [Equest-users] Baseline fan curve
Dear All,
The fan curve coefficient mentioned in ASHRAE 2004 and 2007 for baseline fan is applicable only for VAV or also for PVAV system.
Regards
Sambhav.