[Equest-users] Expression Evaluation Error
Robby Oylear
robbyoylear at gmail.com
Thu Aug 22 09:23:53 PDT 2013
I poked around in your file and couldn't see an obvious answer to your
problem. I was able to eliminate the errors for the referenced plenum
spaces being called out but not existing by changing your floor to ceiling
height to match the floor to floor, which essentially deleted the plenum
spaces.
Though I can't say for sure that there is a maximum number of spaces that
can be defined per floor in the wizard, that would be my guess as to what's
happening here. If I were in your shoes I'd break the floor into two
floors at the same elevation and see if that works out. I took a crack at
doing that and it seems to work. I've run into a similar issue where I
exceeded the number of allowed vertices for a single floor polygon and had
to break it in two.
May not be the answer you're looking for. Hope this helps.
[image: Inline image 1]
On Thu, Aug 22, 2013 at 8:55 AM, Eric O'Neill <ELO at michaelsenergy.com>wrote:
> This one has me stumped, and it looks like it’s been an issue before, so
> I’m hoping someone has an idea. I was building a model in the wizard and
> went to save-as before something got screwy, and it appeared I was too
> late. I got an error for multiple zones that read “MULTIPLIER in *XXXzone*has Expression Evaluation Error: Invalid BDL reference”, followed up by a
> bunch of zone errors stating that they were “referenced but not defined”. I
> did some searching and came up with a few hits, but no solutions (that I
> could see). I bit the bullet and went back and tried to rezone it from my
> last save, and while the error seems to occur for different zones, I still
> got it. I went through and tried to purge out some AHU’s and spaces that
> may have pushed me up against some limit I’m not aware of, but nothing’s
> helped so far.****
>
> ** **
>
> Below is what I’m currently zoning, and you can see that in the building
> footprint screen, there are zones that I’ve defined that aren’t showing up.
> I’m attaching the pd2. Any thoughts or ideas would be appreciated!****
>
> ** **
>
> ****
>
> ** **
>
> ** **
>
> ****Eric L. O'Neill, P.E., LEED AP
> Managing Engineer - Implementation | Michaels Energy
> Phone 608.785.3328 | Cell 608.792.7721
> www.michaelsenergy.com <http://facebook.com/MichaelsEnergy> <http://www.linkedin.com/company/michaels-energy>
> <http://www.youtube.com/user/MichaelsEnergy> <http://twitter.com/MichaelsEnergy>
> ****
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 714 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 6319 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 29045 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 857 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 739 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 40839 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 549 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0019.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 12455 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130822/b646c0ac/attachment-0020.png>
More information about the Equest-users
mailing list