CFM/person is given in ASHRAE 62.1 Table 6-1.

Two values are given in the table which affect your eQUEST input:


1)    CFM/person

2)    CFM/SF

The combination of the two values is your minimum OA – see Equation 6-1 of ASHRAE 62.1.

Therefore, your eQUEST input should go something like this:

((#LR(“SPACE”, “NUMBER-OF-PEOPLE”)*([CFM/PERSON])) + (#LR(“SPACE”, “AREA”)*([CFM/SF])))/ (#LR(“SPACE”, “AREA”)

Refer to ASHRAE 62.1 Table 6 for [CFM/PERSON] and [CFM/SF] values.

I hope this helps with your question. If anything is unclear, I’m sure the forum will clarify.

Thanks,

David Griffin
Energy Analyst
ETC Group, LLC
801.278.1927 ext. 128
Cell 480.235.0899
Fax 801.486.0668
dgriffin at etcgrp.com<mailto:dgriffin at etcgrp.com>

[Copy of ETC_LogoOnly2_rgb_sm.png]
1997 South 1100 East, Suite 201, Salt Lake City, UT 84106-4471 – www.etcgrp.com<http://www.etcgrp.com/>
-------------------------------------------------------------------------------------------------------------------
CONFIDENTIALITY NOTICE This e-mail transmission, and any documents, files or previous e-mail messages attached to it may contain confidential information that is legally privileged.  If you are not the intended recipient or the person responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of any of the information contained in or attached to this transmission is strictly prohibited.  If you have received this transmission in error, please immediately notify us by telephone at (801) 278-1927 and destroy the original transmission and its attachments without reading them. Thank you.

From: ritu garg [mailto:engg_ritz at yahoo.co.in]
Sent: Monday, July 01, 2013 7:58 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] cfm/person

please let me know the formula to calculte the cfm/person
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130701/a4d33c98/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1559 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130701/a4d33c98/attachment-0002.jpg>


More information about the Equest-users mailing list