[Equest-users] How to delete a floor in eQuest model in detail design mode.
Nick Caton
ncaton at smithboucher.com
Tue May 21 06:54:38 PDT 2013
Hi Ankit,
Shell (floor) multipliers in wizard mode manifest in the detailed mode under building shell tab - double click the shell in the component tree to edit:
[cid:image001.png at 01CE553D.10ED8290] --> [cid:image003.png at 01CE553E.9A4D8CF0]
Worth noting: wizards can also introduce shell multipliers if you have multi-story shells and don't un-tick the "use multipliers" box that pops up.
Also, when you double click a space in the tree, the "floor multiplier" input there mirrors the parent shell's multiplier by default (green text). Revising the parent shell multiplier value per above will in turn correct all its child spaces if you haven't manually entered something else. Manually editing the space multipliers (red text) overrides the shell multiplier, should you have cause to maintain a multiplier for select spaces.
[cid:image004.png at 01CE553F.B36DEF30]
Hope this helps!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ankit.Anil.Gupta at jci.com
Sent: Monday, May 20, 2013 8:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] How to delete a floor in eQuest model in detail design mode.
Hi,
I have build a model for LEED compliance using a multiplier option in eQuest, now by mistake my multiplier went wrong resulting in one excess floor in each wing of building.
So can anyone guide me to delete a floor eQuest model in detail design wizard mode.
Thanks
Ankit
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130521/29f0e397/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8683 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130521/29f0e397/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130521/29f0e397/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 31831 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130521/29f0e397/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 25747 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130521/29f0e397/attachment-0008.png>
More information about the Equest-users
mailing list