Try this option; In detailed data edit mode, pick that particular zone
under "Air-side HVAC Zone parameters" and slightly increase your "Min
design flow". Normally this will be at 0.5 cfm/sq.ft. This will fix the
unmet hours issue.
Thanks
Gopi
On Wed, Apr 3, 2013 at 3:45 PM, Sambhav Tiwari <tiwari.sambhav at gmail.com>wrote:
> Dear All,
> I am modelling VRV unist as PVVT system but PVVT system is
> giving lot of unmet hours if i change it to PVV system then my unmet hours
> are controlled to the limits so can i go with PVV system for VRV.
>
> Or how can i remove unmet hrs from PVVVT system any suggestions.
>
>
> Thanks