[Equest-users] Error: Hot Water Loop has zero design flow
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Thu Feb 7 20:46:32 PST 2013
Hi Mike,
without looking at your modeling files directly, it may be an input issue
at your airside level. If you have a hot water loop system, then it is
likely that on your airside heating tab you do not have an input value for
your reheat delta T. This needs to be entered in most cases to generate a
heating demand on the hot water loop. I suggest checking your input on
this tab and using a starter number of 30 F for a delta T. see if this
corrects your error.
Other than that, I suggest that you post your .pd2 & .inp file (maybe your
weather file too if it is a custom file) and letting someone on this list
take a look at your file to help you troubleshoot your issue for corrective
action.
Cheers,
Pasha
On Mon, Feb 4, 2013 at 3:49 PM, Mike Raiva
<mraiva at williamsengineering.com>wrote:
> Hello,****
>
> ** **
>
> I have been scratching my head trying to located the following simulation
> error:****
>
> ** **
>
> “Loop: Hot Water Loop has zero design flow.****
>
> Check input for consistency, or specify design loads.
> ****
>
> “****
>
> ** **
>
> I have gone into my HW plant and entered my loop head and flow. See below.
> However, the error won’t go away.****
>
> ** **
>
> ****
>
> ** **
>
> *MICHAEL RAIVA, **P.Eng., LEED® AP*****
>
> *Mechanical*
>
> ** **
>
> *Williams Engineering Canada Inc.*
>
> *T:* 778.484.2983 *F:* 778.484.3901****
>
> *W:* williamsengineering.com <http://www.williamsengineering.com>****
>
> * *
>
> *Engage. Innovate. Inspire.*
>
> * *
>
> *Please consider the environment before printing this email.*
>
> *Email Transmission Policy* <http://www.williamsengineering.com/legal>****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130207/00e45399/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 56956 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130207/00e45399/attachment-0002.png>
More information about the Equest-users
mailing list