[Equest-users] Non conditioned regularly occupied space

Singh, Arvind Arvind.Singh at dnvkema.com
Fri Aug 30 08:31:55 PDT 2013


Hi Vamshi,

Based on your sqft and fuel size you will have system type and that will be system 6 in your case. Baseline model and proposed both will need heating and cooling system for non-conditioned space. But you can set up high cooling set point for baseline and proposed model to avoid any cooling in the non-conditioned space.

Thanks,
Arvind

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of vamshi ranga
Sent: Friday, August 30, 2013 10:21 AM
To: David Eldridge
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Non conditioned regularly occupied space

Dear David,

The 95,000 ft2 area has only normal ceiling fans.

As I read in ASHRAE 90.1, it says, we shall model HVAC (Cooling or Heating) even if there is NO system proposed. But in this case, VRV system is proposed for 5000 ft2 area, so how shall I proceed with the remaining 95,000 ft2 area?

Thanks,
Vamshi.

On Fri, Aug 30, 2013 at 4:31 PM, David Eldridge <DEldridge at grummanbutkus.com<mailto:DEldridge at grummanbutkus.com>> wrote:
Just to clarify - does the remaining 95,000 ft2 of regularly occupied office have an engineered natural ventilation scheme?

There are some cases where 90.1 asks for cooling systems to be modeled even if none are proposed. You'll need to find out if those conditions apply to you.

DSE Mobile

On Aug 30, 2013, at 4:06 AM, "vamshi ranga" <vamshiranga at gmail.com<mailto:vamshiranga at gmail.com>> wrote:

> Dear All,
>
> We are modeling Non residential building for USGBC New Construction rating, which has regularly occupied (office) area of 100000 sq ft, out of which only 5000 sq ft of the regularly occupied (office) area is conditioned with VRV systems.
>
> Could you please let us know how the conditioned area shall be considered in Baseline and Proposed case. my doubts is,
>
> Shall this be modeled with 5000 sq ft  conditioned area in both Base and Proposed or Is there any minimum requirement for percentage conditioned area?
>
> Thanks,
> Vamshi.
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130830/ee3ce9b9/attachment-0001.htm>


More information about the Equest-users mailing list