[Equest-users] existing buildings/alterations
Bishop, Bill
bbishop at pathfinder-ea.com
Thu Jul 25 13:24:36 PDT 2013
Kent,
The exception to 6.1.1.2 (allowing existing systems to handle the HVAC needs of additions) provides a way to comply with Standard 90.1 without replacing existing systems. But your question is not about 90.1 compliance, it is about Appendix G modeling (presumably for LEED New Construction). Table G3.1 (10.) is clear on the Baseline HVAC system requirements and provides no exception for existing buildings. There may be exceptions if this is for a utility incentive program or some other application other than for a LEED NC model. Otherwise, I am not aware of any CIRs or other interpretations that would allow modeling existing systems in the Baseline.
~Bill
From: Kent Beason [mailto:kbeason at estesmcclure.com]
Sent: Thursday, July 25, 2013 4:03 PM
To: Bishop, Bill; 'Nick Caton'; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] existing buildings/alterations
Bill,
Okay...I would classify this as one of those nuances that Nick characterized earlier. It seems strange to me that this would only apply to the envelope, but after all, it is only stipulated in Table G3.1 under Section 5f Building Envelope.
To complicate the issue though, someone else's response was to use existing HVAC systems. Normally I would dismiss his response out of hand, but he was a LEED reviewer at one time and is more 90.1 knowledgeable than me currently. I was about to send this message, sure that I would model baseline per Appendix G, until I thought to look in Section 6. Does Section 6.1.1.2 provide the adequate Exception to clarify that old HVAC systems must be modeled in the baseline for a renovation/alteration project? The term "alteration" in the definitions appears to be applicable as an "addition" as shown in this Exception of 6.1.1.2. However, the verbiage "shall not be required to comply with this standard" implies that it's optional.
Kent Beason
-------------------------
office - 903 581 2291
cell - 830 609 8904
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Thursday, July 25, 2013 1:55 PM
To: Kent Beason; 'Nick Caton'; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] existing buildings/alterations
Kent,
I didn't notice your message was only to me. I assumed it would be a matter of seconds before others replied in the negative. The "existing conditions" caveat applies only to the envelope. You must use the Appendix G baseline systems and plants for the LEED Baseline, with the possible exception of the central plant for DES systems as you mention.
~Bill
From: Kent Beason [mailto:kbeason at estesmcclure.com]
Sent: Thursday, July 25, 2013 2:49 PM
To: 'Nick Caton'; Bishop, Bill; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] existing buildings/alterations
Thanks for the feedback. As I asked Bill offline, and I feel it goes without saying, but never hurts to be thorough :-): this applies to the old HVAC systems too, correct? Obtaining the old HVAC system info could be a daunting challenge unfortunately.
I've learned alot about nuances... One area of this building is storefront (essentially 100%) single pane glass around the whole perimeter!
Kent Beason
-------------------------
office - 903 581 2291
cell - 830 609 8904
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Thursday, July 25, 2013 1:32 PM
To: Bishop, Bill; Kent Beason; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] existing buildings/alterations
Agreed. Take note there are a couple nuances between what's written in 90.1 and what's required by the LEED reviewership. I believe they draw a line in the sand where if more than 50% of a project is "retrofit" vs. NC by square footage, then rotations go away.
I just had 3 LEED projects wrap up at silver/gold where in the initial submission I used thoroughly documented prescriptive baseline envelopes and 4 rotations. The preliminary review commentary required changing the envelopes to remove the rotations and match reality instead. The previous reality was (mostly) uninsulated grout filled block walls, single pane windows without film treatments, and zero wall insulation =D!
As a net result, each of these projects jumped way up in unanticipated modeling credits. It was a good day.
Outside the constraints of LEED, the closer your baseline models can reflect existing realities, the better and more informative the results of your models become for a retrofit analysis.
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Thursday, July 25, 2013 1:17 PM
To: Kent Beason; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] existing buildings/alterations
Kent,
Yes, for existing buildings, use the wall & roof assemblies, glazing properties etc. of the existing building for the Baseline values. Also, you don't have to simulate in four orientations.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kent Beason
Sent: Thursday, July 25, 2013 1:09 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] existing buildings/alterations
This question isn't eQuest specific, but deals with 90.1 interpretation.
For an existing building, with regards to shell alterations, G3.1.5-f says that "the baseline building shall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated." Is this statement as far-reaching as I believe, indicating that U-values, SHGC etc, listed in Tables 5.5 and Appendix A are ignored in a similar way as done in the proposed, since the "baseline" in this case is a real design, rather than a hypothetical baseline?
Kent Beason
Estes, McClure & Associates, Inc.
3608 West Way
Tyler, TX 75703
-------------------------
office - 903 581 2721
cell - 830 609 8904
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130725/53a6bbb6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130725/53a6bbb6/attachment-0002.jpg>
More information about the Equest-users
mailing list