[Equest-users] Is there a way to extract specific data from sim result?
Joe Huang
yjhuang at whiteboxtechnologies.com
Wed May 22 18:11:01 PDT 2013
Ivan,
After sending my previous post, I realized that the example sshF.awk script actually did
not search for the report title and count lines, but rather just picked out the exact
lines because they had unique patterns ( 0TOTAL, 0MAX). Therefore, I'm attaching this
time two other awk scripts, one that picks out the total annual heating and cooling energy
consumptions from the SS-F report, which counts lines, and another that picks out the
annual end-uses from the BEPS report, which doesn't count lines but looks for the end-use
names. I think those show better the "technique" that I use to extract data from
DOE-2/eQUEST *.OUT/*.SIM files.
To run these awk scripts, you need of course a copy of awk, of which there are many
version freely available on the Web. Then, to run it on a file, just type in a command
line terminal:
awk -f [awk script name] [any options] = [option name] [name of file to be
processed] > [name of output file]
If "> [name of output file]" is left off, the result will just appear on the monitor.
For example, If you were to run ssf.awk to get total annual loads, type
awk -f ssf.awk yourfile.SIM > yourfile.SSF
If you want the loads normalized per square foot, type
awk -f ssf.awk o=sf yourfile.SIM > yourfile.SSF.a
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 5/22/2013 5:35 PM, Yf Sun wrote:
> Hi Joe
>
> Im trying to do configuration perturbation analyse like you and your colleague did
> before, there's large amount of simulations to do and thats why i need to automate some
> data process, finally i got a solution from the specialist like you.
>
> Thanks!
>
>
> On Wed, May 22, 2013 at 11:33 PM, Joe Huang <yjhuang at whiteboxtechnologies.com
> <mailto:yjhuang at whiteboxtechnologies.com>> wrote:
>
> As others have pointed out, eQUEST runs DOE-2.2 which outputs a text file originally
> renamed *.OUT in DOE-2 but now renamed *.SIM in eQUEST. As a long-time DOE-2 user,
> I've written lots of awk scripts to extract out the variables of interest from the
> *.OUT/*.SIM files. In fact, I only look at the *.OUT/*.SIM file during the
> debugging phase of a project, or when some results look suspicious.
>
> I don't know how many people still use awk, but I've found it absolutely
> indispensible in my work (no exaggeration). Basically, awk is a scripting language
> with C-like syntax, but more contextual than formal languages like C or Fortran,
> i.e., you don't have to define variable types, set array sizes, etc.
>
> When I use awk to extract data from a *.OUT/*.SIM file, I basically do a pattern
> search for the title of the report (SS-A, SS-H, etc.), and when I find it, I start
> counting lines. Then, when I get to the correct line number, I pull out the
> variables of interest, which in awk are simply the strings with a blank as the
> "field separator". I've done this so many times that it takes me only a few minutes
> to write an awk script for what you're trying to do. For your info, I'm attaching
> a sample awk script that I use to pull out the heating and cooling loads and peak
> loads from an SS-H file.
>
> Awk has been around since the 1980's. I'm sure you can do the same with Ppython,
> Perl, VB, etc., but I've never felt the need because awk worked so well for me.
>
> Joe
>
>
> On 5/21/2013 6:48 PM, Yf Sun wrote:
>> Hi,dear Equesters!
>> Im currently doing my ph.d research using equest to analyse building energy
>> performance, i found its time consuming to find the data i need from sim result, as
>> the data i need almost the same for every simulation, do you know a way to extract
>> the specific text data(for importing to excel) quickly by using some third party
>> program maybe?
>>
>> --
>> Best regards
>> Ivan
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> --
> Best regards
> 孙一峰
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130522/a931cec9/attachment-0002.htm>
-------------- next part --------------
An embedded and charset-unspecified text was scrubbed...
Name: ssf.awk
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130522/a931cec9/attachment-0002.txt>
-------------- next part --------------
An embedded and charset-unspecified text was scrubbed...
Name: beps.awk
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130522/a931cec9/attachment-0002.asc>
More information about the Equest-users
mailing list