[Equest-users] Big Baseline Boilers - COMBUSTION efficiencies!?
Nick Caton
ncaton at smithboucher.com
Mon Apr 29 08:55:13 PDT 2013
Mike - thanks a bunch for your response!
I can appreciate and relate to your experience with the boiler industry marketing folks... it's very easy to get the run-around, and is often difficult/impossible to get information needed for modeling from product literature. I've come to the same conclusion as you advised, and here's my accounting/reasoning for those interested:
The footnote in 90.1 Table 6.8.1-F defines combustion efficiency as "100% less flue losses," so I that was the basis of this query. There's additionally reference to this procedure: 10 CFR part 431<http://www.ecfr.gov/cgi-bin/text-idx?c=ecfr&tpl=/ecfrbrowse/Title10/10cfr431_main_02.tpl>
That procedure defines combustion and thermal efficiency as follows<http://www.ecfr.gov/cgi-bin/text-idx?c=ecfr&SID=bceba9fa026032bc4b393f9c462988bf&rgn=div8&view=text&node=10:3.0.1.4.19.5.54.2&idno=10>:
Combustion efficiency for a commercial packaged boiler is determined using test procedures prescribed under § 431.86 and is equal to 100 percent minus percent flue loss (percent flue loss is based on input fuel energy)
Thermal efficiency for a commercial packaged boiler is determined using test procedures prescribed under § 431.86 and is the ratio of the heat absorbed by the water or the water and steam to the higher heating value in the fuel burned.
Clearly they're not quite the same thing, where combustion efficiency does not account for jacket/standby/other losses affecting net output.
I haven't seen numbers to verify this, but perhaps ultimately jacket losses are such a small fraction (at these largest capacities) that it's accepted to be irrelevant. Put another way, the actual values for Et and Ec for boilers larger than 2.5MBtuh/h just aren't very different.
Running with that assumption, and unless anyone can answer further to this, I'll treat baseline thermal and combustion efficiencies identically moving forward for large boilers: HIR = 1/Ec = 1/Et. If nothing else, it's a "safe/conservative" approach for LEED, in the sense that if there is an error of procedure here it is only artificially helping the baseline and would in turn prove a beneficial correction for the performance rating down the road.
Thanks again!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Busman, Michael R [mailto:MBusman at chevron.com]
Sent: Friday, April 26, 2013 1:47 PM
To: Nick Caton; equest-users at lists.onebuilding.org
Subject: RE: Big Baseline Boilers - COMBUSTION efficiencies!?
Nick,
It has always been my understanding that combustion efficiency includes flue losses as it is calculated based on CO2% or O2% in the stack gas and net stack temperature (stack temp.-boiler room ambient temp entering the burner). The only other thing I can think of that would affect the thermal efficiency or useful Btu's output as steam or hot water/fuel Btu's input would be radiant and convective jacket losses from the boiler shell at 100% firing rate. Although manufacturers are reluctant to publish data on jacket losses, they could typically range from about 1%-4% based on the design and mfg. This will be a fixed quantity of Btu's no matter what the firing rate is, so this loss as a % of boiler load increases as % load decreases.
As an example, look at an Ajax or Rite Boiler. They look pretty similar and are both manufactured within a fairly close proximity of each other. The front and back ends have uninsulated steel head plates about 1" thick to gain access to the tube bundle. Below the head plates are uninsulated thin sheet metal panels to gain access to the burners. With the boilers firing, I've measured temperatures of the upper plates in the 200-300 deg. range and the lower sheet metal panels in the area of 450 deg. This is kind of an extreme scenario, but the jacket losses are probably a significant number even though the rated or measured combustion efficiency might be 82%.
The other piece of the puzzle when it comes to seasonal boiler efficiency I don't know how DOE-2 handles would be cycling losses. If you take that Rite or Ajax boiler equipped with an atmospheric burner, the seasonal efficiency could easily approach 50%. During every off cycle, boiler room air will flow up through the boiler cooling the firebrick and mass of the boiler. The next firing cycling, those draft cooling losses need to be replaced by additional Btu's. A cycling boiler with a power burner could also have a low seasonal efficiency as the result of cooling losses from pre-purge and post-purge operation to get rid of unburned fuel.
I don't know if that helps or confuses the matter. After that long dissertation, I would suggest using the rated combustion efficiency.
My best,
Mike Busman
Michael R. Busman, CEM
Lead Project Engineer II
Chevron Energy Solutions
A Division of Chevron U.S.A., Inc.
145 S. State College Blvd.
Brea, CA 92821
Direct 714-671-3561
Fax 714-671-3438
eFax 866-420-0335 (Include my Full Name followed by "CAI:MHTZ" on Cover Sheet)
Mobile 310-387-2083
mbusman at chevron.com<mailto:mbusman at chevron.com>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Friday, April 26, 2013 10:55 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Big Baseline Boilers - COMBUSTION efficiencies!?
Hi everyone!
90.1-2007 Table 6.8.1F for boilers prescribes a minimum combustion efficiency (EC) of 82% for gas boilers larger than 2.5MBtu/h. This is the burner's efficiency before flue losses.
The same boiler's thermal efficiency, inclusive of flue losses, would be a lesser figure.
When modeling such boilers for an Appendix G baseline, what is actually appropriate to enter for the boiler's HIR input? As I understand it, this HIR input in eQuest is the inverse of thermal efficiency (net input vs. net output), and would be inclusive of flue losses.
This is for a LEED project, so I'd like to cite something solid to demonstrate what thermal efficiency is appropriate to assume for a baseline boiler of this size. Has anyone gone down this path before?
Thanks!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130429/a8ac80e8/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130429/a8ac80e8/attachment-0002.jpg>
More information about the Equest-users
mailing list