Has anyone encountered the following problem?
DD wizard incorrectly assigns the return path to "DUCTED" for "PACKAGED DX
PARALLEL FAN-POWERED VAV W/ ELEC REHEAT".
We discovered this problem after only changing "RETURN AIR PATH" from
default "DUCTED" to "PLENUM" and then reviewing the SS-J report to find the
SQFT/Ton is 2x what it should be (968 ducted vs. 526 plenum).
Please let me know your feedback ASAP.