[Equest-users] App G model VAV w unmet loads in heating
Walson, Kristy
kristy.walson at tlc-eng.com
Tue Jul 30 06:17:32 PDT 2013
VAV units in Equest only have heating at the zones level, not at the system level. Look at the SV-A report and you should see a heating capacity for each zone.
Kristy M. Walson, PE, LEED AP BD+C, BEMP
Associate / Sustainability Consultant
407-487-1118
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matthew Baron
Sent: Tuesday, July 30, 2013 9:03 AM
To: 'equest-users at lists.onebuilding.org'
Subject: [Equest-users] App G model VAV w unmet loads in heating
HI,
I am working on several school models and they generally fall into the packaged vav with reheat category. The spaces are fine for cooling, but are way off for heating. When I look at the ss-p report the heating capacity for the units shown to be zero, when I look at the ss-a report it indicates the heating load. I have entered the hot deck temp, zone entering temp, a preheat coil. Any suggestions would be appreciated.
Thanks,
Matthew J. Baron
[cid:image001.png at 01CE8D05.9E4DBA10]
Wendel, 140 John James Audubon Pkwy, Suite 201, Buffalo, NY 14228
p 716.688.0766 f 716.625.6825 e mbaron at wendelcompanies. com w wendelcompanies. com
ARCHITECTURE ENGINEERING PLANNING ENERGY SERVICES CONSTRUCTION MANAGEMENT
CONFIDENTIALITY NOTICE: This email transmission is confidential and is intended only for the person(s) named above. Its contents may also be protected by privilege, and all rights to privilege are expressly claimed and not waived. If you have received this email in error, please call us immediately and destroy the entire email. If this email is not intended for you, any reading, distribution, copying or disclosure of this email is strictly prohibited.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130730/3cb07b4e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 3940 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130730/3cb07b4e/attachment-0002.png>
More information about the Equest-users
mailing list