[Equest-users] Pump and Flow sizing issue
Jacob Goodman
jacobgoodman22 at gmail.com
Thu Aug 14 09:49:52 PDT 2014
Dear All,
I am working on a model using the DES option 1 for supplying steam to my
building (district heating only so system 3). The baseline and proposed
have working steam meters and all looks well. My problem arose when I
went to fill in the new Section 1.4 tables for the pumping which brought
my attention to the fact that both models had auto-sized gpm flow and
pump size.
The auto sized values are WAY lower than the values on the mechanical
schedules! Auto-sized proposed model = 23gpm and .325kW...designed
proposed model = 141gpm and 11kW! Auto-sized baseline = 33 gpm and
0.467kW. If I input corrected pump size as per G3.1.3.5 this will give
me a baseline pump of 0.627kW. I'm worried that if I correct the
proposed pump size and flow to the designed numbers it will destroy my
energy cost savings.
Attached are the files for both models.
Thank you all,
Jacob Goodman, LEED AP
-------------- next part --------------
INPUT ..
$ ---------------------------------------------------------
$ Abort, Diagnostics
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Global Parameters
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Title, Run Periods, Design Days, Holidays
$ ---------------------------------------------------------
TITLE
LINE-1 = *UofM Athletic Addition baseline*
..
"Entire Year" = RUN-PERIOD-PD
BEGIN-MONTH = 1
BEGIN-DAY = 1
BEGIN-YEAR = 2014
END-MONTH = 12
END-DAY = 31
END-YEAR = 2014
..
"Standard US Holidays" = HOLIDAYS
LIBRARY-ENTRY "US"
..
$ ---------------------------------------------------------
$ Compliance Data
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Site and Building Data
$ ---------------------------------------------------------
"Site Data" = SITE-PARAMETERS
ALTITUDE = 0
..
"Building Data" = BUILD-PARAMETERS
HOLIDAYS = "Standard US Holidays"
..
PROJECT-DATA
..
$ ---------------------------------------------------------
$ Materials / Layers / Constructions
$ ---------------------------------------------------------
"1stEWall Cons Mat 2 (16.34)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 16.34
..
"2ndRoof Cons Mat 4 (31.45)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 31.45
..
"1stUFMat (G.NW1.U2.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 1.25183
..
"1stUFMat (G.E2.U3.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 0.1
..
"1stUFMat (G.E3.U4.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 2.42182
..
"1stUFMat (G.N4.U5.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 7.50989
..
"1stUFMat (G.S5.U6.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 5.01542
..
"BseUFMat (B.N1.U2.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 100
..
"BseUWMat (B.N1.U2.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 3.00557
..
"1stEWall Cons Layers" = LAYERS
MATERIAL = ( "Stucco 1in (SC01)", "Insul Bd 3/4in (IN62)",
"1stEWall Cons Mat 2 (16.34)", "GypBd 1/2in (GP01)" )
..
"1stCeilg Cons Layers" = LAYERS
MATERIAL = ( "AcousTile 1/2in (AC02)" )
..
"1stIFlr Cons Layers" = LAYERS
MATERIAL = ( "Conc HW 140lb 6in (HF-C13)" )
..
"2ndRoof Cons Layers" = LAYERS
MATERIAL = ( "Blt-Up Roof 3/8in (BR01)", "Bldg Paper Felt (BP01)",
"Plywd 5/8in (PW04)", "2ndRoof Cons Mat 4 (31.45)",
"AcousTile 1/2in (AC02)" )
..
"1stUFLyrs (G.NW1.U2)" = LAYERS
MATERIAL = ( "1stUFMat (G.NW1.U2.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.E2.U3)" = LAYERS
MATERIAL = ( "1stUFMat (G.E2.U3.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.E3.U4)" = LAYERS
MATERIAL = ( "1stUFMat (G.E3.U4.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.N4.U5)" = LAYERS
MATERIAL = ( "1stUFMat (G.N4.U5.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.S5.U6)" = LAYERS
MATERIAL = ( "1stUFMat (G.S5.U6.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"BseUFLyrs (B.N1.U2)" = LAYERS
MATERIAL = ( "BseUFMat (B.N1.U2.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"BseUWLyrs (B.N1.U2)" = LAYERS
MATERIAL = ( "BseUWMat (B.N1.U2.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 6in (HF-C13)" )
..
"Exterior Wall Assembly" = CONSTRUCTION
TYPE = U-VALUE
ABSORPTANCE = 0.6
ROUGHNESS = 1
U-VALUE = 0.064
..
"1stCeilg Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stCeilg Cons Layers"
..
"1stIWall Construction" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.1
..
"1stIFlr Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"1stIFlSP Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"Roof Assembly" = CONSTRUCTION
TYPE = U-VALUE
ABSORPTANCE = 0.6
ROUGHNESS = 1
U-VALUE = 0.048
..
"2ndGFlr Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"2ndGFlSP Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"1stUFCons (G.NW1.U2)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.NW1.U2)"
..
"1stUFCons (G.E2.U3)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.E2.U3)"
..
"1stUFCons (G.E3.U4)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.E3.U4)"
..
"1stUFCons (G.N4.U5)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.N4.U5)"
..
"1stUFCons (G.S5.U6)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.S5.U6)"
..
"Below Grade Floor Assembly" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.54
..
"Below Grade Wall Assembly" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.119
..
"Dbl Lyr Unins Mtl Door" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.7
..
