Just to reiterate Nicks point – 1 KBTU/ft2-yr is a REALLY low number – especially for source energy. Site energy typically runs much lower than source energy, and even that is normally an order of magnitude higher.
Vikram Sami
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Monday, June 03, 2013 11:26 AM
To: John Aulbach; Ginnie Schofield; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Equest - Simulation Report BEPS
One extra thought: Your expectation (<1 kBtu/SF/yr) catches my eye immediately…
If I’m not mistaken, only unconditioned warehouses have values under 1.0 for the 2030 challenge EUI targets. I would expect any regularly occupied school to be magnitudes larger.
2030 challenge may not be on your project’s radar, but might serve a useful point of reference for what to expect. Here’s a quick link: www.architecture2030.org/.../2030_Challenge_Targets_National.pdf<http://www.architecture2030.org/.../2030_Challenge_Targets_National.pdf>
Best of luck!
~Nick
[cid:image001.jpg at 01CE6058.04079F40]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Monday, June 03, 2013 11:32 AM
To: Ginnie Schofield; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Equest - Simulation Report BEPS
Yes, please post your files, Ginnie. Otherwise, all is speculation.
John R. Aulbach, PE
From: Ginnie Schofield <GSchofield at edaengineering.com<mailto:GSchofield at edaengineering.com>>
To: "equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>" <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Sent: Monday, June 3, 2013 9:08 AM
Subject: [Equest-users] Equest - Simulation Report BEPS
Equest Users:
I am modeling a school building, and on this BEPS report for baseline run and parametric runs,
the Total Source Energy KBTU/SQFT-YR
Gross-Area and Net-Area number is higher than expected.
Actually, I would expect it to be quite a bit lower in the 0.75 range.
Anyone have some approach I could follow to verify these and what could be driving this
elevated number. I could post INP and PD2 files if necessary.
Any and all suggestions are sincerely appreciated, and thank you in advance.
GINNIE SCHOFIELD
ENGINEERING DESIGN ASSOCIATES
1607 CY Ave, Ste 303, Casper, WY 82604
(Ph) 307-266-5033 (Fx) 307-234-3805
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130603/4d22c595/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130603/4d22c595/attachment-0002.jpg>
More information about the Equest-users
mailing list