[Equest-users] Appendix G Baseline Systems 6 and 8 - supply air temperature controls?
Bishop, Bill
bbishop at pathfinder-ea.com
Thu Nov 21 10:28:23 PST 2013
I also created an input file template for System 6 which could be used for System 8 with some modification. Comments/mods are welcomed.
$ *********************************************************
$ ** **
$ ** Performance Curves **
$ ** **
$ *********************************************************
"G3.1.3.15 VAV Fan Curve fPLR" = CURVE-FIT
TYPE = CUBIC
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.0013, 0.147, 0.9506, -0.0998 )
..
$ *********************************************************
$ ** **
$ ** HVAC Systems / Zones **
$ ** **
$ *********************************************************
SET-DEFAULT FOR ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3 $ Per G3.1.3.14
ZONE-FAN-KW/FLOW = 0.00035 $ Per G3.1.3.14
ZONE-FAN-RATIO = 0.5 $ Per G3.1.3.14
TERMINAL-TYPE = PARALLEL-PIU $ For all zones served by Sys 6 or Sys 8
..
SET-DEFAULT FOR SYSTEM
TYPE = PIU $ For Baseline System 6 and System 8
HEAT-SOURCE = ELECTRIC $ Per Table G3.1.1B and User's Manual p.G-23
ZONE-HEAT-SOURCE = ELECTRIC $ Per Table G3.1.1B and User's Manual p.G-23
HEAT-SIZING-RATI = 1.25 $ Per G3.1.2.2
COOL-SIZING-RATI = 1.15 $ Per G3.1.2.2
COOL-SOURCE = ELEC-DX $ Per Table G3.1.1B
MAX-SUPPLY-T = 92 $ Per G3.1.2.8 (20F above room heat T-Stat
HEAT-SET-T = 62 $ = COOL-MAX-RESET-T plus 1F
MIN-SUPPLY-T = 56 $ Per G3.1.2.8 (20F below room cool T-Stat
COOL-CONTROL = WARMEST $ Per G3.1.3.12
ECONO-LIMIT-T = 70 $ Per G3.1.2.7 and Table G3.1.2.6B by climate zone
ECONO-LOCKOUT = YES $ (Seems like a reasonable baseline default)
COOL-MIN-RESET-T = 56 $ = MIN-SUPPLY-T
RESET-PRIORITY = AIRFLOW-FIRST $ Per G3.1.3.12 and G3.1.3.14
COOL-MAX-RESET-T = 61 $ Per G3.1.3.12 (5F above MIN-SUPPLY-T)
OA-CONTROL = OA-TEMP $ Per G3.1.2.6 and Table G3.1.2.6A
FAN-CONTROL = FAN-EIR-FPLR $ Per G3.1.3.15
NIGHT-CYCLE-CTRL = CYCLE-ON-ANY $ Per G3.1.2.4
FAN-EIR-FPLR = "G3.1.3.15 VAV Fan Curve fPLR" $ Per G3.1.3.15
REHEAT-DELTA-T = 36 $ = MAX-SUPPLY-T minus MIN-SUPPLY-T
..
$ Bill
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Thursday, November 21, 2013 1:14 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Appendix G Baseline Systems 6 and 8 - supply air temperature controls?
ASHRAE Standard 90.1, G3.1.3.12 requires cooling supply air temperature reset for Systems 5 through 8.
G3.1.3.14 requires "supply air temperature setpoint shall be constant at the design condition" for Systems 6 and 8.
How should we interpret this and model it in eQUEST (for Systems 6 and 8)?
If the "design condition" in G3.1.3.14 means "peak design flow rate", I suggest the following cooling control settings:
- COOL-CONTROL = WARMEST
- COOL-MIN-RESET-T = 56 $ (assumes 76F cooling T-stat; 56F MIN-SUPPLY-T for 20F difference per G3.1.2.8)
- RESET-PRIORITY = AIRFLOW-FIRST
- COOL-MAX-RESET-T = 61 $ (5F reset per G3.1.3.12; assumes 76F cooling T-stat)
Using a RESET-PRIORITY of "TEMP-FIRST" resets the supply air temperature before the airflow, which does not satisfy the G3.1.3.14 requirement.
Using a RESET-PRIORITY of "TEMP-FIRST" or "SIMULTANEOUS" does not satisfy the G3.1.3.12 requirement, since temperature is reset well before minimum cooling load conditions are reached.
Does anyone have an alternative/additional suggestion or interpretation?
Thanks,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[webCertified_logo_colorRGB72DPI.jpg]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131121/788365f6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131121/788365f6/attachment-0002.jpg>
More information about the Equest-users
mailing list