[Equest-users] LS-C Report showing zero area
    Lijun Larry 
    lijun.larry at gmail.com
       
    Mon Feb 25 17:37:36 PST 2013
    
    
  
You should look at your LS-B for the plenum zone. Since eQUEST calculate
heat transfer within the conditioned zone and unconditioned zone separately,
heat loss through the roof should be included in the plenum zone if it's
there. 
 
 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike Raiva
Sent: February-25-13 7:26 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LS-C Report showing zero area
 
Hello,
 
My LS-C report is showing a zero number for a building with a roof area.
 
 
I have looked at our model and I don't see where the roof is not being
picked up.
 
MICHAEL RAIVA, P.Eng., LEEDR AP, CCGDR 
Mechanical Engineer
 
Williams Engineering Canada Inc.
T:  778.484.2983    F:  778.484.3901
W:   <http://www.williamsengineering.com> williamsengineering.com
 
Engage.  Innovate.  Inspire.
 
Please consider the environment before printing this email.
 <http://www.williamsengineering.com/legal> Email Transmission Policy
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130225/4a92e2d8/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 32073 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130225/4a92e2d8/attachment-0002.png>
    
    
More information about the Equest-users
mailing list