$ ---------------------------------------------------------
$ Glass Type Codes
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Glass Types
$ ---------------------------------------------------------
"Baseline Windows" = GLASS-TYPE
TYPE = SHADING-COEF
SHADING-COEF = 0.46
GLASS-CONDUCT = 0.39
VIS-TRANS = 0.43
..
$ ---------------------------------------------------------
$ Window Layers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Lamps / Luminaries / Lighting Systems
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Day Schedules
$ ---------------------------------------------------------
"1stBldg Occup S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, 0.0005, 0.0039, 0.005, &D, &D,
0.0028, &D, 0.005, &D, &D, 0.0039, 0.0016, 0.0005, &D, &D, &D, 0 )
..
"1stBldg Occup S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, 0.054, 0.225, 0.9, &D, &D,
0.783, &D, 0.801, &D, 0.711, 0.414, 0.207, 0.387, &D, 0.288, 0.099,
0.045, 0 )
..
"1stBldg Occup S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"1stBldg InsLt S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.0512, 0.0535, 0.054, &D,
&D, &D, &D, &D, &D, &D, 0.0535, 0.0521, 0.0512, &D, 0.0502, &D,
0.05 )
..
"1stBldg InsLt S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.1605, 0.424, 0.9, &D, &D,
&D, &D, &D, 1, 0.713, 0.611, 0.5005, 0.679, &D, 0.6705, 0.288,
0.101, 0.05 )
..
"1stBldg InsLt S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"1stBldg Misc S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.051, &D, &D, &D, &D, &D, 0.0514, 0.0536, 0.054, &D,
&D, &D, &D, &D, &D, &D, &D, 0.0523, 0.0514, &D, 0.051 )
..
"1stBldg Misc S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.058, &D, &D, &D, &D, &D, 0.1085, 0.4201, 0.9, &D,
&D, &D, &D, &D, &D, 0.7063, 0.6137, 0.5043, 0.6811, &D, 0.6727,
0.2938, 0.1085, 0.058 )
..
"1stBldg Misc S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"BseBldg OffEq S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05 )
..
"BseBldg OffEq S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.1355, 0.6143, 0.905, &D,
&D, 0.5886, &D, 0.8879, &D, 0.8622, 0.6571, 0.3151, 0.2039, &D,
0.1868, 0.144, 0.0586, 0.05 )
..
"BseBldg OffEq S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"BseBldg SCRfg S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6636, &D, 0.656, &D, &D, 0.6636, 0.6723, 0.6887,
0.705, 0.7301, 0.7465, 0.7563, 0.765, &D, &D, &D, 0.7563, 0.7465,
0.7377, 0.729, 0.7127, 0.6876, 0.6723, 0.6636 )
..
"BseBldg SCRfg S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.64, &D, &D, &D, &D, 0.6556, 0.6712, 0.731, 0.7908,
0.8558, &D, 0.8818, 0.9, &D, &D, &D, 0.8818, 0.874, 0.8454, 0.8168,
0.7726, 0.7206, 0.6972, 0.6556 )
..
"BseBldg SCRfg S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"BseBldg Cook S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, 0.0011, &D, 0.0005, &D, 0.0016,
0.0032, 0.004, 0.0024, 0.0011, 0.0005, &D, &D, &D, 0.0003, 0 )
..
"BseBldg Cook S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, 0.1407, 0.2881, 0.1541, 0.1072, 0.0536,
0.0134, 0.0603, 0.1407, 0.2278, 0.1206, 0.0268, 0.1474, 0.3819,
0.67, 0.3819, 0.1474, 0.0603, 0 )
..
"BseBldg Cook S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"Ext Lighting W1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, &D, &D, &D, 0.3, 0.1, 0, &D, &D, &D,
&D, &D, 0.1, 0.55, 0.9, &D, &D, &D, &D, 0.8, 0.7 )
..
"Ext Lighting W2 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, &D, 0.45, 0.15, 0, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 0.25, 0.7, 0.9, &D, &D, 0.8, 0.7 )
..
"Ext Lighting W5 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, 0.3, 0, &D, &D, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, &D, &D, 0.25, 0.8, &D, 0.7 )
..
"Ext Lighting W8 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, &D, 0.45, 0.25, 0, &D, &D, &D, &D,
&D, &D, &D, &D, 0.1, 0.5, 0.9, &D, &D, &D, 0.8, 0.7 )
..
"DHW Eqp NRes W1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.03 )
..
"DHW Eqp NRes W2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.2, 0.5975, 0.7025, 0.8,
&D, &D, &D, &D, &D, &D, 0.7025, 0.5, &D, &D, 0.4025, 0.2, 0.1025,
0.05 )
..
"DHW Eqp NRes W2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"ZG0-S1 (PVAVS) P-Inf S1 All" = DAY-SCHEDULE-PD
TYPE = MULTIPLIER
VALUES = ( 1 )
..
"ZG0-S1 (PVAVS) P-Inf S2 WD" = DAY-SCHEDULE-PD
TYPE = MULTIPLIER
VALUES = ( 1, &D, &D, &D, &D, 1.004, 1.175, 1.25, &D, 0.5, 0.701,
&D, 0.5, &D, 0.62, 1.25, &D, 0.971, 1.13, 1.049, 1.238, 1.193,
1.049, 1 )
..
