[Equest-users] Fw: ERV on OA-From-System Comments from Jeff Hirsch
Paul Diglio
paul.diglio at sbcglobal.net
Mon Jun 3 16:53:37 PDT 2013
Stormy:
In the past when I have modeled just an DOAS that did not have any heating or
cooling capacity with and ERV was to add an ERV to each zone system that the
DOAS fed. I used the same kw/cfm that the DOAS system had. So I chopped up the
DOAS with it's ERV into smaller ERV's on each system. This seemed to work good.
The problem with the project that I am working on now, is that the DOAS feeds
chilled beams. The DOAS chilled water coil and heating coil is sized in the
design with the assumption that and ERV is conditioning the outside air. The
DOAS has to dehumidify the air because the chilled beams cannot remove moisture
as there is no provision for condensate removal. If I remove the ERV from the
DOAS, the chilled and hot water coils are not large enough to condition the OA
before it reaches the ERV on the chilled beams and I can't add a chilled or hot
water coil to the ERV's on the chilled beams. So I loose the additional
heat/cool capacity designed into the DOAS.
Confusing.
Regards,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
________________________________
From: Stormy L. Shanks <shankssl at kjww.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>
Sent: Mon, June 3, 2013 7:15:24 PM
Subject: RE: [Equest-users] ERV on OA-From-System Comments from Jeff Hirsch
Wow, thank you for sharing that. That’s definitely a bummer. I just did a test
on a model that I did with DOAS where I had defined an ERV in the DOAS system.
I deleted the ERV from the system, and my energy was lower than when the ERV was
included. Not good. I should have known better. I suppose I will start modeling
ERV/DOAS settings in spreadsheets outside of eQUEST. Or in other software.
Stormy L. Shanks, PE
Mechanical Engineer
2882 106th St, Des Moines, IA 50322
D 515.334.4315
web | Facebook | Twitter | LinkedIn
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Monday, June 03, 2013 5:17 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] ERV on OA-From-System Comments from Jeff Hirsch
Just wanted to share an e-mail from Jeff. I did not know that an ERV on a
OA-From system was not supported by eQuest. That explains why I could never get
the correct airflows on this type of design.
Unfortunately almost every project I work on does specify a VAV DOAS with an ERV
to supply ventilation air to some type of HVAC system, such as VRF indoor coils,
chilled beams or PTHP units. I will have to try the work around Jeff suggested.
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
----- Forwarded Message ----
From: Jeff Hirsch <James.J.Hirsch at gmail.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>
Sent: Mon, June 3, 2013 12:17:58 PM
Subject: Re: [Equest-users] OA From System Question
Setting your OA system (ERU1) to be vav and having the ERV on it will not work
correctly. If you need ERV you must place your ERV in the IU system and use
that system to supply the conditioned OA. ERV on a OA-FROM system is not
supported. VAV on an OA-FROM system is possibly not what you want but I cannot
tell what you are trying to do. An IU system has a central constant volume air
supply with each zone then having zone coil to do the zone thermostat
controlled conditioning via room air flow induced as a constant ratio supply air
fro the IU (the induction-ratio). So it seems you can use the IU system as your
ERU system supplying the zones. If there is some other reason you used an
OA-FROM system, then perhaps my suggestions don’t apply, but the ERV and VAV
comments always apply.
________________________________
Jeff Hirsch
James J. Hirsch & Associates
12185 Presilla Road - Camarillo, CA 93012-9243 USA
phone: (805) 553-9000 mobile: (805) 532-1045 fax: (805) 532-2401
email: James.J.Hirsch at gmail.com
From:Paul Diglio
Sent:Monday, June 03, 2013 6:11 AM
To:equest-users at lists.onebuilding.org
Subject:[Equest-users] OA From System Question
Morning:
I am trying to model a chilled beam system as induction units. The primary air
is supplied by an ERU. I set the outside air to 0 on the chilled beams HVAC
systems tab.
In the chilled beam zone tab I set the outside air to the primary CFM and the
overall CFM to the induced air flow.
Per the eQuest help menu, "The sum of the OA requirements for all SYSTEMs that
reference an OA-FROM-SYSTEM is used to set the referenced OA-FROM-SYSTEM value
for MIN-OUTSIDE-AIR, SUPPLY-FLOW as well as adjust the referenced OA-FROM-SYSTEM
directly served ZONE maximum and minimum flows for both heating and cooling."
But per my hourly reports, the ERU is not supplying the necessary amount of
primary air and in the summer the ERU flow drops to .01 CFM.
Attached are the project files. Any ideas?
Thank you,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________
This message and any attachments contain information intended for a specific
party and may include sensitive or confidential material. If you are not the
intended recipient, please do not read, copy, use, or disclose to others.
Please notify the sender of the delivery error by reply and then permanently
delete this message and all attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130603/112a0fa2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 9229 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130603/112a0fa2/attachment-0002.png>
More information about the Equest-users
mailing list