[Equest-users] Excessive pumping power consumption
zhaoyongqing1987
zhaoyongqing1987 at 126.com
Thu Dec 5 05:06:24 PST 2013
Don't know whether the humidifer is included in your project.the consumption of humidifer is usually included in pumps & auxiliary section.
At 2013-12-05 19:53:09,"Javed Iqbal" <eee.javed at gmail.com> wrote:
Hi,
Continuing to the above problem, I've generated hourly kWh consumption for all pumps and found that pump power in "Annual Energy Consumption End use report" is almost double than the summation of hourly pumps kWh consumption which includes Primary, Secondary and Condenser pumps.
Does eQuest reports all pumping power (Primary, Secondary and Condenser pumps) in pumps & auxiliary section?
I would appreciate any help on this.
Thanks in Advance!
On Thu, Dec 5, 2013 at 8:35 AM, zhaoyongqing1987 <zhaoyongqing1987 at 126.com> wrote:
you can set pump schedule in chilled water loop to force pump running as per building operating hours .
yongqing zhao
At 2013-12-04 05:12:08,"John Aulbach" <jra_sac at yahoo.com> wrote:
Then there is a cooling load that is not shutting off. A space on 24/7? Send the .INP and .PD2. And version number. Not all of us have gone to 3.65.
John
From: Javed Iqbal <eee.javed at gmail.com>
To: John Aulbach <jra_sac at yahoo.com>
Cc: equest-users <equest-users at lists.onebuilding.org>
Sent: Tuesday, December 3, 2013 1:08 PM
Subject: Re: [Equest-users] Excessive pumping power consumption
Yes, All the chilled water loop operation is on demand. As such there is no heating so all the problem is on chilled water pump.
Thanks!!
On Tue, Dec 3, 2013 at 4:01 PM, John Aulbach <jra_sac at yahoo.com> wrote:
Javel:
Did you put the entity (chiller, boiler) that the pump is serving on DEMAND? Otherwise, the pump will never stop.
John R. Aulbach, PE
From: Javed Iqbal <eee.javed at gmail.com>
To: equest-users <equest-users at lists.onebuilding.org>
Sent: Tuesday, December 3, 2013 12:58 PM
Subject: [Equest-users] Excessive pumping power consumption
Dear All,
I'm simulating a large commercial building for LEED compliance. There i am facing a major issue in pumping power annual consumption. The proposed case pumping power is almost 7 times higher than the ASHRAE baseline case which has great impact on my overall anticipated savings. I've generated hourly report to see the pump operations power and found propose case pump is running all year round whereas baseline is running as per building operating hours. I've thoroughly checked all the schedules assigned and it seems fine to me. My gut feeling is there is some load which is driving the pump to run throughout the year. I would appreciate if someone can give expert advice to troubleshoot this.
Thanks in Advance!!
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131205/a9aa58e2/attachment-0002.htm>
More information about the Equest-users
mailing list