[Equest-users] Modeling site obstructions for EAp2c1
Cam Fitzgerald
cam at energyopportunities.com
Thu Mar 21 03:33:35 PDT 2013
Good morning, all,
The ASHRAE User's Manuals are generally well accepted supplements to the
standards and should be uses as long as its guidance does not directly
contradict the standard or official guidance offered by GBCI in the form of
interpretations. You should look at ASHRAE 90.1-2010. I believe a new
section to Table G3.1 (#14) which describes the modeling protocol for
shading from site features. I am not certain if this was an addendum item
for 90.1-2007. If it is, you should indicate which addendum you are
applying. If not, you should just indicate what guidance you are following
and cite the more recent version of the standard. If you follow this
guidance you should be fine.
Hope this helps.
Cam Fitzgerald
Energy Opportunities/a 7group company
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Wednesday, March 20, 2013 4:55 PM
To: Demba Ndiaye; Arpan Bakshi
Cc: equest-users
Subject: Re: [Equest-users] Modeling site obstructions for EAp2c1
Arpan & others:
In my experiences with the LEED reviewership (your mileage may vary), I have
found the User's manual to be at least as solid a source for citation as the
90.1 Standard itself, for a variety of topics. If I recall correctly,
reviewers have in fact cited the User's Manual on occasion within their
commentary.
I have not as of yet attempted modeling adjacent buildings or other
permanent shading elements for a LEED submission, but it seems the User's
Manual is clear enough: model any such remote shading sources identically
in both models, if at all. An extra nuance to consider however is how you
handle the baseline rotations (assuming LEED-NC here) in regards to those
exterior elements. I would be sure to touch on that for your EAp2
documentation. Intuitively, I would expect such elements should not rotate
with the building, in the spirit of substantiating the "site orientation"
decision-making, which may (or may not) require some additional legwork
beyond the usual simple baseline parametric runs.
IF such shading demonstrates a legitimate improvement in the proposed design
relative to the baseline averages (I wouldn't count on it for all cases),
AND the shading sources in question are at least as permanent as the
building itself (i.e. other buildings, a sheer cliff face, etc. - something
more transient like trees/foliage I would feel dubious about) I'd give it a
shot, with care to document your procedure very clearly, including the
User's Manual citation.
Worst case scenario: Reviewer tells you to remove them in their technical
advice - live & learn (and let us know!) ;)
Regards,
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Demba
Ndiaye
Sent: Wednesday, March 20, 2013 3:19 PM
To: Arpan Bakshi
Cc: equest-users
Subject: Re: [Equest-users] Modeling site obstructions for EAp2c1
Arpan,
The User's Manual seeks to explain the intent of the Standard. I see no
wording related to neighboring buildings in the applicable sections of the
Standard, meaning it does not regulate this aspect, and consequently the
Baseline should not be penalized if deciding to model neighboring building
effects.
From: Arpan Bakshi [mailto:arpanbakshi at gmail.com]
Sent: Wednesday, March 20, 2013 2:27 PM
To: Demba Ndiaye
Cc: equest-users
Subject: Re: [Equest-users] Modeling site obstructions for EAp2c1
Demba, unfortunately, the User's Manual cannot be used as the word of the
rating authority. It would need to be cited somewhere in the Standard, or in
a ruling by the GBCI.
Arpan Bakshi LEED AP BD+C, ESTIDAMA PQP
On Wed, Mar 20, 2013 at 2:25 PM, Demba Ndiaye <Demba.Ndiaye at setty.com>
wrote:
Arpan,
The 90.1-2007 User's Manual clearly states (page G-15):
"Shading of the building by surrounding structures and topography should be
modeled identically in both the proposed and baseline buildings."
Which confirms what you have grasped.
Regards,
S&A LogoDemba Ndiaye, Ph.D., P.E., LEED AP BD+C, BEMP
Senior Energy Analyst/Mechanical Engineer
Setty & Associates, Ltd.
MEP Design Engineering | Project Management
|Construction Management | Design-Build Services | Commissioning
|3040 Williams Drive, Suite 600 | Fairfax, VA 22031
|Voice 703.691.2115 | Fax 703.691.8084 | cell 571.830.9913
demba.ndiaye at setty.com | www.setty.com <http://www.setty.com/>
This e-mail and any files transmitted with it are confidential and are
intended solely for the use of the individual or entity to whom they are
addressed. If you are NOT the intended recipient or the person responsible
for delivering the e-mail to the intended recipient, be advised that you
have received this e-mail in error and that any use, dissemination,
forwarding, printing or copying this e-mail is strictly prohibited.
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Arpan
Bakshi
Sent: Wednesday, March 20, 2013 12:53 PM
To: equest-users
Subject: [Equest-users] Modeling site obstructions for EAp2c1
All,
I have learned through informal conversations that modeling site
obstructions from (surrounding buildings) is fine by GBCI, so long as there
is consistency and the same approach is taken in both Baseline and Proposed
models, i.e. either both models include surrounding buildings, nor neither
does.
Is there a CIR or other reference anyone is familiar with which records this
guidance, which can be cited?
Thanks.
Arpan Bakshi LEED AP BD+C, ESTIDAMA PQP
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130321/d5e058fc/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130321/d5e058fc/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 167 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130321/d5e058fc/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2912 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130321/d5e058fc/attachment-0005.jpeg>
More information about the Equest-users
mailing list