[Equest-users] Space heating components...
    Sunil Nair 
    energymodel.sunil at gmail.com
       
    Sat Jan 19 03:08:24 PST 2013
    
    
  
Hi Zheng,
The SS-A report will provide you system wise loads summary. This may help
to identify the systems and period during which you have unexpected heating.
Once you identify the systems you can use the SS-G report to figure out
what's happening at individual zone level for the systems affected.
I hope this helps.
Sunil Nair
On Sat, Jan 19, 2013 at 5:30 AM, Zheng Ling
<zling at williamsengineering.com>wrote:
> Hi there:****
>
> ** **
>
> I meet a strange simulation result. The project is is 6000 SQM warehouse
> plus a 1000 SQM office. The result shows a surprising natural gas usage
> 84581 MBTU or 89237 GJ. 96% belongs to space heating. ****
>
> ** **
>
> REPORT- LS-C BuiLding Peak Load Components shows heating load 32.5 W/m2
> (excluding outside ventilation air loads). This is normal. ****
>
> ** **
>
> REPORT- SS-D Building HVAC Load Summary shows annual heating energy 1460
> MBTU or 1540 GJ.****
>
> ** **
>
> Is there anywhere else to check the source of the extra abnormal space
> heating load?****
>
> ** **
>
> THX!****
>
> *ZHENG LING, **P.Eng.*****
>
> *Mechanical*
>
>  ****
>
> *Williams Engineering Canada Inc.*
>
> 10010-100 Street, Edmonton, AB, T5J 0N3****
>
> *T:  *780.409.3185 *  F:  *780.425.1520   *W:  *williamsengineering.com<http://www.williamsengineering.com/>
>   ****
>
>
> *Engage.  Innovate.  Inspire.*
>
> *Please consider the environment before printing this email.**
> **Email Transmission Policy* <http://www.williamsengineering.com/legal>***
> *
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130119/e849d447/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list