"ZG0-S1 (PVAVS) P-Inf S2 HDD" = DAY-SCHEDULE-PD
TYPE = MULTIPLIER
VALUES = ( 1, &D, &D, &D, &D, &D, &D, 0.5, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 1 )
..
"ZG0-S1 (PVAVS) C-Inf S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 1 )
..
"ZG0-S1 (PVAVS) C-Inf S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 1, &D, &D, &D, &D, &D, &D, 0.5, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 1 )
..
"S1 Sys1 (PVAVS) Fan S1 All" = DAY-SCHEDULE-PD
TYPE = ON/OFF/FLAG
VALUES = ( 0 )
..
"S1 Sys1 (PVAVS) Fan S2 WD" = DAY-SCHEDULE-PD
TYPE = ON/OFF/FLAG
VALUES = ( 0, &D, &D, &D, &D, &D, &D, 1, &D, &D, &D, &D, &D, &D,
&D, &D, &D, &D, 0 )
..
"S1 Sys1 (PVAVS) Cool S1 All" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 82 )
..
"S1 Sys1 (PVAVS) Cool S2 WD" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 82, &D, &D, &D, &D, &D, &D, 76, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 82 )
..
"S1 Sys1 (PVAVS) Heat S1 All" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64 )
..
"S1 Sys1 (PVAVS) Heat S2 WD" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64, &D, &D, &D, &D, &D, &D, 70, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 64 )
..
"S1 1stSys1 (PVAVS) (G.NW1) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.E2) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.E3) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.N4) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.S5) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S12ndSys1 (PVAVS) (G.NNW1) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.C2) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.N3) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.SW4) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.W5) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.C6) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.NE7) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S12ndSys1 (PVAVS) (G.ESE8) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"Cust 1 Elec Seas1 Day" = DAY-SCHEDULE-PD
TYPE = FLAG
VALUES = ( 1 )
..
"Day Schedule 50" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D,
&D, 1, 0 )
..
"Day Schedule 51" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.1605, 0.424, 0.9, &D, &D,
&D, &D, &D, &D, 0.713, 0.611, 0.5005, 0.679, &D, 0.6705, 0.288,
0.101, 0.05 )
..
"Day Schedule 52" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"Day Schedule 53" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64 )
..
"Day Schedule 54" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64, &D, &D, &D, &D, &D, &D, 70, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 64 )
..
"Elevator sch week day" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, &D, &D, &D, 1, 0 )
..
"Elevator sch weekend" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"Day Schedule RESET-TEMP" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 50
OUTSIDE-LO = 20
SUPPLY-HI = 180
SUPPLY-LO = 150
..
$ ---------------------------------------------------------
$ Week Schedules
$ ---------------------------------------------------------
"1stBldg Occup S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Occup S1 All" )
..
"1stBldg Occup S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Occup S2 WD", &D, &D, &D, &D,
"1stBldg Occup S1 All", &D, &D, "1stBldg Occup S2 HDD" )
..
"1stBldg InsLt S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg InsLt S1 All" )
..
"1stBldg InsLt S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg InsLt S2 WD", &D, &D, &D, &D,
"1stBldg InsLt S1 All", &D, &D, "1stBldg InsLt S2 HDD" )
..
"1stBldg Misc S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Misc S1 All" )
..
"1stBldg Misc S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Misc S2 WD", &D, &D, &D, &D,
"1stBldg Misc S1 All", &D, &D, "1stBldg Misc S2 HDD" )
..
"BseBldg OffEq S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg OffEq S1 All" )
..
"BseBldg OffEq S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg OffEq S2 WD", &D, &D, &D, &D,
"BseBldg OffEq S1 All", &D, &D, "BseBldg OffEq S2 HDD" )
..
"BseBldg SCRfg S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg SCRfg S1 All" )
..
"BseBldg SCRfg S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg SCRfg S2 WD", &D, &D, &D, &D,
"BseBldg SCRfg S1 All", &D, &D, "BseBldg SCRfg S2 HDD" )
..
"BseBldg Cook S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg Cook S1 All" )
..
"BseBldg Cook S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg Cook S2 WD", &D, &D, &D, &D,
"BseBldg Cook S1 All", &D, &D, "BseBldg Cook S2 HDD" )
..
"Ext Lighting Wk1" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W1 All" )
..
"Ext Lighting Wk2" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W2 All" )
..
"Ext Lighting Wk5" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W5 All" )
..
"Ext Lighting Wk8" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W8 All" )
..
"DHW Eqp NRes Wk1" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "DHW Eqp NRes W1 All" )
..
"DHW Eqp NRes Wk2" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "DHW Eqp NRes W2 WD", &D, &D, &D, &D,
"DHW Eqp NRes W1 All", &D, &D, "DHW Eqp NRes W2 HDD" )
..
"ZG0-S1 (PVAVS) P-Inf S1 Wk" = WEEK-SCHEDULE-PD
TYPE = MULTIPLIER
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) P-Inf S1 All" )
..
"ZG0-S1 (PVAVS) P-Inf S2 Wk" = WEEK-SCHEDULE-PD
TYPE = MULTIPLIER
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) P-Inf S2 WD", &D, &D, &D, &D,
"ZG0-S1 (PVAVS) P-Inf S1 All", &D, &D,
"ZG0-S1 (PVAVS) P-Inf S2 HDD" )
..
"ZG0-S1 (PVAVS) C-Inf S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) C-Inf S1 All" )
..
