[Equest-users] Questions about 9.6.2 Additional Interior	Lighting Power
    Jeremy Poling 
    jeremy.poling at att.net
       
    Wed Jan 16 21:59:41 PST 2013
    
    
  
I believe the answer lies in the text directly part of 9.6.2 before the
subpargraphs on the specific allowances.  Note that all lighting that is
installed using the additional allowance must be on automatic controls to
turn off during non-business hours.  Right after that, I find this to be
the best answer the what the additional lighting allowance is good for:
"This additional power shall be used only for the specified luminaires and
shall not be used for any other purpose."
Just like the site lighting allowance, this is a non-tradable allowance
only good for the space the lighting is installed in and even more
specifically, only for the lighting that meets the definition.  This means
you can't use the additional allowance to make up for an overage in this
space or an overage in the total results of the space-by-space method
caused by non-qualifying fixtures.  This has been a LEED review comment in
the past as well.
The math is also explained in the 90.1-2007 compliance forms.  They are
optional for LEED purposes, but worth a review, especially for complicated
lighting calculations.  They are attached for reference and can be found on
the ASHRAE website.
Jeremy R. Poling, PE, LEED AP+BDC
Sustainability Consultant
On Wed, Jan 16, 2013 at 8:12 PM, Arpan Bakshi <arpanbakshi at gmail.com> wrote:
> Jie, another good forum for that type of question is LEEDuser.
>
> In the spirit of full disclosure, YR&G is the primary author for the
> forum, but guidance is posted by hundreds of LEED experts from a variety of
> firms.
>
>
>
> Arpan Bakshi, BD+C, PQP
> T (646) 704-2880
>
> YR&G
> www.yrgxyz.com
>
>
> ...
>
> On Jan 16, 2013, at 20:15, Nick Caton <ncaton at smithboucher.com> wrote:
>
>  Hi Jie!****
>
> ** **
>
> This is certainly a great forum for general 90.1 questions, though you
> will reach a broader audience I think with the [bldg-sim] mailing list.
> [bldg-rate] is a less active list that I’ve used in the past to reach an
> audience better suited for more technical interpretations, as well. ****
>
> ** **
>
> Note well: *italicized phrases* in 90.1 have definitions you can refer to
> for clarification.****
>
> ** **
>
> 1.       9.6.1.d addresses your concern about exceeding the
> space-by-space LPD.  “Trade-offs” are permitted for the space-by-space
> method, permitting some spaces to exceed the prescribed level (with or
> without additional lighting power per 9.6.2.a) so long as the building
> total installed lighting power does not exceed the total allowance.  LEED
> EAp2/EAc1 does not change any of these rules to my understanding.****
>
> 2.       Yes.  Proposed model should reflect actual design, and Baseline
> model should reflect prescribed levels, inclusive of additional lighting
> power credits for applicable spaces.****
>
> 3.       Interesting question!  Your interpretation is probably
> defensible, but in my opinion overly conservative.  I would not limit the
> prescribed additional 1.0W/ft2 (108.W/m2) to a lesser calculated value to
> match the installed “decorative LPD.”  LEED has some extra rules found in
> the footnotes of the EAp2 modeling spreadsheet along these lines to match
> exterior non-tradable totals between models, but I haven’t encountered any
> similar restrictions along these lines for interior LPD calculations. ****
>
> ** **
>
> That said, I can’t recall using these additional allowances heavily on a
> submitted LEED project, so perhaps/hopefully someone else can chime in with
> such experience!****
>
> ** **
>
> ~Nick****
>
> ** **
>
> ** **
>
> ** **
>
> <image001.jpg>**
>
> * *
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER****
>
> ** **
>
> Smith & Boucher Engineers****
>
> 25501 west valley parkway, suite 200****
>
> olathe, ks 66061****
>
> direct 913.344.0036****
>
> fax 913.345.0617****
>
> www.smithboucher.com* *****
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jenny Zhang
> *Sent:* Tuesday, January 15, 2013 8:15 PM
> *To:* 'equest-users at lists.onebuilding.org'
> *Subject:* [Equest-users] Questions about 9.6.2 Additional Interior
> Lighting Power****
>
> ** **
>
> Dear All equest-users,****
>
> I have a question about the interpretation of ASHRAE 90.1-2007 9.6.2.****
>
> Though it’s not about eQuest, I think I could get useful information here
> because many of you are familiar with 90.1.****
>
> ** **
>
> 9.6.2 presents that the additional lighting power shall not exceed
> 10.8W/m2. For example if a lift lobby has a general LPD is 10W/sqm and
> decorative LPD is 14W/sqm.****
>
> The additional LPD is exceed 14W/sqm and whether is complied with LEED EA
> Pr2 and how to do in the ASHRAE energy models?****
>
> ** **
>
> Following is my understanding:****
>
> 1.       Item a.in 9.6.2 states that:  the additional lighting power
> shall not exceed 10.8 W/sqm, but this is not included in 9.4. A project
> with additional LPD 14w/sqm could also achieve EA Pr2 & Cr1.****
>
> 2.       For energy models: 1)baseline: the additional LPD should be
> 10.8W/sqm in this space while 14W/sqm should be 14W/sqm as design.****
>
> 3.       For spaces with additional LPD lower than 10.8W/sqm, both the
> baseline model and proposed model should be with additional LPD the same
> with design.****
>
> ** **
>
> Am I correct? ****
>
> Thanks for your attentions.****
>
> ** **
>
> Jie Zhang****
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup  business
> systems are scanned for acceptability of content and viruses****
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130116/61a14699/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20090604_lightingcompformsinstrxev4209.pdf
Type: application/pdf
Size: 377752 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130116/61a14699/attachment-0004.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20120510_9012007_lighting_forms.pdf
Type: application/pdf
Size: 812799 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130116/61a14699/attachment-0005.pdf>
    
    
More information about the Equest-users
mailing list