[Equest-users] Question regarding DX-Cool-EIR-fPLR & IEER

Kathryn Kerns kathryn.kerns at bceengineers.com
Wed Oct 30 08:03:00 PDT 2013


I don't know. I asked this question earlier because I sensed that there
was a way to show extra energy savings if we could define the baseline,
but I don't think anyone in the community has an answer. I am thinking
that unless someone gets an official ruling otherwise, I am going to
assume the DX baseline is single stage for smaller DX units, 2 stage for
larger (above 10 tons?) DX units, and 4 stage for really large (above 40
ton) DX units. It may not be right, but if people force you to use
things and not define them, you have to guess something.

 

 

________________________________

From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com] 
Sent: Tuesday, October 29, 2013 4:56 PM
To: Kathryn Kerns; Paul Riemer; Bishop, Bill; Bobby Almeida;
equest-users at lists.onebuilding.org
Subject: RE: Question regarding DX-Cool-EIR-fPLR & IEER

 

ASHRAE 90.1-2010 Section G3.1.2.1 specifically requires that modelers
reset the baseline equipment to match the IEER specified in the code.

 

I'm curious if the modeling research community (eg ASHRAE-funded,
utility-funded, etc) have given any thought to an expected procedure to
accomplish this. 

 

One option would be for ASHRAE or another entity to produce
peer-reviewed research developing specific baseline curves for specific
pieces of equipment.

 

Until that time, the IEER rating conditions allow for a multitude of
possible part load curves that would all comply with the minimum IEER. 

 

Until that time, if any individual modeler creates a baseline curve that
successfully calculates to the required baseline IEER, on what grounds
could a reviewer or authority challenge that the modeler has violated
the intent of G3.1.2.1?

 

Then, 

 

Aaron Dahlstrom, PE, LEED(r) AP

In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414,
Philadelphia, PA 19102 

d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF:
212-354-5656

e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com
<http://www.in-posse.com/>  | akf web: www.AKFGroup.com

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn
Kerns
Sent: Thursday, October 03, 2013 1:50 PM
To: Paul Riemer; Bishop, Bill; Bobby Almeida;
equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Question regarding DX-Cool-EIR-fPLR & IEER

 

Thanks for the input. Yes I know we need to pull out the fan energy and
yes I am familair with the AHRI 340/360-2007 methodology for creating an
IEER value, and yes I concede that modifying the part load curve without
modyfing the other curve is going to be an approximation. The point is -
given a baseline IEER value can we create a baseline part load DX curve
without the raw data? For that matter, given a proposed system IEER can
we create a part load curve? I think the answer is, you can't. I can
probably solve the proposed part load problem by asking a manufacturer
for their IEER data, but what to do about the baseline?

 

I sense there is a way to gain energy savings here, but I am not sure
how to go about proving it to the satisfaction of our unfortunately
challenged LEED reviewers.

 

________________________________

From: Paul Riemer [mailto:Paul.Riemer at dunhameng.com]
Sent: Thu 10/3/2013 8:20 AM
To: 'Bishop, Bill'; Bobby Almeida; Kathryn Kerns; 
equest-users at lists.onebuilding.org
Subject: RE: Question regarding DX-Cool-EIR-fPLR & IEER

Remember a packaged cooling equipment EER is the ratio of cooling effect
(Btu/hr) provided divided by the total (supply fan, compressor,
condenser fans and controls) energy draw (W).

So to get from the packaged unit EER to DOE-2 cooling EIR value and the
EIR curves you need to remove the fan energy at each point.  That AHRI
standard that Bill mentioned addresses what the fan volume and static
pressure (but not explicitly fan power) has to be at each of the four
part load points.  Good luck.  

 

Paul Riemer, PE, LEED AP BD+C 

DUNHAM

 

From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop,
Bill
Sent: Thursday, October 03, 2013 8:58 AM
To: Bobby Almeida; Kathryn Kerns; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Question regarding DX-Cool-EIR-fPLR & IEER

 

You would need to evaluate/modify two separate curves to match the IEER.
IEER is a function of part load and condenser temperature, holding
return air temperature (EAT) constant. The COOL-EIR-FPLR curve is a
function of the part load ratio only, not temperature. The COOL-EIR-FT
curve is a function of EAT and condenser temperature (OAT or EWT).

