>From the DOE-2 HELP manual:
EXTRACTION RATE
is the cooling extraction rate at design conditions. This is not the value used in the simulation; that value is recalculated hourly and depends on the loads, the conditions, the thermostat type and the thermostat throttling range. ADDITION RATE (heating) is treated similarly.
I interpret this to mean the Addition rate of the heating coil at 70 DegF room teperature (the LOADS based parameter).
John Aulbach, PE
________________________________
From: Paul Diglio <paul.diglio at sbcglobal.net>
To: equest-users at lists.onebuilding.org
Sent: Wednesday, April 24, 2013 1:34 PM
Subject: [Equest-users] SV-A Addition Rate
Folks:
Does anyone know what the SV-A Addition Rate (kbtu/hr) means?
Thank you,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
http://www.pdigliollc.com/