[Equest-users] How to set the COP of a chiller as constant in eQuest?
James Hess
JHess at tmecorp.com
Mon Apr 22 06:13:29 PDT 2013
FYI, email I sent on 4/7/13 at 10:12 PM CST shows how to verify COP is constant.
Thanks!
Regards,
JAH
James A. Hess, PE, CEM, BEMP
Energy Engineer
TME, Inc.
Little Rock, AR
Mobile: (501) 351-4667
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Esmireta
Sent: Sunday, April 21, 2013 11:55 PM
To: Nick Caton
Cc: equest-users at lists.onebuilding.org; Erik Kolderup
Subject: Re: [Equest-users] How to set the COP of a chiller as constant in eQuest?
Dear Nick,
Thanks for your patient instruction!
I now know how to set the COP of a chiller. But I also have two quesions:
1 where to find the meaning of these parameters of the curve? Are them in the DOE help?
2 How to verify that the COP is set as constant from the simulation output file of eQuest?
Thanks!
Esmi
At 2013-04-18 08:34:50,"Nick Caton" <ncaton at smithboucher.com<mailto:ncaton at smithboucher.com>> wrote:
Absolutely, and thanks for correcting me guys!
All: Apologies for just throwing the concept out there without thinking it through totally. Here's a fresh shot at the procedure with a more complete explanation, to make amends and reinforce the lesson for myself. I'm wide open for corrections if I've missed something =):
The typical function for determining a chiller's hourly energy consumption is:
Elechour = Caphour * EIR * EIRf(t1,t2) * EIRf(PLR,dT) / 3413 Btu/Kw
Erik's direction, setting only the 'b' coefficient to 1.0 and the rest to zero, turns EIRf(PLR,dT) into a linear curve that will very simply return the PLR. This reduces the formula to:
Elechour = Caphour * EIR * EIRf(t1,t2) * PLR / 3413 Btu/kW
Following my original direction for coefficients, setting only 'a' to 1.0 and the rest to zero, will turn EIRf(t1,t2) into a curve that will always return 1.0. This reduces the formula to:
Elechour = Caphour * EIR * 1.0 * PLR / 3413 Btu/kW
By their respective definitions in this context (see DOE2 entry below), (Caphour * PLR) equals the Hourly Load, in Btuh. The formula is therefore reduced to:
Elechour = "The Hourly Load (Btuh)" * EIR * / 3413 Btu/kW
So now we are finally utilizing the input EIR every hour, as intended! Interesting to note, one need not even touch the CAPf(t1,t2) curve as its effects are canceled out along the way.
~Nick
PS: ...If all this is looking foreign, here's the DOE2 help entry I'm starting from:
[cid:image001.png at 01CE3F31.43520840]
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Joe Huang
Sent: Wednesday, April 17, 2013 6:56 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] How to set the COP of a chiller as constant in eQuest?
Erik,
You're right. It should be a straight diagonal line from 0,0 to 1,1.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>
www.whiteboxtechnologies.com<http://www.whiteboxtechnologies.com>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 4/17/2013 3:43 PM, Erik Kolderup wrote:
Nick,
One point of correction regarding curves to provide constant COP... I'm pretty sure you do not want the EIR-FPLR curve to be constant 1.0. The value of that curve is actually (normalized EIR)*(part load ratio). So if you want constant EIR, then the curve should just equal PLR. That's a straight line between (0,0) and (1,1). So the "a" coefficient should be zero and the "b" coefficient should be 1.0. All other coefficients for that curve should be zero.
-Erik
Erik Kolderup, PE, LEED AP
erik at kolderupconsulting.com<mailto:erik at kolderupconsulting.com> | 415.531.5198<tel:415.531.5198> | www.kolderupconsulting.com<http://www.kolderupconsulting.com>
---------- Forwarded message ----------
From: Nick Caton <ncaton at smithboucher.com<mailto:ncaton at smithboucher.com>>
To: Joe Huang <yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>>, Esmireta <e2fye2 at 163.com<mailto:e2fye2 at 163.com>>
Cc: "equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>" <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Date: Wed, 17 Apr 2013 19:40:31 +0000
Subject: Re: [Equest-users] How to set the COP of a chiller as constant in eQuest?
After identifying the curves in play per Joe's suggestion, you could achieve a constant COP, independent of part load or other variables, by making a set of custom curves (of appropriate/acceptable type) using coefficient inputs.
Example from the library:
CentH2O-EIR-fPLR&dT looks like this from the library before modification. This curve works alongside others to determine how to modify the input EIR for a chiller:
[cid:image003.png at 01CE3F31.43520840]
What we want is for this and all the other curves to return a value of 1.0, whatever the hourly variables throw at it. Simply enter all coefficients preceding a variable (b,c,d,e,f) to 0. Set the coefficient for the curve's constant (a) at 1.0:
[cid:image004.png at 01CE3F31.43520840]
Doing the same for all associated curves (again, read up in the help/documentation for your particular equipment to be sure), at all hours the chiller in question will operate at the specified EIR without variance.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036<tel:913.344.0036>
fax 913.345.0617<tel:913.345.0617>
www.smithboucher.com<http://www.smithboucher.com>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130422/712e278d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 57602 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130422/712e278d/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130422/712e278d/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 31137 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130422/712e278d/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 29199 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130422/712e278d/attachment-0008.png>
More information about the Equest-users
mailing list