"ZG0-S1 (PVAVS) C-Inf S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) C-Inf S2 WD", &D, &D, &D, &D,
"ZG0-S1 (PVAVS) C-Inf S1 All" )
..
"S1 Sys1 (PVAVS) Fan S1 Wk" = WEEK-SCHEDULE-PD
TYPE = ON/OFF/FLAG
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Fan S1 All" )
..
"S1 Sys1 (PVAVS) Fan S2 Wk" = WEEK-SCHEDULE-PD
TYPE = ON/OFF/FLAG
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Fan S2 WD", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Fan S1 All" )
..
"S1 Sys1 (PVAVS) Cool S1 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Cool S1 All" )
..
"S1 Sys1 (PVAVS) Cool S2 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Cool S2 WD", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Cool S1 All" )
..
"S1 Sys1 (PVAVS) Heat S1 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S1 All" )
..
"S1 Sys1 (PVAVS) Heat S2 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S2 WD", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Heat S1 All" )
..
"S1 1stSys1 (PVAVS) (G.NW1) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.NW1) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.E2) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E2) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.E3) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E3) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.N4) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.N4) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.S5) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.S5) CRS-D" )
..
"S12ndSys1 (PVAVS) (G.NNW1) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.NNW1) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.C2) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C2) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.N3) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.N3) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.SW4) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.SW4) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.W5) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.W5) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.C6) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C6) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.NE7) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.NE7) CRS-D" )
..
"S12ndSys1 (PVAVS) (G.ESE8) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.ESE8) CRS-D" )
..
"Cust 1 Elec Seas1 Week" = WEEK-SCHEDULE-PD
TYPE = FLAG
DAY-SCHEDULES = ( "Cust 1 Elec Seas1 Day" )
..
"Week Schedule 41" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Day Schedule 50", &D, &D, &D, &D,
"1stBldg InsLt S2 HDD" )
..
"Week Schedule 42" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Day Schedule 51", &D, &D, &D, &D,
"1stBldg InsLt S1 All", &D, &D, "Day Schedule 52" )
..
"Week Schedule 43" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "Day Schedule 53" )
..
"Week Schedule 44" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "Day Schedule 54", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Heat S1 All" )
..
"Elevator sch week" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Elevator sch week day", "Elevator sch weekend",
"Elevator sch weekend", &D, "Elevator sch weekend",
"Elevator sch weekend" )
..
$ ---------------------------------------------------------
$ Annual Schedules
$ ---------------------------------------------------------
"1stBldg Occup Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "1stBldg Occup S1 Wk", "1stBldg Occup S2 Wk",
"1stBldg Occup S1 Wk", "1stBldg Occup S2 Wk", "1stBldg Occup S1 Wk",
"1stBldg Occup S2 Wk", "1stBldg Occup S1 Wk", "1stBldg Occup S2 Wk",
"1stBldg Occup S1 Wk" )
..
"1stBldg InsLt Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "1stBldg InsLt S1 Wk", "1stBldg InsLt S2 Wk",
"1stBldg InsLt S1 Wk", "1stBldg InsLt S2 Wk", "1stBldg InsLt S1 Wk",
"1stBldg InsLt S2 Wk", "1stBldg InsLt S1 Wk", "1stBldg InsLt S2 Wk",
"1stBldg InsLt S1 Wk" )
..
"1stBldg Misc Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "1stBldg Misc S1 Wk", "1stBldg Misc S2 Wk",
"1stBldg Misc S1 Wk", "1stBldg Misc S2 Wk", "1stBldg Misc S1 Wk",
"1stBldg Misc S2 Wk", "1stBldg Misc S1 Wk", "1stBldg Misc S2 Wk",
"1stBldg Misc S1 Wk" )
..
"BseBldg OffEq Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "BseBldg OffEq S1 Wk", "BseBldg OffEq S2 Wk",
"BseBldg OffEq S1 Wk", "BseBldg OffEq S2 Wk", "BseBldg OffEq S1 Wk",
"BseBldg OffEq S2 Wk", "BseBldg OffEq S1 Wk", "BseBldg OffEq S2 Wk",
"BseBldg OffEq S1 Wk" )
..
"BseBldg SCRfg Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "BseBldg SCRfg S1 Wk", "BseBldg SCRfg S2 Wk",
"BseBldg SCRfg S1 Wk", "BseBldg SCRfg S2 Wk", "BseBldg SCRfg S1 Wk",
"BseBldg SCRfg S2 Wk", "BseBldg SCRfg S1 Wk", "BseBldg SCRfg S2 Wk",
"BseBldg SCRfg S1 Wk" )
..
"BseBldg Cook Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "BseBldg Cook S1 Wk", "BseBldg Cook S2 Wk",
"BseBldg Cook S1 Wk", "BseBldg Cook S2 Wk", "BseBldg Cook S1 Wk",
"BseBldg Cook S2 Wk", "BseBldg Cook S1 Wk", "BseBldg Cook S2 Wk",
"BseBldg Cook S1 Wk" )
..
"Ext Lighting Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12 )
DAY = ( 31, 28, 31, 30, 31, 30, 31, 31, 30, 31, 30, 31 )
WEEK-SCHEDULES = ( "Ext Lighting Wk1", "Ext Lighting Wk2",
"Ext Lighting Wk2", "Ext Lighting Wk2", "Ext Lighting Wk5",
"Ext Lighting Wk5", "Ext Lighting Wk5", "Ext Lighting Wk8",
"Ext Lighting Wk8", "Ext Lighting Wk8", "Ext Lighting Wk1",
"Ext Lighting Wk1" )
..
