Yashika,
Assuming you are trying to create a custom condensing-boiler curve
(HIR-FPLR), it's important to understand how the curve is defined. The
result of the curve is normalized HIR*PLR, i.e. normalized heat input ratio
*times* part load ratio, and it is a biquadratic function of part load
ratio and HW return temperature. It should equal 1.0 at 100% load and 80F
HW return. If the efficiency (HIR) stayed constant with changing part load
(which it doesn't in your graph, but just assume it did for illustration),
then the value of the curve would be 0.8 at 80% load, 0.5 at 50% load, etc.
-Erik
*Erik Kolderup, PE, LEED AP*
erik at kolderupconsulting.com | 415.531.5198 | www.kolderupconsulting.com
On Tue, Apr 8, 2014 at 12:32 PM, yashika gulati <yashika.gulati111 at gmail.com
> wrote:
> Hi great minds.
>
> How can I plot the graph for given boiler (attachment)? I know we can give
> rough data in "create new" graph but my results for heating are
> absurd. Please suggest me the proper technique to do that.
>
> Thanks a lot in advance
> Yashika
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140408/ac3d3255/attachment-0001.htm>
More information about the Equest-users
mailing list