HI Vamshi,
If the 95,000 sqft spaces are deemed to be conditioned per Section 3 ASHRAE
90.1 space definition, your Baseline system type based on 100,000 sqft not
5000 sqft. You will then have to model a baseline cooling and heating
system in the Proposed model and model your office space system as
designed. You can then claim savings for natural ventilation / fans using
exceptional calculation method.
Hope this helps.
Regards
Ramya
On Fri, Aug 30, 2013 at 12:10 PM, Singh, Arvind <Arvind.Singh at dnvkema.com>wrote:
> I am telling you with my experience. The minute you include this space
> in your model your system type will change. You have to assigned a system
> to “95,000 ft2 of regularly occupied office” and claim the saving of
> natural ventilation using exceptional calculation.****
>
> ** **
>
> Arvind ****
>
> ** **
>
> *From:* Kushagra Juneja [mailto:maverick.kushagra at gmail.com]
> *Sent:* Friday, August 30, 2013 10:59 AM
> *To:* Singh, Arvind
> *Cc:* vamshi ranga; David Eldridge; equest-users at lists.onebuilding.org
>
> *Subject:* Re: [Equest-users] Non conditioned regularly occupied space****
>
> ** **
>
> Hi guys. ****
>
> ** **
>
> I somehow agree with Arvind. However, ASHRAE system type selection is
> based on conditioned area and not overall area. ****
>
> ** **
>
> If you think you need to claim savings for natural ventilation, the same
> can be done using exceptional calculation. One approach I saw and was
> approved by GBCI was when a HVAC system was modeled in both Baseline and
> Proposed Case. The schedule of Proposed Case was so adjusted, to turn the
> system off when the adaptive comfort temperature is met in the space in the
> Proposed Case. That ways, the Baseline system was still running to meet
> space temperatures while the Proposed system was not running and hence the
> savings. ****
>
> ** **
>
> There are few CIRs on this which I might be able to share in the due
> course. ****
>
> ****
>
> ** **
>
> Thanks****
>
> ** **
>
> Kushagra****
>
> ** **
>
> ** **
>
> On Fri, Aug 30, 2013 at 9:01 PM, Singh, Arvind <Arvind.Singh at dnvkema.com>
> wrote:****
>
> Hi Vamshi,****
>
> ****
>
> Based on your sqft and fuel size you will have system type and that will
> be system 6 in your case. Baseline model and proposed both will need
> heating and cooling system for non-conditioned space. But you can set up
> high cooling set point for baseline and proposed model to avoid any cooling
> in the non-conditioned space.****
>
> ****
>
> Thanks,****
>
> Arvind****
>
> ****
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *vamshi ranga
> *Sent:* Friday, August 30, 2013 10:21 AM
> *To:* David Eldridge
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Non conditioned regularly occupied space****
>
> ****
>
> Dear David,****
>
> ****
>
> The 95,000 ft2 area has only normal ceiling fans.****
>
> ****
>
> As I read in ASHRAE 90.1, it says, we shall model HVAC (Cooling or
> Heating) even if there is NO system proposed. But in this case, VRV system
> is proposed for 5000 ft2 area, so how shall I proceed with the remaining
> 95,000 ft2 area?****
>
> ****
>
> Thanks,****
>
> Vamshi.****
>
> ****
>
> On Fri, Aug 30, 2013 at 4:31 PM, David Eldridge <
> DEldridge at grummanbutkus.com> wrote:****
>
> Just to clarify - does the remaining 95,000 ft2 of regularly occupied
> office have an engineered natural ventilation scheme?
>
> There are some cases where 90.1 asks for cooling systems to be modeled
> even if none are proposed. You'll need to find out if those conditions
> apply to you.
>
> DSE Mobile****
>
>
> On Aug 30, 2013, at 4:06 AM, "vamshi ranga" <vamshiranga at gmail.com> wrote:
>
> > Dear All,
> >
> > We are modeling Non residential building for USGBC New Construction
> rating, which has regularly occupied (office) area of 100000 sq ft, out of
> which only 5000 sq ft of the regularly occupied (office) area is
> conditioned with VRV systems.
> >
> > Could you please let us know how the conditioned area shall be
> considered in Baseline and Proposed case. my doubts is,
> >
> > Shall this be modeled with 5000 sq ft conditioned area in both Base and
> Proposed or Is there any minimum requirement for percentage conditioned
> area?
> >
> > Thanks,
> > Vamshi.****
>
> > _______________________________________________
> > Equest-users mailing list
> > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> > To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG****
>
> ****
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130830/5de2b822/attachment-0002.htm>
More information about the Equest-users
mailing list