"DHW Eqp NRes Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "DHW Eqp NRes Wk1", "DHW Eqp NRes Wk2",
"DHW Eqp NRes Wk1", "DHW Eqp NRes Wk2", "DHW Eqp NRes Wk1",
"DHW Eqp NRes Wk2", "DHW Eqp NRes Wk1", "DHW Eqp NRes Wk2",
"DHW Eqp NRes Wk1" )
..
"ZG0-S1 (PVAVS) P-Inf Sch" = SCHEDULE-PD
TYPE = MULTIPLIER
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk" )
..
"ZG0-S1 (PVAVS) C-Inf Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk" )
..
"S1 Sys1 (PVAVS) Fan Sch" = SCHEDULE-PD
TYPE = ON/OFF/FLAG
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk" )
..
"S1 Sys1 (PVAVS) Cool Sch" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk" )
..
"S1 Sys1 (PVAVS) Heat Sch" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk" )
..
"S1 1stSys1 (PVAVS) (G.NW1) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.NW1) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.E2) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E2) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.E3) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E3) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.N4) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.N4) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.S5) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.S5) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.NNW1) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.NNW1) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.C2) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C2) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.N3) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.N3) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.SW4) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.SW4) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.W5) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.W5) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.C6) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C6) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.NE7) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.NE7) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.ESE8) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.ESE8) CRS-W" )
..
"Cust 1 Elec Season Sched" = SCHEDULE-PD
TYPE = FLAG
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "Cust 1 Elec Seas1 Week" )
..
"Lighting Low occ year" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "Week Schedule 41", "Week Schedule 41",
"Week Schedule 41", "Week Schedule 41", "Week Schedule 41",
"Week Schedule 41", "Week Schedule 41", "Week Schedule 41",
"Week Schedule 41" )
..
"Unocc Heat Shc" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk" )
..
"GYMNASIUM LTG" = SCHEDULE-PD
LIBRARY-ENTRY "GYMNASIUM LTG"
..
"Elevator sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "Elevator sch week" )
..
"Schedule RESET-TEMP" = SCHEDULE-PD
LIBRARY-ENTRY "Schedule RESET-TEMP"
..
$ ---------------------------------------------------------
$ Polygons
$ ---------------------------------------------------------
"1stFloor Polygon" = POLYGON
V1 = ( 32.4, 290.3 )
V2 = ( 32.4, 271.1 )
V3 = ( 32.4, 228.9 )
V4 = ( 32.4, 201.65 )
V5 = ( 81.65, 201.5 )
V6 = ( 81.65, 221.4 )
V7 = ( 61.65, 221.4 )
V8 = ( 61.65, 228.95 )
V9 = ( 61.85, 271.1 )
V10 = ( 46.35, 271.1 )
V11 = ( 46.35, 281.15 )
V12 = ( 55.15, 281.15 )
V13 = ( 62.6, 281.15 )
V14 = ( 62.6, 290.3 )
V15 = ( 55.4, 290.3 )
..
"1stSpace Polygon 1" = POLYGON
V1 = ( 0, 0 )
V2 = ( 19.2, 0 )
V3 = ( 19.2, 7.15 )
V4 = ( 9.15, 7.15 )
V5 = ( 9.15, 13.95 )
V6 = ( 9.15, 22.75 )
V7 = ( 0, 23 )
..
"1stSpace Polygon 2" = POLYGON
V1 = ( 0, 0 )
V2 = ( 7.45, 0 )
V3 = ( 7.45, 9.15 )
V4 = ( 0.25, 9.15 )
..
"1stSpace Polygon 3" = POLYGON
V1 = ( 0, 0 )
V2 = ( 10.05, 0 )
V3 = ( 10.05, 6.8 )
V4 = ( 0, 6.8 )
..
"1stSpace Polygon 4" = POLYGON
V1 = ( 0, 0 )
V2 = ( 42.2, 0 )
V3 = ( 42.15, 29.25 )
V4 = ( 0, 29.45 )
V5 = ( 0, 13.95 )
V6 = ( 0, 7.15 )
..
"1stSpace Polygon 5" = POLYGON
V1 = ( 0, 0 )
V2 = ( 27.25, 0 )
V3 = ( 27.4, 49.25 )
V4 = ( 7.5, 49.25 )
V5 = ( 7.5, 29.25 )
V6 = ( -0.05, 29.25 )
..
"2ndFloor Polygon" = POLYGON
V1 = ( 25.85, 276.6 )
V2 = ( 25.85, 222.6 )
V3 = ( 25.85, 207.35 )
V4 = ( 46.9, 207.35 )
V5 = ( 80.3, 207.35 )
V6 = ( 80.3, 282 )
V7 = ( 80.3, 295.95 )
V8 = ( 62.1, 295.95 )
V9 = ( 55.2, 295.95 )
V10 = ( 32.4, 295.95 )
V11 = ( 32.4, 287.1 )
V12 = ( 25.85, 287.1 )
..
"2ndSpace Polygon 1" = POLYGON
V1 = ( 0, 0 )
V2 = ( 8.85, 0 )
V3 = ( 8.85, -6.55 )
V4 = ( 19.35, -6.55 )
V5 = ( 19.05, 7.65 )
V6 = ( 9.05, 7.65 )
V7 = ( 9.15, 13.95 )
V8 = ( 8.65, 22.8 )
V9 = ( 0, 22.8 )
..
