[Equest-users] HVAC systems: Baseboard Heating
    Bishop, Bill 
    bbishop at pathfinder-ea.com
       
    Mon Feb  4 12:06:06 PST 2013
    
    
  
Mike,
Baseboard capacity is entered/determined at the zone level. Read the DOE-2 help menu item for the field below for the explanation of how eQUEST determines the default capacity.
If you leave it blank, eQUEST will autosize each zone. You need to enter zero values for zones that don't have baseboards, otherwise all of a system's zones with heating loads will be modeled with them.
Negative values should be used for manually-entered capacities other than zero.
If you select Outdoor Reset instead of Thermostatic control, you have to enter a reset schedule at the system level or the baseboards will not operate.
Regards,
Bill
[cid:image004.jpg at 01CE02E9.28022DB0]
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike Raiva
Sent: Monday, February 04, 2013 2:48 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HVAC systems: Baseboard Heating
Hello,
I am modeling a reference building with an HVAC system that requires baseboards with hot water.
How do you handle the capacity? Is there a way to get eQuest to autosize the capacity? Or am I missing something.
Thanks.
MICHAEL RAIVA, P.Eng., LEED(r) AP
Mechanical
Williams Engineering Canada Inc.
T:  778.484.2983    F:  778.484.3901
W:  williamsengineering.com<http://www.williamsengineering.com>
Engage.  Innovate.  Inspire.
Please consider the environment before printing this email.
Email Transmission Policy<http://www.williamsengineering.com/legal>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130204/eb6c7f27/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130204/eb6c7f27/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 20966 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130204/eb6c7f27/attachment-0005.jpg>
    
    
More information about the Equest-users
mailing list