[Equest-users] Baseline PTAC Fan Energy for a Proposed Merv13	+	Return Duct System
    James Hess 
    JHess at tmecorp.com
       
    Tue Feb 26 21:01:37 PST 2013
    
    
  
Interesting question about DOAS and the current fan power allowance for system types 1 & 2.  I think we very much need an update to Appendix G to account for the fan power requirements of the dedicated outdoor air systems that are (in my opinion) required for unitary type systems such as PTACs as well as the PSZ-ACs.
I'm in the south, and so we cannot count on simply opening the windows to meet our ASHRAE ventilation requirements, at least not anymore :) (we did exactly that through until ~ 1988 at the school in Louisiana I attending while growing up, at which point we finally got air conditioning and promptly shut the windows).
I would argue that a DOAS is necessary in the south to properly provide outside air, while maintaining acceptable building humidity conditions, for unitary type systems.  Anything less is negligent design, in our opinion.  However, at the present time, Appendix G assumes that PTACs (or PSZ-ACs) will bring outside air continuously into the zones and cycle the compressor to control room temp while ignoring humidity.  You can't do that in real life.  Where we have seen that done, you get condensation and eventually mold, and eventually you get sued.
I think you have run into a gray area for which there is no good answer currently.  Assuming that you are working on a LEED project, you'll have to hope that you run up against a LEED reviewer that will exercise good judgment and common sense, and understand that this area is not covered by Appendix G currently and that a reasonable allowance for DOAS fan power should work and should be allowed, since it can be argued that DOAS are required to meet the ASHRAE 62 ventilation requirements.
The issue is that the 0.3 watts/CFM is only enough fan power allowance to account for a motel "thru the wall" type unit.  No external ductwork (supply or return), barely a filter, and certainly no allowance for a DOAS.
My recommended solution would be to model the DOAS with the same fan power in the Baseline as in the Proposed.
That's conservative in my opinion.  You aren't taking credit for any fan energy savings associated with the DOAS, but neither are you unnecessarily penalizing yourself either for something that is required for the Proposed Design.
Regarding AHRI fan power assumptions, I'm not sure about that question.  But I did a quick test in eQuest.  I built a quick sample model in the DD wizard, selected PTAC, and entered 11 EER for cooling efficiency.  I then went to the detailed mode and the EIR conversion was the exact same that eQuest does for any system --> EIR = 0.2580 for EER =11.0.  Consequently, we know that eQuest is using the 365 watts/KCFM conversion.  But that's eQuest. I don't know what AHRI 310 uses for fan power assumption, if anything.  I looked into this a while back and I don't think that eQuest is on the same page with the AHRI fan power assumptions used in the ratings.  I could be incorrect, however.  Another thing is that the fan power assumptions used in the AHRI ratings have absolutely nothing to do with the Appendix G fan power requirements.  I do know that.  I think we need to let eQuest do its thing in the wizard/detailed interface transition, and then go to the detailed interface and change the EIR ourselves to whatever is appropriate, if we can figure out what AHRI is doing regarding fan power assumptions.
Hope this helps!  :)
Regards,
JAH
James A. Hess, PE, CEM, BEMP
Energy Engineer
TME, Inc.
Little Rock, AR
Mobile: (501) 351-4667
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn Kerns
Sent: Monday, February 25, 2013 5:57 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline PTAC Fan Energy for a Proposed Merv13 + Return Duct System
Everyone, I have been modeling some dormitories with a proposed HVAC system involving a DOA with a full exhaust air HX and MERV 13 filters. The puzzle is what to do about the baseline PTAC fan power energy? If I use 0.3 w/cfm as Appendix G suggests, my PTAC baseline system does not account for a fully ducted return\exhaust or MERV 13 filters. The commercial fan power equation for systems 3-8 accounts for this, but I am not supposed to use that formula for System 1 and 2.
Another puzzle is if I develop an cooling EIR value for my baseline PTAC using the 365 w/kCFM conversion rule and equate that with 0.3 w/cfm, what happened to the other 65 w/kCFM?
Maybe ARI 310/380 doesn't use 365 w/cfm fan power?  I read it and didn't find any statement regarding fan power requirements, but I assume it works the same as ARI 210/240?
I am wondering if a compromise of
                        PTAC fan power = CFMs *0.000365 + A             where A= PD*CFMs /4131 and PD = 1.4
might be a reasonable solution?
                        PTAC fan power = 0.00063 kw/cfm
Does anyone else have experience with this puzzle?
Kathryn Kerns
Systems Specialist
BCE Engineers, Inc.
| Ph: 253.922.0446 | Fx: 253.922.0896 |
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130227/68c3f4ba/attachment-0001.htm>
    
    
More information about the Equest-users
mailing list