"2ndSpace Polygon 2" = POLYGON
V1 = ( 0, 0 )
V2 = ( 6.3, 0 )
V3 = ( 6.3, 9.9 )
V4 = ( 0, 10 )
..
"2ndSpace Polygon 3" = POLYGON
V1 = ( 0, 0 )
V2 = ( 8.65, 0 )
V3 = ( 8.65, 7.4 )
V4 = ( 0, 7.4 )
..
"2ndSpace Polygon 4" = POLYGON
V1 = ( 0, 0 )
V2 = ( 15.25, 0 )
V3 = ( 15.25, 21.05 )
V4 = ( 0.15, 21.05 )
..
"2ndSpace Polygon 5" = POLYGON
V1 = ( 0, 0 )
V2 = ( 54, 0 )
V3 = ( 54.15, 21.05 )
V4 = ( 54.15, 41.15 )
V5 = ( -0, 41.15 )
V6 = ( -0.3, 20.5 )
V7 = ( -0.3, 14.2 )
..
"2ndSpace Polygon 6" = POLYGON
V1 = ( 0, 0 )
V2 = ( 20.65, -0.3 )
V3 = ( 20.65, 5.1 )
V4 = ( 20.65, 10.4 )
V5 = ( 16.25, 10.4 )
V6 = ( 8.85, 10.4 )
V7 = ( 0, 9.9 )
..
"2ndSpace Polygon 7" = POLYGON
V1 = ( 0, 0 )
V2 = ( 13.95, 0 )
V3 = ( 13.95, 17.7 )
V4 = ( 5.3, 17.7 )
V5 = ( 5.3, 13.3 )
V6 = ( 0, 13.3 )
..
"2ndSpace Polygon 8" = POLYGON
V1 = ( 0, 0 )
V2 = ( 33.4, 0 )
V3 = ( 33.4, 74.65 )
V4 = ( 20.1, 74.65 )
V5 = ( 20.1, 15.1 )
V6 = ( 0, 15.1 )
..
"BseFloor Polygon" = POLYGON
V1 = ( 32.4, 178.75 )
V2 = ( 32.4, 129.75 )
V3 = ( 76.75, 129.75 )
V4 = ( 76.75, 148.55 )
V5 = ( 80.9, 148.55 )
V6 = ( 80.9, 157.45 )
V7 = ( 89.9, 157.45 )
V8 = ( 89.9, 175.6 )
V9 = ( 60.9, 175.6 )
V10 = ( 60.9, 179.15 )
V11 = ( 60.9, 207.6 )
V12 = ( 32.4, 207.6 )
..
"BseSpace Polygon 1" = POLYGON
V1 = ( 0, 0 )
V2 = ( 28.85, 0 )
V3 = ( 28.45, 28.5 )
V4 = ( 0, 28.5 )
..
"BseSpace Polygon 2" = POLYGON
V1 = ( 0, 0 )
V2 = ( 49, 0 )
V3 = ( 49, 44.35 )
V4 = ( 30.2, 44.35 )
V5 = ( 30.2, 48.5 )
V6 = ( 21.3, 48.5 )
V7 = ( 21.3, 57.5 )
V8 = ( 3.15, 57.5 )
V9 = ( 3.15, 28.5 )
V10 = ( -0.4, 28.5 )
..
"1stSpace Polygon 1 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 23, 0 )
V3 = ( 22.75, 9.15 )
V4 = ( 13.95, 9.15 )
V5 = ( 7.15, 9.15 )
V6 = ( 7.15, 19.2 )
V7 = ( 0, 19.2 )
..
"1stSpace Polygon 2 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 9.15, 0.25 )
V3 = ( 9.15, 7.45 )
V4 = ( 0, 7.45 )
..
"1stSpace Polygon 3 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 6.8, 0 )
V3 = ( 6.8, 10.05 )
V4 = ( 0, 10.05 )
..
"1stSpace Polygon 4 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 7.15, 0 )
V3 = ( 13.95, 0 )
V4 = ( 29.45, 0 )
V5 = ( 29.25, 42.15 )
V6 = ( 0, 42.2 )
..
"1stSpace Polygon 5 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 29.25, -0.05 )
V3 = ( 29.25, 7.5 )
V4 = ( 49.25, 7.5 )
V5 = ( 49.25, 27.4 )
V6 = ( 0, 27.25 )
..
"2ndSpace Polygon 1 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 22.8, 0 )
V3 = ( 22.8, 8.65 )
V4 = ( 13.95, 9.15 )
V5 = ( 7.65, 9.05 )
V6 = ( 7.65, 19.05 )
V7 = ( -6.55, 19.35 )
V8 = ( -6.55, 8.85 )
V9 = ( 0, 8.85 )
..
"2ndSpace Polygon 2 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 10, 0 )
V3 = ( 9.9, 6.3 )
V4 = ( 0, 6.3 )
..
"2ndSpace Polygon 3 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 7.4, 0 )
V3 = ( 7.4, 8.65 )
V4 = ( 0, 8.65 )
..
"2ndSpace Polygon 4 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 21.05, 0.15 )
V3 = ( 21.05, 15.25 )
V4 = ( 0, 15.25 )
..
"2ndSpace Polygon 5 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 14.2, -0.3 )
V3 = ( 20.5, -0.3 )
V4 = ( 41.15, -0 )
V5 = ( 41.15, 54.15 )
V6 = ( 21.05, 54.15 )
V7 = ( 0, 54 )
..
