[Equest-users] Baseline Fan power calculation
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Mar 25 09:40:04 PDT 2013
Hi Robert,
I apologize for confusing motor efficiency with fan mechanical efficiency. Since section 6.5.3.1 describes the maximum allowable fan power, we can expect it to use conservative allowances for mechanical efficiency and static pressure. Using the allowance for bhp (bhp ≤ CFMS*0.00094 + A) and neglecting the pressure drop adjustments (A), we can determine static pressures (SP) for a range of mechanical efficiencies by setting 0.00094 = SP/(6356xefficiency). Using a range of mechanical efficiencies from 0.4 to 0.6 (ASHRAE Pocket Guide, 7th ed. p. 246), we get a range of static pressures from 2.4" to 3.6" w.g. That's higher than your 0.5", but seems reasonable to me for determining max allowable fan power.
Regards,
Bill
William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: RobertWichert [mailto:robert at wichert.org]
Sent: Monday, March 25, 2013 12:17 PM
To: Bishop, Bill
Cc: Nick Caton; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Fan power calculation
Thanks Bill,
I verified that the references you gave lead to the result of the calculation in the spreadsheet, but if the theoretical calculation below has any validity at all, the assumed fan efficiency in 90.1 is about 8%. I used a fan static pressure rise of .5 in. H2O.
So, this fan efficiency seems a little low to me.
You said "Fan efficiency is from ASHRAE 90.1, Table 10.8 as described in G3.1.2.9." but Table 10.8 is Fan Motor efficiency, which is about 85%. I have no problem with that, but to use the theoretical fan power equation I need the Fan efficiency. Do you have any idea what fan efficiency is assumed in 90.1?
I also notice that the fan power calculation in 90.1 does not include a pressure rise component, which I find odd. Is the pressure rise across the fan assumed somewhere? From the checks described above, it appears to be about .5 in. H2O. Does this seem reasonable?
Your thoughts?
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 3/25/2013 8:01 AM, Bishop, Bill wrote:
Robert,
I'm sure Nick is typing furiously as I write this, but I'll probably finish before him.
Taking a quick look at the spreadsheet that Nick attached to his email, it calculates baseline fan power using the method described in Appendix G and 6.5.3.1.1. Fan efficiency is included in the Pfan calculation per G3.1.2.9.
Fan efficiency is from ASHRAE 90.1, Table 10.8 as described in G3.1.2.9.
Regards,
Bill
William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of RobertWichert
Sent: Monday, March 25, 2013 10:52 AM
To: Nick Caton; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Baseline Fan power calculation
I believe I have written about this in the past, but since this seems to be on-topic, I'll bring it up again.
The theoretical fan power equation, Fan BHP = (cfm x static press "w.c.) / (6356 x fan efficiency) can be used to calculate the theoretical fan BHP, but you need the fan efficiency. This seems to be NOT the way the BHP is being calculated by the spreadsheet that was attached previously.
Is there a reason for that?
Was there an assumed fan efficiency used in the spreadsheet, and was it based on anything particular, or just a conservative assumption?
Thanks!
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 3/25/2013 7:34 AM, Nick Caton wrote:
Hi Vamshi,
I advise carefully reviewing the footnotes under Table 6.5.3.1.1A, which include procedure for determining baseline fan power adjustments.
1. Pfan represents the sum power of all fans in a given baseline system (with exception to baseline systems #6/#8, fan powered VAV boxes).
2. Again, there is not a separate supply/return power calculation (see answer #1). You can however account for adjustments present in separate airstreams from the proposed design.
3. Probably not. Review the difference between CFMS and CFMD carefully at the cited Table. A CFM quantity representing the airflow each element encounters (CFMD) should be applied against each pressure drop adjustment, not an 'aggregate' of supply+return.
You may also find the attached resource published by 7group helpful to cement your procedural understanding of how to arrive at the sum total for "A."
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of vamshi ranga
Sent: Monday, March 25, 2013 8:17 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Baseline Fan power calculation
Hi All,
I have a doubt regarding calculating fan power as per ASHRAE 90.1-2007.
My proposed system has, supply return and exhaust fans separately with kW and cfm mentioned for each fan.
So, for calculating baseline fan power,
1. should I calculate it separately for each fan type?
2. can I take pressure drop adjustment both in supply and return fan power calculation?
3. should I sum all the cfms of supply, return and exhaust and than apply pressure drop adjustments to aggregated cfm.
Kindly help me out in solving the doubt. If you have any example fan power calculations, or web links those could guide me regarding this, plz do share them.
Thanks in advance.
Regards,
Vamshi.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130325/0795bed3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130325/0795bed3/attachment-0002.jpg>
More information about the Equest-users
mailing list