[Equest-users] Another DCV question - when to claim credit per G3.1.2.5?
Daniel Knapp
danielk at arborus.ca
Tue May 21 07:12:08 PDT 2013
Hi Bill,
You can model DCV for credit in the Proposed design. I believe the procedure is to model the Proposed as designed and to model the Baseline to ASHRAE 62 in those zones that have DCV. Also, you need to make sure that the DCV sensors are in the zones and not in the return ducts for multi-zone systems.
Cheers,
Dan
—
Daniel Knapp, PhD, P Phys, LEED® AP O+M
danielk at arborus.ca
Arborus Consulting
Energy Strategies for the Built Environment
www.arborus.ca
76 Chamberlain Avenue
Ottawa, ON, K1S 1V9
Phone: (613) 234-7178 ext. 113
Fax: (613) 234-0740
On 2013-05-20, at 7:02 PM, "Bishop, Bill" <bbishop at pathfinder-ea.com> wrote:
> [This is a LEED/Appendix G question – not an eQUEST-specific issue. My apologies if this has been answered before. I didn’t see it in the archives.]
>
> Can a proposed design claim credit for DCV if DCV is not required for the proposed design per 6.4.3.9, even though DCV would be required for the baseline under the same criteria?
>
> Proposed designs modeled for LEED and/or Appendix G can claim credit for reduced ventilation rates per the exception to ASHRAE Standard 90.1, G3.1.2.5.
> The exception is “When modeling demand-control ventilation in the proposed design when its use is not required by Section 6.4.3.8.” [The typo appears in App. G. 2007 – should be “6.4.3.9”.]
>
> My proposed design does not require DCV per 6.4.3.9, because all of the systems that serve spaces meeting the DCV requirement also have energy recovery, which is exception (a.) for 6.4.3.9.
> Therefore, I would argue that the proposed design can claim credit for DCV.
> However, none of the baseline systems that serve the same spaces meet the G3.1.2.10 requirement for energy recovery. The baseline systems do not meet any of the exceptions to 6.4.3.9.
>
> Does the exception to G3.1.2.5 imply “…when its use is not required in either the proposed or baseline design”?
> I’m hoping not, otherwise this is a blue Monday. Tell me how you feel.
>
> Thanks,
> Bill
>
> William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
> Senior Energy Engineer
>
> 134 South Fitzhugh Street Rochester, NY 14608
> T: (585) 325-6004 Ext. 114 F: (585) 325-6005
> bbishop at pathfinder-ea.com www.pathfinder-ea.com
> P Sustainability – the forest AND the trees. P
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list