[Equest-users] Question: Modeling Specific Chillers
Sunil Nair
energymodel.sunil at gmail.com
Thu Aug 15 21:40:06 PDT 2013
Dave and Mike,
Thanks for your inputs.
Mike,
Yes, I am referring to the multistage chiller where the liquid is flashed
to the inlet of the second stage impeller. As you have mentioned this
process is internal to the chiller.
My thought initially was I may have to model multiple compressors per
circuit for a chiller without VFD. I did not find this option in eQUEST. As
I think about it now, my case would be quite different from having multiple
compressors per circuit.
I am in the process of obtaining data points for the chiller from the
manufacturer so I can input the data points into eQUEST.
I'll keep this thread updated.
Sincerely,
Sunil Nair
*Ab Initio*
TMA House, Plot No. 6, 2nd Floor,
Main Road, Wagle Industrial Area,
Thane (West) - 400 604
Ph: +91-22 - 3243 7023
Cell: +91-8879595123
web: www.abinitio.co.in
On Wed, Aug 14, 2013 at 10:56 PM, Busman, Michael R <MBusman at chevron.com>wrote:
> Sunil,****
>
> ** **
>
> My understanding of an economizer for a multi-stage centrifugal is that
> some of the liquid refrigerant flashes as it passes through the expansion
> device. This flash gas, I believe is introduced to the input side of the
> second stage impeller. Since the economizer is internal to the chiller,
> one set of curves should be sufficient as there is only one mode of
> operation as I understand it. You didn’t specify, so I’m assuming you are
> not referring to a water-side economizer.****
>
> ** **
>
> I haven’t custom defined a chiller yet in eQUEST, however, it appears that
> several performance data points from the manufacturer are required for
> eQUEST to generate the curves if you select this method. The other is to
> generate your own curves. Many years ago when I used to work in VisualDOE,
> I found the calculation methodology to define chiller curves from the
> Pacific Gas & Electric web site, which I used to set up a spreadsheet to
> calculate the curve coefficients. This was originally set up for constant
> speed chillers. A number of months ago I added a spreadsheet tab to handle
> variable speed chillers. To create the 3 sets of curve coefficients, at
> least 10 full load data points at different chilled and condenser water
> temperatures were required from the manufacturer in order to map the
> compressor. There was no max or min limit for the part-load data points as
> I recall.****
>
> ** **
>
> If you’d like a copy of the spreadsheet, I can email it to you, however,
> you might want to check the eQUEST manual or DOE-2.2 reference manuals
> regarding directly entering data points into eQUEST and let the program
> figure out the curves for you.****
>
> ** **
>
> My best,****
>
> ** **
>
> Mike Busman****
>
> ** **
>
> *Michael R. Busman, CEM*****
>
> Lead Project Engineer II****
>
> ****
>
> *Chevron Energy Solutions*****
>
> A Division of Chevron U.S.A., Inc.****
>
> 145 S. State College Blvd.****
>
> Brea, CA 92821 ****
>
> Direct 714-671-3561****
>
> Fax 714-671-3438****
>
> eFax 866-420-0335 (Include my Full Name followed by "CAI:MHTZ" on Cover
> Sheet)****
>
> Mobile 310-387-2083****
>
> mbusman at chevron.com****
>
> ** **
>
> ** **
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *David Eldridge
> *Sent:* Wednesday, August 14, 2013 9:46 AM
> *To:* Sunil Nair
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Question: Modeling Specific Chillers****
>
> ** **
>
> When the chiller runs on economizer it will use a separate set of curves
> and be modeled as a distinct chiller.****
>
> ** **
>
> One set of curves will be difficult to model both modes of operation.
>
> DSE Mobile****
>
>
> On Aug 14, 2013, at 11:34 AM, "Sunil Nair" <energymodel.sunil at gmail.com>
> wrote:****
>
> Hi All,****
>
> ****
>
> I have a couple of questions with respect to modeling specific chillers.**
> **
>
> ****
>
> 1) I am trying to model a centrifugal chiller with an economizer. The
> chiller in question is a centrifugal chiller running on R123 with an
> economizer installed to it. Do I just need to get data from the chiller
> manufacturer and input the curves into the model? Is this the right way to
> go?****
>
> ****
>
> 2) How do you model multi stage centrifugal chillers without VFD's?****
>
> ****
>
> Thanks,****
>
> ****
>
> Sunil Nair****
>
> *Ab Initio*****
>
> TMA House, Plot No. 6, 2nd Floor,****
>
> Main Road, Wagle Industrial Area,****
>
> Thane (West) - 400 604****
>
> www.abinitio.co.in****
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG****
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130816/c625ee40/attachment-0002.htm>
More information about the Equest-users
mailing list