[Equest-users] zones/hvac system assignments
Nick Caton
ncaton at smithboucher.com
Fri Jun 14 10:54:01 PDT 2013
Hi everyone,
The detailed mode procedure for removing and rearranging parent/child components applies to many other instances. Here's a visual guide for common reference:
To achieve your intent in the wizards:
1. First, select something other than "system per zone" in the first screen for both HVAC systems. I use "system per site" when I expressly do not a system replicated:
[cid:image002.png at 01CE68F7.051EABB0]
2. After all your systems are defined, for all shells, navigate to the "Zone Group Definitions" input screen to group your zones as intended, and also assign them to the intended system. As you're describing, you should create 2 zone groups to reflect the intended split, then remove the default zone groups, then be sure you've assigned the intended system to each zone group on this screen.
[cid:image001.png at 01CE68F7.77C6C850]
To correct in detailed edit mode:
1. Identify which systems you want to keep - I'd personally assign those systems to remain identifiable names at this point:
[cid:image004.png at 01CE68F8.563030E0]
2. Re-assign the parent system for all zones under systems you don't want to keep to the appropriate system. You can do this by either double-clicking the zones in the component tree, or also via the spreadsheet view. Upon changing this input, you'll find the component tree to the left re-arranges to slot the revised zone under the newly-assigned parent system. If needed, the "Zone Locations" graphic in the Air-Side HVAC System tab can assist with determining where any selected zone in the tree is located in the shell.
[cid:image005.png at 01CE68F8.C01FCA10] and/or[cid:image006.png at 01CE68F8.C01FCA10]
Result: [cid:image007.png at 01CE68FA.97001200]
3. Finally, right click the systems in the component tree you want to get rid of (they should have no child zones), and delete them. This is not an optional step - you'll run into errors trying to simulate if you leave them in. Note this right-click context menu from the component tree is also a means to create/copy/link systems and other components, in detailed mode. You should explore the possibilities if you haven't already before removing the unintended systems completely.
[cid:image008.png at 01CE68FA.97001200] [cid:image009.png at 01CE68FA.97001200]
Hope this helps - plenty of related discussions are available in the mailing list archives, for further reading.
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kent Beason
Sent: Friday, June 14, 2013 8:21 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] zones/hvac system assignments
In the attached you will see a simple building which is (supposed to be) served by just two HVAC systems, each serving one-half the building. In DD wizard, I defined only two systems accordingly, however you will see how the four zones on one half of the building each have separate systems (referencing model tree on left), whereas the red highlighted zone is on the same system as the four other zones on that half of the building as intended. How do I get the four zones on the other half of the building assigned to the same system in DD edit (and then delete the other three HVAC systems)?
Kent Beason
-------------------------
office - 903 581 2291
cell - 830 609 8904
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Tuesday, June 11, 2013 2:47 PM
To: John Aulbach; Kent Beason; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] zones/hvac system assignments
Hi Kent,
Another approach could be to have 2 instances of eQuest open - one looking at your wizard level zonal names/inputs for reference only, and the other open to a separate "working" detailed model (these being 2 separate project files). Multiple monitors makes this sort of exercise notably simpler.
For the detailed model, I'd suggest navigating to the airside HVAC tab, and from here you can double click on systems and zones to rename as you wish to. Note that highlighting a zone on the left will highlight the corresponding zone in the 2D zone window. Between these visuals, you can almost certainly figure out which is which in 9 out of 10 cases. If you have lots of shells, multiple floors, or other contributing factors making this tricky, you can navigate over to the space tab to review where spaces are from the 3D view as needed.
Lots of ways to skin this cat. For future reference, I too only very rarely invest time trying to name stuff in the wizards, as very little carries forward into detailed mode (note some prefix/suffix options that are of use for shells and systems however). Naming of stuff basically happens in detailed edits, to the extent needed.
Hope this helps too!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Tuesday, June 11, 2013 12:06 PM
To: Kent Beason; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] zones/hvac system assignments
Hi Kent:
Unfortunately, the wonderful names you established in the Wizard do not translate into the Detailed Edit mode. You will need to rename them in the Detailed edit Mode (always save a copy of your Wizard Mode in case you need to recreate). To figure out which zone and HVAC systems are which in Detail, go back to Wizard and take a screen shot (or sketch) the shapes of your zones (with names). Go to the Detail Edit mode and gp to a zone and ompare the shape to your Wizard mode. Now you can retype the name into the Detail mode.
Just the way it is. Good luck.
John R. Aulbach, PE
From: Kent Beason <kbeason at estesmcclure.com<mailto:kbeason at estesmcclure.com>>
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Sent: Tuesday, June 11, 2013 8:58 AM
Subject: [Equest-users] zones/hvac system assignments
I have an existing building that has been renovated and expanded. The existing area and new addition area are basically an open area with only a service counter separating the two areas (new pharmacy). The existing HVAC system is left in place to serve the existing floor area, and the addition is getting a new system. There are two restrooms; one served by the existing HVAC, and the other served by the new HVAC. An elec/data room has its own little mini-split, and one other room has a unit heater. So this brings a total of four different HVAC systems. I defined these systems in the DD wizard, and wasn't able to utilize the zone assignments screen after drawing new zones to coincide with these systems and different occupancy types, so I intended to finish assigning zones in detailed edit. I did not separate existing floor area vs new area since it is open area. After defining the HVAC four systems in the DD wizard, I can't seem to find any trace of them in detailed edit. Where do I best define these six thermal zones and HVAC systems?
Kent Beason
Estes, McClure & Associates, Inc.
3608 West Way
Tyler, TX 75703
-------------------------
office - 903 581 2721
cell - 830 609 8904
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 35567 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 36255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 20558 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 35585 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0019.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 85748 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0020.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 88231 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0021.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 38718 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0022.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 28199 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130614/9141a4d5/attachment-0023.png>
More information about the Equest-users
mailing list