[Equest-users] Fwd: I got 26% OF HOURS OUTSIDE OF THROTTLING RANGE after rotating my model by 5 degrees?
Yf Sun
caselysun at gmail.com
Wed May 22 23:19:29 PDT 2013
here i attached the reports for 10,15,20 degree azimuths respectively!
On Thu, May 23, 2013 at 2:16 PM, Yf Sun <caselysun at gmail.com> wrote:
> Hi Joe
> I also suspected that the under cooled hours may caused by window angular
> property, but the loads reports you indicated show there's no big swing on
> the solar heat gain for 15 degree azimuth compared to 10 and 20 degrees
> azimuth, however i found there's a great difference in peak system cooling
> load in SS-J reports, the peak load for 15 azimuth is about a half of the
> load for 10,20 azimuth, so I guess the DOE program may uncorrectly
> calculated the system peak load?but when i used your weather file for
> simulation the unmatch hours disappeared!
>
>
> On Thu, May 23, 2013 at 1:01 PM, Joe Huang <
> yjhuang at whiteboxtechnologies.com> wrote:
>
>> 孙一峰,
>> Ivan 是不是你的英文名字?
>> The only difference between the different azimuths is the solar
>> radiation.
>> I think you should compare the summary loads report (LS-E by space, or
>> LS-F for the whole building) for the different orientations and see how
>> much the solar heat gains, especially through the windows, change. If you
>> really want to get into it, you can also print out hourly reports for the
>> solar heat gains, heating and cooling loads for the ground floor zones.
>> You can also switch weather files and see what happens. I will send you by
>> e-mail a different weather file for Wuhan that I've created.
>> Good luck.
>>
>> Joe
>>
>> Joe Huang 黄昱
>> White Box Technologies, Inc.
>> 346 Rheem Blvd., Suite 108D
>> Moraga CA 94556
>> yjhuang at whiteboxtechnologies.com
>> http://weather.whiteboxtechnologies.com
>> http://www.whiteboxtechnologies.com
>> (o) (925)388-0265
>> (c) (510)928-2683
>> "building energy simulations at your fingertips"
>>
>>
>>
>>
>> On 5/22/2013 7:02 PM, Yf Sun wrote:
>>
>> Hi dear equesters!
>> I was doing orientation study on my office module i can not figure out
>> why i got 26% OF HOURS OUTSIDE OF THROTTLING RANGE in BEPU report when i
>> set the azimuth at 15 degrees for ground floor, the system worked in
>> throttling range when azimuth at 10 or 20 degrees! the weather file i used
>> is CTYW Wuhan (china).
>>
>> I attached the model, reports and the weather file. Any help will be
>> appreciated!
>>
>>
>> --
>> Best regards
>> 孙一峰
>>
>>
>> _______________________________________________
>> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
>
> --
> Best regards
> 孙一峰
>
--
Best regards
孙一峰
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130523/69cd99be/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 10.sim
Type: application/octet-stream
Size: 604371 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130523/69cd99be/attachment-0006.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 15.sim
Type: application/octet-stream
Size: 604371 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130523/69cd99be/attachment-0007.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20.sim
Type: application/octet-stream
Size: 604371 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130523/69cd99be/attachment-0008.obj>
More information about the Equest-users
mailing list