"2ndSpace Polygon 6 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 9.9, 0 )
V3 = ( 10.4, 8.85 )
V4 = ( 10.4, 16.25 )
V5 = ( 10.4, 20.65 )
V6 = ( 5.1, 20.65 )
V7 = ( -0.3, 20.65 )
..
"2ndSpace Polygon 7 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 13.3, 0 )
V3 = ( 13.3, 5.3 )
V4 = ( 17.7, 5.3 )
V5 = ( 17.7, 13.95 )
V6 = ( 0, 13.95 )
..
"2ndSpace Polygon 8 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 15.1, 0 )
V3 = ( 15.1, 20.1 )
V4 = ( 74.65, 20.1 )
V5 = ( 74.65, 33.4 )
V6 = ( 0, 33.4 )
..
"BseSpace Polygon 1 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 28.5, 0 )
V3 = ( 28.5, 28.45 )
V4 = ( 0, 28.85 )
..
"BseSpace Polygon 2 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 28.5, -0.4 )
V3 = ( 28.5, 3.15 )
V4 = ( 57.5, 3.15 )
V5 = ( 57.5, 21.3 )
V6 = ( 48.5, 21.3 )
V7 = ( 48.5, 30.2 )
V8 = ( 44.35, 30.2 )
V9 = ( 44.35, 49 )
V10 = ( 0, 49 )
..
$ ---------------------------------------------------------
$ Wall Parameters
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Fixed and Building Shades
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Misc Cost Related Objects
$ ---------------------------------------------------------
"Baseline Data" = BASELINE
..
$ *********************************************************
$ ** **
$ ** Performance Curves **
$ ** **
$ *********************************************************
$ *********************************************************
$ ** **
$ ** Floors / Spaces / Walls / Windows / Doors **
$ ** **
$ *********************************************************
"1stGround Flr" = FLOOR
AZIMUTH = 360
POLYGON = "1stFloor Polygon"
SHAPE = POLYGON
FLOOR-HEIGHT = 12
SPACE-HEIGHT = 12
C-DIAGRAM-DATA = *Bldg Envelope & Loads 1 Diag Data*
..
"Entry 103" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0827134
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 1"
LOCATION = FLOOR-V1
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stWest Wall (G.NW1.E1)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stWest Win (G.NW1.E1.W1)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 11.1383
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.NW1.E1.W2)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 15.3083
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78332
FRAME-CONDUCT = 2.781
..
"1stWest Door (G.NW1.E1.D1)" = DOOR
CONSTRUCTION = "Dbl Lyr Unins Mtl Door"
X = 1.9
HEIGHT = 7
WIDTH = 3
..
"1stSouth Wall (G.NW1.E2)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V5
SHADING-SURFACE = YES
..
"1stNorth Wall (G.NW1.E3)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V7
SHADING-SURFACE = YES
..
"1stSouth Wall (G.NW1.I1)" = INTERIOR-WALL
NEXT-TO = "Lobby 101"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"1stEast Wall (G.NW1.I2)" = INTERIOR-WALL
NEXT-TO = "Elev 104"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"1stSouth Wall (G.NW1.I3)" = INTERIOR-WALL
NEXT-TO = "Elev 104"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"1stEast Wall (G.NW1.I4)" = INTERIOR-WALL
NEXT-TO = "Mech 106"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"1stFlr (G.NW1.U1)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.NW1.U2)"
LOCATION = BOTTOM
..
"Mech 106" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.161925
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 2"
LOCATION = FLOOR-V12
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stSouth Wall (G.E2.E4)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stEast Wall (G.E2.E5)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"1stNorth Wall (G.E2.E6)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"1stFlr (G.E2.U2)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.E2.U3)"
LOCATION = BOTTOM
..
"Elev 104" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0670588
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 3"
LOCATION = FLOOR-V10
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stEast Wall (G.E3.E7)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stFlr (G.E3.U3)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.E3.U4)"
LOCATION = BOTTOM
..
"Lobby 101" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0367835
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 4"
LOCATION = FLOOR-V2
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stWest Wall (G.N4.E8)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stWest Win (G.N4.E8.W1)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 14.0583
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W2)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 18.2283
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W3)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 22.3983
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W4)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 26.5683
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W5)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 33.9383
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W6)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 38.1083
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W7)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 4.37999
Y = 0.488056
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W8)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 0.108333
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stEast Wall (G.N4.E9)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"1stNorth Wall (G.N4.E10)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V4
SHADING-SURFACE = YES
..
"1stSouth Wall (G.N4.I5)" = INTERIOR-WALL
NEXT-TO = "Office South 107"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"1stNorth Wall (G.N4.I6)" = INTERIOR-WALL
NEXT-TO = "Elev 104"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"1stFlr (G.N4.U4)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.N4.U5)"
LOCATION = BOTTOM
..
"Office South 107" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0472394
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 5"
LOCATION = FLOOR-V3
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stWest Wall (G.S5.E11)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stWest Win (G.S5.E11.W1)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 10.6783
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W2)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 14.8983
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W3)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 19.1183
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W4)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 23.2383
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W5)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 4.27833
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W6)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 0.108333
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stSouth Wall (G.S5.E12)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"1stEast Wall (G.S5.E13)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"1stNorth Wall (G.S5.E14)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V4
SHADING-SURFACE = YES
..
