[Equest-users] 3-D Geometry Lost
Sheila Sagerer
sheila at energyopportunities.com
Tue Oct 8 15:58:57 PDT 2013
Good evening Everyone,
The following procedure usually solves the problem without fooling with the
.pd2 file:
Create a brand new project in the wizard. It does not matter what the new
project looks like or what info is in it. The new project can be all
defaults!!! Just MAKE SURE YOU HAVE THE CORRECT WEATHER FILE!!! Once the
wizard has created the new project, change the project from wizard mode to
detailed mode. Save the project with a new name. Close the project.
In Windows Explorer, open the .inp file for the project which has lost the
3D view in Wordpad. Under the Edit tab, Select all and copy. Then open the
newly created .inp file as a text file also in Wordpad , select all, and
paste the original project data into the newly created .inp file; i.e.
overwrite the entire file. Save the .inp file. Close, then open the new file
in eQuest. The 3D picture should be there.
For future prevention:
The main issue which results in a lost 3D usually occurs in large projects
when a lot of editing is taking place. I am not exactly sure why, but I
think it occurs when the RAM is used up. eQuest will use every bit of RAM
available on your computer!!! As a result, I make a habit of SAVING every 5
minutes in large projects, and rebooting every hour or so. If the 3D picture
disappears, IMMEDIATELY close eQuest WITHOUT SAVING! If you save, you will
lose the 3D. If you have not saved, reboot your computer, reopen the
project, and the 3D is usually there, but you will have lost any edits made
since the last save. It’s a toss-up: either save the 3D or save the most
recent edits
Good luck and have a nice evening.
Sheila Sagerer
Energy Engineer, EIT, LEED AP
Energy Opportunities, Inc, a 7group company
Phone: 717-880-9069
<http://www.sevengroup.com/> www.sevengroup.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, October 08, 2013 6:22 PM
To: Juan Carlos Lopez; 'Adam Towell'; equest-users at lists.onebuilding.org;
'Thulasi Ram'
Subject: Re: [Equest-users] 3-D Geometry Lost
Want to try something new, and possibly a little dangerous?
(that’s one way of saying save a separate copy of the project before
proceeding)
If you have a copy of the project files where the 3D view is still working,
you could try opening that file up, navigating to the (working) 3D view,
then double click the top item of the component tree to view these “camera”
view details:
Keeping this window open for reference, open the .pd2 file of the “problem”
project in notepad (keep a separate copy!), and try editing the 6
consecutive lines in the beginning section which specify the view
properties:
After editing to match, save, close, cross your fingers, and try opening
with eQuest
Good luck!
If all else fails, our forefathers in energy modeling got by without
fancy-schmancy 3D visuals, walked uphill both ways to school and liked it
too (or so I gather)!
Mildly interesting: I’m finding with a little toying around here that you
can effect new 3D views that wouldn’t otherwise be possible with the rotate
and zoom features by messing with these pd2 values
mostly with confusing or
less-than-practical results however so far
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Juan Carlos
Lopez
Sent: Tuesday, October 08, 2013 4:42 PM
To: 'Adam Towell'; equest-users at lists.onebuilding.org; 'Thulasi Ram'
Subject: Re: [Equest-users] 3-D Geometry Lost
No, I still can’t see the 3D. it is appearing like this after make a
simulation and right click and try to reset camera.
Thanks
Juan Carlos López
Ing. De Modelaje Energético
Tel / Fax: +52(55)52536030 ext. 304
<http://www.ibe-mexico.com.mx/> www.ibe-mexico.com.mx
ibe
De: Adam Towell [mailto:atowell at cxegroup.com]
Enviado el: martes, 8 de octubre de 2013 03:47 p. m.
Para: Juan Carlos Lopez; equest-users at lists.onebuilding.org
Asunto: RE: [Equest-users] 3-D Geometry Lost
Juan,
Try right clicking and select “Reset Camera.” Then click on one of the other
tabs of the program (Internal Loads, Water-Side HVAC, etc.), then go back to
your Building Shell. Your 3D geometry should reappear.
Hope this helps!
-Adam Towell
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Juan Carlos
Lopez
Sent: Tuesday, October 08, 2013 3:14 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 3-D Geometry Lost
Dear All
I was working on a multifamily high rise building and suddenly the 3-D
Geometry disappear, I don-t know where to find it.
Do you know how to solve this?
I open other projects and the geometry is still there.
Juan Carlos López
ibe
Se certificó que el correo no contiene virus.
Comprobada por AVG - www.avg.es
Versión: 2013.0.3408 / Base de datos de virus: 3222/6733 - Fecha de la
versión: 08/10/2013
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131008/f7f6aaaf/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 57649 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131008/f7f6aaaf/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 51219 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131008/f7f6aaaf/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131008/f7f6aaaf/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 116162 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131008/f7f6aaaf/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 7715 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131008/f7f6aaaf/attachment-0008.png>