[Equest-users] Ductless Split
Nick Caton
ncaton at smithboucher.com
Mon Dec 2 08:03:13 PST 2013
Hi Nikki,
You can get started defining a direct return split heat pump system as follows via DD wizards:
[cid:image001.png at 01CEEF42.3693F7F0]
I'll caution first that eQuest cannot specify non-rectilinear windows, so you'll want to define rectangular windows of equivalent area as those occur. That said, to accurately handle the roof geometries you're showing will require some degree of detailed mode (post wizard) edits. There are many ways to approach this, but I would probably set up a single shell of a height to match the lower roof. In defining custom zones, I'd be mindful to ensure the higher elevation roof sections are provided distinct zones so that I will be able to easily "raise the roof" in detailed mode by editing the space height properties for the corresponding areas. Air wall partitions can thermally account up for walls created in this way that don't really exist.
To get the tilted roof sections done, you'd need to first delete/edit the polygon(s) for the remaining roof sections so that they only extend to the point I'm indicated below. Then you'd create one new roof section and polygon to include a tilt of what looks like approximately 45 degrees. I'd use the 3D model you're currently sharing to first determine the properties of that rectangle, to save some guesswork (width/length/tilt). After defining the new roof section, play with its X/Y/Z coordinate and azimuth properties as required, using the 3D view as a reference) to ensure it lines up correctly in the model. If it ends up partially or wholly within the building it will simulate without errors but will be incorrectly "shaded" by the surrounding surfaces.
[cid:image002.png at 01CEEF42.3693F7F0]
All that said, I expect it would be reasonable to more simply approximate this roof as two flat sections, particularly if it's a well-insulated roof assembly (making the precise area/orientation less critical, relatively speaking). That would trim my instructions down to simply editing the appropriate space height properties in detailed mode.
Hope that helps get you started! There are additional visual guides for polygon and exterior surface edits available in the mailing list archives and elsewhere on the web if you are interested in further reading on the topic.
Best regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nikki
Sent: Monday, December 02, 2013 8:10 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Ductless Split
Hi,
I am a grad student just learning eQuest and I am not sure how to input Ductless Split System into my model. Also, I've attached a photo.... is there any way to model the roof of the building with the door labeled 1437.
Any help is appreciated, thank you!!!
[Inline image 1]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131202/5707407a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 58149 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131202/5707407a/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 677868 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131202/5707407a/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131202/5707407a/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 64694 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131202/5707407a/attachment-0005.jpg>
More information about the Equest-users
mailing list