[Equest-users] Aluminum infill panel behind the glass
Howe, Timothy
Timothy.Howe at stantec.com
Fri Aug 16 12:26:11 PDT 2013
Spandrel isn't vision glazing and should not be modeled as a "window". It is a particular opaque wall type that should be modeled as a wall. The only difference is that instead of having a brick, EFIS, stone, metal panel, etc., the exterior surface in a spandrel wall assembly is glass.
Tim.
Timothy Howe, MS, BEMP, LEED® AP BD+C
Mechanical Engineer
Stantec
61 Commercial Street
Rochester NY 14614
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 281-3223
stantec.com<http://www.stantec.com/>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Morteza Kasmai
Sent: Friday, August 16, 2013 3:10 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Aluminum infill panel behind the glass
Hello all,
Attached is a part of wall section of the proposed model of office building anticipated LEED silver certification.
8-43 is Alum. Curtain wall system (KAWNEER CLEARWALL) fritted pattern on #2 clear glazing surface and painted spandrel on #4 clear glazing (U-0.48, SHGC-0.39) and 8-45 is Aluminum infill panel with 2" rigid insulation.
I am assuming this part as spandrel glass in the proposed model. How can I add the effect of 8-45 that is behind the glass?
I would appreciate your comments.
Morteza
[cid:image001.png at 01CE9A94.F0057590]
[https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130816/d51a1c25/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 46157 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130816/d51a1c25/attachment-0002.png>
More information about the Equest-users
mailing list