The functionality that Vikram mentions – hovering the mouse over an input field to see basic information – has to be enabled in the eQUEST initiation file.

[cid:image002.jpg at 01CE82D4.2D321E60]

You have to use a text editor to add the following line to the EQUEST.INI file:
ShowBDLComKeyInToolTip=1

This file is in the eQUEST data folder, the location of which is easily found by selecting Tools -> View File Locations -> View eQUEST Data Directory…

Additional directions are found in the RMI Model Manager Set Up and User’s Guide<http://www.rmi.org/Content/Files/RMI%20Model%20Manager%20BETA%20TEST%204.0%20Users%20Guide.pdf>, courtesy of Ellen Franconi at RMI.

Regards,
Bill

William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P   Sustainability – the forest AND the trees. P

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Tuesday, July 16, 2013 6:39 PM
To: Sambhav Tiwari; equest-users
Subject: Re: [Equest-users] Condenser water loop

Yeah – the CHW temp is the design temp in the condenser loop. The delta T is the temp rise in the loop between return and supply.

Also – if you ever wondered what a certain item means in eQUEST – hover your mouse over it and it will give you some basic information. If you right click – you can go to item specific information or general topic information too.

[cid:image004.png at 01CE82D1.47E419F0]

-Vikram



Vikram Sami
Associate Partner



ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104


From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sambhav Tiwari
Sent: Monday, July 15, 2013 5:02 AM
To: equest-users
Subject: [Equest-users] Condenser water loop

Dear All,
               In my condenser water loop ie CW loop under basic specificatiob tab there are two parameters design CHW temperature and loop design delta T

Does these two parameters represent condenser water inlet temparature and range of cooling tower which is (condenser inlet- condenser outlet) respectively.?


Regards
Sambhav

________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130717/e5e58710/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 64749 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130717/e5e58710/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 11788 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130717/e5e58710/attachment-0002.jpg>


More information about the Equest-users mailing list