[Equest-users] Cooling EIR and Supply Fan Energy broken down forPVAV w/ PFP (System 6)
赵永青
503271081 at qq.com
Mon May 27 01:54:46 PDT 2013
Tabel 6.8.1 B Electrically Operated Unitary and Applied Heat Pumps―Minimum Efficiency Requirements
Equipment
TypeSize CategoryHeating
Section TypeMinimumEfficiencya
Cooling ModeHeating Mode
Air cooled<19 kWcElectric resistance3.81(SCOP)
13.0(SEER)2.25(SCOPH)
7.7(HSPF)
≥19 kW and <40 kW3.22(COP)
11.0(EER)3.3(COPH)
≥40 kW and <70 kW3.10(COP)
10.6(EER)3.2(COPH)
≥70 kW2.78(COP)
9.5(EER)
EIR in eQuest detail interface, as follows
Equipment
TypeSize CategoryHeating
Section TypeMinimumEfficiencya
Cooling ModeHeating Mode
Air cooled<19 kWcElectric resistance0.2507(EIR)0.2742(EIR)
≥19 kW and <40 kW0.2580(EIR)0.2728(EIR)
≥40 kW and <70 kW0.2693(EIR)0.2827(EIR)
≥70 kW0.3051(EIR)
PPlease consider the environment before printing this email
保护环境-请在确实需要时再打印此邮件
------------------
祝:身体健康,工作顺利!
长沙绿建节能科技有限公司
赵永青
13808474213
----- Original Message -----
From: Ting Wang
To: equest-users
Date: 2013-05-27, 16:30:10
Subject: [Equest-users] Cooling EIR and Supply Fan Energy broken down forPVAV w/ PFP (System 6)
Dear eQuest folks,
The following comment turned up twice in the preliminary and final design phase review.
The SV-A reports indicates that the cooling efficiencies for the HVAC systems were not correctly reflected in the Baseline model and the supply fan energy has not been broken out as required. The response narrative to the Preliminary Review comment number 1 indicates that the cooling efficiencies were recalculated and then entered in the Wizard; however as stated in the Preliminary Review, eQUEST performs this step automatically between the wizard and detailed interface (for example, a 10.0 EER packaged DX unit with efficiencies entered in the wizard is shown in the detailed interface with a cooling-only EIR of 0.2878 (EER = 11.86)) Section G3.1.2.1 requires that where efficiency ratings, such as EER and COP, include fan energy, the descriptor shall be broken down into its components so that supply fan energy can be modeled separately. Note that the cooling efficiency without the fan power is typically rated higher than when the fan power is included as a component in the rated efficiency If appealing this prerequisite, revise the Baseline model so that fans have been broken out separately from the cooling EIR indicates in the SV-A report.
I attach the sample SV-A and SV-B report below. I modeled this type 6 baseline system using a PIU, which, based on my digging in the archived mailing list, is the closest way to model a VAV system with PFP boxes. The cooling EIR was automatically generated in eQuest assuming the supply fan energy (ARI 340/360) was subtracted from EER 10. Actually, in the previous comment response, I calculated cooling EIR using two approaches found in the archived mails (ARI and non-ARI conditions). But our reviews tended to neglect the narratives and focus on how to confirm the supply fan energy has been broken out per G3.1.2.1, although the SV-B report already showed the modeled PFan.
Any ideas on what additional proof documents I need to provide to meet the reviewer's requirements?
Thanks
--
王 亭
Ting Wang / Environment Consultant
BEIJING EVENDESIGN LTD.
T: +86 10 8776 5074 - 801
M: +86 13910854291
E: wangting.ioz at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130527/bed5b473/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 55452 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130527/bed5b473/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22990 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130527/bed5b473/attachment-0005.jpeg>
More information about the Equest-users
mailing list