[Equest-users] Only natural gas consumption in February?
James Hansen
JHANSEN at ghtltd.com
Sat Aug 17 19:27:41 PDT 2013
At first glance, I would say it is because:
1) All spaces are underground, and the wall and floor construction has
a pretty good insulation value.
2) There is no outside air scheduled at all
3) Whenever the space is occupied, there is a decent amount of lighting
and power to help with any internal heating requirements
I changed the OA to 17 CFM / person, and heating went up dramatically.
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Naisby,
Claire
Sent: Saturday, August 17, 2013 9:10 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Only natural gas consumption in February?
Sorry about that - here are both attachments.
From: Naisby, Claire
Sent: Saturday, August 17, 2013 9:08 PM
To: 'equest-users at lists.onebuilding.org'
Subject: Only natural gas consumption in February?
Hello,
I am doing an energy simulation for our College's church for some energy
efficiency retrofits.
I can't figure out why my energy simulation is only using natural gas in
February in the Building Creation Wizard (simplified version). The
actual natural gas usage of the building I am trying to model is much
higher. I have been trying all day to tweak various items, but still
only shows consumption for February. The electricity usage (in kWh),
however, is very accurate.
What am I doing wrong/overlooking?
Thank you,
Claire Naisby
Energy Manager, CEM
Davidson College
Office: 704-894-2388
Cell: 281-702-0534
clnaisby at davidson.edu
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130817/5f3ff6f1/attachment-0002.htm>
More information about the Equest-users
mailing list