[Equest-users] EEM neglible change in different Runs
    Sami, Vikram 
    Vikram.Sami at perkinswill.com
       
    Tue Feb 26 07:42:50 PST 2013
    
    
  
How many stories does your building have?
Also - you might want to try reducing it down to R 10 or something lower - just to see what the sensitivity is - you might be into diminishing returns for the added insulation.
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Eldridge
Sent: Monday, February 25, 2013 6:52 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] EEM neglible change in different Runs
I think the results are probably as eQUEST intended then.
Heat gain would be transferred directly to the conditioned zones if there was no plenum zone, and heat would be transferred to the AHU airstream if the system was plenum return.
With a plenum combined with ducted return, eQUEST is going to model the heat as moving through an insulation value to enter the conditioned spaces, so you will definitely see a diminishing return on roof insulation.
I believe there are some variables to allow a higher percentage of heat transfer through the return ductwork. There probably isn't a lot of insulation value to tweak in terms of allowing heat to conduct from the plenum space into the occupied zone space, although you might review your assumptions in case the heat transfer coefficients might be adjusted to allow more connection between plenum zone and conditioned zone if you think it to be more accurate.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Mike Raiva [mailto:mraiva at williamsengineering.com]
Sent: Monday, February 25, 2013 4:52 PM
To: David Eldridge; equest-users at lists.onebuilding.org
Subject: RE: EEM neglible change in different Runs
Yes I have both a plenum zone and ducted return.
MICHAEL RAIVA, P.Eng., LEED(r) AP, CCGD(r)
Mechanical Engineer
Williams Engineering Canada Inc.
T:  778.484.2983    F:  778.484.3901
W:  williamsengineering.com<http://www.williamsengineering.com>
Engage.  Innovate.  Inspire.
Please consider the environment before printing this email.
Email Transmission Policy<http://www.williamsengineering.com/legal>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Eldridge
Sent: Monday, February 25, 2013 2:45 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] EEM neglible change in different Runs
Is there a plenum zone, while you are also using ducted return?
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike Raiva
Sent: Monday, February 25, 2013 4:42 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] EEM neglible change in different Runs
I am running an EEM wizard where I changing the Roof R-Value from R-42 to R-24.
Here are my results. (almost the same) Am I missing something.
Base Results:
[cid:image001.jpg at 01CE140E.050C4170]
EEM with Roof R-24.
[cid:image002.jpg at 01CE140E.050C4170]
MICHAEL RAIVA, P.Eng., LEED(r) AP, CCGD(r)
Mechanical Engineer
Williams Engineering Canada Inc.
T:  778.484.2983    F:  778.484.3901
W:  williamsengineering.com<http://www.williamsengineering.com>
Engage.  Innovate.  Inspire.
Please consider the environment before printing this email.
Email Transmission Policy<http://www.williamsengineering.com/legal>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130226/9525fee9/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 59765 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130226/9525fee9/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 59804 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130226/9525fee9/attachment-0005.jpg>
    
    
More information about the Equest-users
mailing list