[Equest-users] Replacing baseboard with heat pump results in higher space heating
    Chris Jones 
    cj at enersave.ca
       
    Mon Feb 18 18:58:05 PST 2013
    
    
  
Yes, it is rough.  Where does one begin?  I generally like to look at 
the results in the .SIM file.  First look at the SV-A reports - one 
model has no outside air, the other has 10000 cfm outdoor air.
Then look at the SS-D report.  The one has a peak heating of 339 
KBTU/hr and the other has 1200 KBTU/hr.   This could be due to adding 
outdoor air to the other.
If I still don't have an inkling, I will add some hourly reports to 
compare the total supply cfm vs outdoor air ratio at different hours 
of the year.  I didn't have to do that in this case.
And if all else fails, I would then ask for help from the egroup.
>
>I submitted this earlier and was asked to add the .INP files to the 
>.PD2 files I attached.  Below is the original message repeated.
>
>
>I'm doing a rough energy model using mostly Equest defaults and 
>wanted to replace the existing baseboard electric heating with a 
>heat pump.  The resulting space heating increased from 57,000 kWh to 
>147,000 kWh (including the HP Supp.).  From the baseline model I 
>went into the wizard and added the dx heating and cooling and 
>aligned the EER/COP with state compliant levels 
>(10.7/3.2).  Attached are the .PD2 files for baseline and HP 
>models.  Many thanks.
>
>
>
>Terry Mapes | Mechanical Engineer
>ACS Professional Staffing Contractor
>USDOE Bonneville Power Administration
>2316 Eastgate St., Suite 160 | Walla Walla, WA | 99362
>office 509-527-6231 | cell 509-970-5715 | fax 509-527-6210
>
>
>
>
>
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to 
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
 >>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130218/448d7828/attachment-0001.htm>
    
    
More information about the Equest-users
mailing list