 

The IEER formula and methodology are described in section 6.2 of AHRI
340/360-2007 with Addenda 1 and 2
<http://www.ahrinet.org/App_Content/ahri/files/standards%20pdfs/ANSI%20s
tandards%20pdfs/ANSI%20AHRI%20Standard%20340-360-2007%20with%20Addenda%2
01%20and%202.pdf> .

 

Regards,

Bill

 

William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers &
Architects LLP

Senior Energy Engineer

 

134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 325-6004 Ext. 114            F: (585) 325-6005

bbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>            
www.pathfinder-ea.com <http://www.pathfinder-ea.com/> 

P   Sustainability - the forest AND the trees. P   

 

From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bobby
Almeida
Sent: Wednesday, October 02, 2013 8:42 PM
To: Kathryn Kerns; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Question regarding DX-Cool-EIR-fPLR

 

Hi Kathryn,

 

On our projects where we take credit for part load efficiencies we use
addendum s to 90.1-2007. This adds in IEER values for units so you're
comparing apples to apples. The only projects we have modeled this on
have had baseline systems that were 9.5 EER with an IEER of 9.6. With
such a small difference between EER and IEER, the 25%, 50% and 75%
values aren't that important. 9.5 EER at full load and 9.6 at the other
values will get you the 9.6 required for baseline. For information on
how to make curves I would look through the archives of this user group,
there have been some great explanations.

 

Bobby Almeida, E.I.T.    

Project Engineer

 

 

4051 Glencoe Ave. Suite 5 

Marina del Rey, CA 90292

p. 310.591.8172

c. 925.980.2025

www.gaiadevelopment.com <http://www.gaiadevelopment.com/> 

 

P Please consider the trees before printing this email

 

Legal Notice: This message and any materials attached are confidential,
and are intended solely for the use of the addressee. If you are not the
intended recipient, be advised that unauthorized use, disclosure,
copying, or distribution is strictly prohibited. If you received this
message in error please do not read it, notify the sender, and delete
your copy immediately. 

 

From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn
Kerns
Sent: Wednesday, October 02, 2013 3:37 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Question regarding DX-Cool-EIR-fPLR

 

Everyone, has anyone ever modified the standard DX-Cool-EIR-fPLR curve
to fit a particular DX cooling system? If so, when you compared it to a
baseline DX cooling system, did you use the original eQuest
DX-Cool-EIR-fPLR? 

 

I looked through ASHRAE 90.1 -2007 and although there is full load EER
data for air conditioners and heat pumps, there is no IEER data. 

 

However, it occurs to me that if ASHRAE 90.1 starts including IEER data
(which shows up in ASHRAE 90.1 -2010 Section 6) how are we going to
modify the eQuest DX-Cool-EIR-fPLR to accommodate the IEER? The IEER is
a single number and we have no idea what the 25%, 50%, 75% cooling load
ratios look like.

 

Hmmm.

 

 

Kathryn Kerns

Systems Specialist

BCE Engineers, Inc.

| Ph: 253.922.0446 | Fx: 253.922.0896 | 

 

 


This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended
recipient of this e-mail, do not duplicate or redistribute it by any
means. Please delete it and any attachments and notify the sender that
you have received it in error. Unintended recipients are prohibited from
taking action on the basis of information in this e-mail. E-mail
messages may contain computer viruses or other defects, may not be
accurately replicated on other systems, or may be intercepted, deleted
or interfered without the knowledge of the sender or the intended
recipient. If you are not comfortable with the risks associated with
e-mail messages, you may decide not to use e-mail to communicate with In
Posse. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131030/46a60e5f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1806 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131030/46a60e5f/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 794 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131030/46a60e5f/attachment-0005.jpeg>


More information about the Equest-users mailing list