[Equest-users] Overload problems.. again.
Nick Caton
ncaton at smithboucher.com
Tue Jul 16 09:38:51 PDT 2013
All,
I've seen this topic come and go many times as well and have hesitated in the past to share my thoughts, but having spent enough time pondering this I figure I may as well share my opinions to further the discussion:
My understanding is that loop capacity warnings often fall in the category of attention messages that can easily be checked and dismissed as erroneous.
It's my understanding one of two things is the usually case when you get one of these warnings:
1. Your primary hydronic heating/cooling equipment is actually of insufficient capacity to keep up with the highest demand incident on the loop, in which case you have a real problem that will likely manifest as significant block of unmet heating/cooling hours, assuming typical thermostat inputs. One way to check appropriate equipment sizing is to check the PEAK load for the loop/equipment of concern in the PS-C/PS-D reports against a tallied sum of the CAPACITY for all associated equipment, as reported in the PV-A report. Be mindful units are typically of different magnitude between these reports.
2. More commonly, the program has calculated a secondary capacity which exceeds the primary equipment capacities *in sum*. This secondary capacity is a "sum of maximum capacities" (i.e. the most each heating/cooling coil can do, as autosized/specified, in sum), and can easily be well in excess of the maximum hourly load incident on the primary equipment during the simulation. Another way to put it is there's no "whole-building" diversity worked into the secondary capacity figure that shows up in the ATTN report. In such cases, the primary capacity as autosized/specified can in fact be just fine.
The designer sizing the primary equipment should be able to speak to what degree of diversity (if any) is intended for the whole building heating and cooling loads for determining equipment capacities. Different systems will have different ranges of "normal" for whole-building diversity, and it isn't uncommon for hydronic cooling vs. heating systems to be designed with different capacity diversities for the same project.
I'd be interested to hear if others have a similar perspective or further insight as to when such cautions can be disregarded and when they're cause for real concern.
Hope this helps you in the meantime Kim!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of DongEun Kim
Sent: Monday, July 15, 2013 7:22 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Overload problems.. again.
Hi All~
I've been posting about loop overload problem and still haven't got any responses.
In the archive, some equesters had cast questions regarding overload problems, but they don't seem to get answers either.
It it really that, no one knows how to fix it, or no one had experienced overload problems but us who question about it.
I just want to know why the over load is being shown in the loop report(PS-D),
and any possible approach to fix the overload.
Any advice or a mere comment will be a great help!
Thank you!
Kim
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130716/7a6072e2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130716/7a6072e2/attachment-0002.jpg>
More information about the Equest-users