[Equest-users] Spray Pump power not showing on PV-A report
    Ritwik Kakati 
    rkakati at dagherengineering.com
       
    Fri Jan 11 09:09:15 PST 2013
    
    
  
Nick, Bill,
Thank you for your responses and for taking the time to look into this. I will use your suggestions and hopefully can convince USCIS.
Ritwik Kakati, LEED Green Associate
Design Engineer
DAGHER ENGINEERING, PLLC
29 Broadway, New York, NY 10006
T. 212.480.2591 x140
F. 212.480.2654
rkakati at dagherengineering.com
www.dagherengineering.com
Save Trees, Consider the Environment. Please print only when necessary.
This email and any attachments may contain confidential or proprietary information and use or distribution is strictly prohibited. If you are not the intended recipient, please notify us and delete.  Dagher Engineering, PLLC has no responsibility for errors or discrepancies that may occur in the electronic transmission of data.
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Friday, January 11, 2013 11:44 AM
To: Nick Caton; Ritwik Kakati
Subject: RE: Spray Pump power not showing on PV-A report
I tried modeling a fluid cooler and got the same results (no Spray kW/cell reported on PV-A). I would just provide a detailed explanation to the reviewer and note that it appears to be a software problem as evidenced by feedback on equest-users.
Regards,
Bill
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Friday, January 11, 2013 11:21 AM
To: Ritwik Kakati; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Spray Pump power not showing on PV-A report
Interesting - I'm observing the same behavior in an independent model.  Detailed reports summary isn't providing any of the usual reporting insights, and after some prodding I can't find any less intuitive input combinations that engage this field in the PV-A report.  This may well be a bug that needs to be ironed out for the next round of updates (fingers crossed!)...
I haven't had to explain this to a reviewer myself yet, but a backup plan from past experience: USGBC reviewers can be sometimes be satisfied by demonstrating your input exists and is being registered in the results, as you describe, with screenshots and an explanation that you cannot get the PV-A report to play nicely...
No guarantees though, definitely consider that a backup plan for if all else fails ;).
Does anyone else have a modeled fluid cooler with a non-zero spray pump result in the PV-A report?
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ritwik Kakati
Sent: Thursday, January 10, 2013 7:01 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Spray Pump power not showing on PV-A report
I modeled a LEED building with a closed circuit cooling tower (fluid cooler) and spray pumps. I entered the SPRAY-KW/CELL value, and verified that it is listed in the INP file. However, my PV-A report displays 0.00 for Spray Pwr Per Cell. I do know that the program is taking into consideration the  SPRAY-KW/CELL value because the Pumps & Aux energy changes when I enter 0 for spray pump power. USGBC has objected to the 0 value on the PV-A report, so can anyone suggest any solution for this issue? Is this a known bug in eQuest?
Thanks,
Ritwik.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130111/7b383599/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130111/7b383599/attachment-0004.jpg>