[Equest-users] maximum humidity limit
David Griffin
dgriffin at etcgrp.com
Wed Jan 9 13:29:14 PST 2013
Amruta,
I'm glad to hear you are still modeling in eQuest. I hope everything else is going well.
To address your question, there are several things to consider.
1) If your building is not 100% OA, you may want to check your user input latent loads since this humidity will show up in your return air stream.
2) Are you modeling your outside air correctly?
3) If your building is 100% outside air, your climate may not be humid enough to merit dehumidification.
4) I doubt it is this, but make sure your cooling coil bypass factor is defaulted.
5) Lastly, consider viewing the following reports to get a better understanding of how your model is dealing with humidity on a system level.
SS-I
SS-N
SUPL
I hope this helps.
Thanks,
David Griffin
Energy Analyst
ETC Group, LLC
801.278.1927 ext. 128
Cell 480.235.0899
Fax 801.486.0668
dgriffin at etcgrp.com
1997 South 1100 East, Suite 201, Salt Lake City, UT 84106-4471 - www.etcgrp.com
-------------------------------------------------------------------------------------------------------------------
CONFIDENTIALITY NOTICE This e-mail transmission, and any documents, files or previous e-mail messages attached to it may contain confidential information that is legally privileged. If you are not the intended recipient or the person responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of any of the information contained in or attached to this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone at (801) 278-1927 and destroy the original transmission and its attachments without reading them. Thank you.
-----Original Message-----
From: Amruta Khanolkar [mailto:askhanol at asu.edu]
Sent: Wednesday, January 09, 2013 1:23 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] maximum humidity limit
Hi all,
I am working on a preservation facility project in eQuest. Because of the specific type of the building, keeping temperature and humidity constant all throughout the year is of high importance. This project also has desiccant system for dehumidification. Due to eQuest's capacity I have modeled the entire building except the desiccant system in eQuest. So right now the dehumidification load is on the cooling coil. The maximum and minimum humidity levels are 45% and 35% respectively. I just wanted to remove the maximum humidity limit (no
dehumidification) and increase it to 80% or 90% just to study the dehumidification load on the cooling coil. I was expecting the cooling energy consumption to go down compared to the original consumption after I remove/increase the max humidity limit but surprisingly my numbers don't change at all. Am I missing something here?
Thanks,
Amruta