[Equest-users] Another DCV question - when to claim credit per G3.1.2.5?
Bishop, Bill
bbishop at pathfinder-ea.com
Mon May 20 16:02:56 PDT 2013
[This is a LEED/Appendix G question - not an eQUEST-specific issue. My apologies if this has been answered before. I didn't see it in the archives.]
Can a proposed design claim credit for DCV if DCV is not required for the proposed design per 6.4.3.9, even though DCV would be required for the baseline under the same criteria?
Proposed designs modeled for LEED and/or Appendix G can claim credit for reduced ventilation rates per the exception to ASHRAE Standard 90.1, G3.1.2.5.
The exception is "When modeling demand-control ventilation in the proposed design when its use is not required by Section 6.4.3.8." [The typo appears in App. G. 2007 - should be "6.4.3.9".]
My proposed design does not require DCV per 6.4.3.9, because all of the systems that serve spaces meeting the DCV requirement also have energy recovery, which is exception (a.) for 6.4.3.9.
Therefore, I would argue that the proposed design can claim credit for DCV.
However, none of the baseline systems that serve the same spaces meet the G3.1.2.10 requirement for energy recovery. The baseline systems do not meet any of the exceptions to 6.4.3.9.
Does the exception to G3.1.2.5 imply "...when its use is not required in either the proposed or baseline design"?
I'm hoping not, otherwise this is a blue Monday<http://www.youtube.com/watch?v=FYH8DsU2WCk>. Tell me how you feel.
Thanks,
Bill
William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130520/6257fa46/attachment.htm>
More information about the Equest-users
mailing list