"1stEast Wall (G.S5.E15)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V5
SHADING-SURFACE = YES
..
"1stFlr (G.S5.U5)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.S5.U6)"
LOCATION = BOTTOM
..
"2ndGround Flr" = FLOOR
Y = -5.75
Z = 12
AZIMUTH = 360
POLYGON = "2ndFloor Polygon"
SHAPE = POLYGON
FLOOR-HEIGHT = 12
SPACE-HEIGHT = 12
C-DIAGRAM-DATA = *EL2 Bldg Envelope & Loads 1 Diag Data*
..
"Vestabule 201" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0633102
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 1"
LOCATION = FLOOR-V10
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndWest Wall (G.NNW1.E1)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndNorth Wall (G.NNW1.E2)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndNorth Win (G.NNW1.E2.W1)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 0.345487
Y = 0.345487
HEIGHT = 11.2833
WIDTH = 5.78333
FRAME-CONDUCT = 2.781
..
"2ndWest Wall (G.NNW1.E3)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"2ndWest Win (G.NNW1.E3.W1)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 0.480902
Y = 0.392918
HEIGHT = 11.2833
WIDTH = 9.44333
FRAME-CONDUCT = 2.781
..
"2ndNorth Wall (G.NNW1.E4)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V9
SHADING-SURFACE = YES
..
"2ndRoof (G.NNW1.E5)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.NNW1.I1)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndSouth Wall (G.NNW1.I2)" = INTERIOR-WALL
NEXT-TO = "Study Lounge 204"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"2ndEast Wall (G.NNW1.I3)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"2ndSouth Wall (G.NNW1.I4)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"2ndSouth Wall (G.NNW1.I5)" = INTERIOR-WALL
NEXT-TO = "IT Elec 205"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V7
..
"2ndEast Wall (G.NNW1.I6)" = INTERIOR-WALL
NEXT-TO = "Mech 203"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V8
..
"Elev 200" = SPACE
X = 40.05
Y = 276.9
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) C-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.001
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 2"
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndRoof (G.C2.E6)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.C2.I7)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"Mech 203" = SPACE
X = 55.2
Y = 295.95
AZIMUTH = 90
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0527166
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 3"
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndNorth Wall (G.N3.E7)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V4
SHADING-SURFACE = YES
..
"2ndRoof (G.N3.E8)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.N3.I8)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"Study 212" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0518192
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 4"
LOCATION = FLOOR-V2
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndWest Wall (G.SW4.E9)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndWest Win (G.SW4.E9.W1)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 0.483748
Y = 0.358333
HEIGHT = 11.2833
WIDTH = 14.2833
FRAME-CONDUCT = 2.781
..
"2ndSouth Wall (G.SW4.E10)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndRoof (G.SW4.E11)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.SW4.I9)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"Study Lounge 204" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0110233
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 5"
LOCATION = FLOOR-V1
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndWest Wall (G.W5.E12)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndWest Win (G.W5.E12.W1)" = WINDOW
GLASS-TYPE = "Baseline Windows"
FRAME-WIDTH = 0.108333
X = 0.298333
Y = 0.348333
HEIGHT = 11.2833
WIDTH = 53.2833
FRAME-CONDUCT = 2.781
..
"2ndRoof (G.W5.E13)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.W5.I10)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndSouth Wall (G.W5.I11)" = INTERIOR-WALL
NEXT-TO = "Study 212"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"2ndSouth Wall (G.W5.I12)" = INTERIOR-WALL
NEXT-TO = "Office 208-16"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"2ndEast Wall (G.W5.I13)" = INTERIOR-WALL
NEXT-TO = "Office 208-16"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"2ndNorth Wall (G.W5.I14)" = INTERIOR-WALL
NEXT-TO = "IT Elec 205"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"2ndNorth Wall (G.W5.I15)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"IT Elec 205" = SPACE
X = 46.35
Y = 276.9
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) C-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.001
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 6.5 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 6"
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndRoof (G.C6.E14)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.C6.I16)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndEast Wall (G.C6.I17)" = INTERIOR-WALL
NEXT-TO = "Office 208-16"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"2ndEast Wall (G.C6.I18)" = INTERIOR-WALL
NEXT-TO = "RestR 206-7"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"2ndNorth Wall (G.C6.I19)" = INTERIOR-WALL
NEXT-TO = "RestR 206-7"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"2ndNorth Wall (G.C6.I20)" = INTERIOR-WALL
NEXT-TO = "Mech 203"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"2ndWest Wall (G.C6.I21)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V7
..
"RestR 206-7" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.064547
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 7"
LOCATION = FLOOR-V6
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndEast Wall (G.NE7.E15)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndNorth Wall (G.NE7.E16)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndRoof (G.NE7.E17)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.NE7.I22)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndWest Wall (G.NE7.I23)" = INTERIOR-WALL
NEXT-TO = "Mech 203"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"Office 208-16" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0380072
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 8"
LOCATION = FLOOR-V4
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndSouth Wall (G.ESE8.E18)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndEast Wall (G.ESE8.E19)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndRoof (G.ESE8.E20)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.ESE8.I24)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndNorth Wall (G.ESE8.I25)" = INTERIOR-WALL
NEXT-TO = "RestR 206-7"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"2ndWest Wall (G.ESE8.I26)" = INTERIOR-WALL
NEXT-TO = "Study 212"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"BseBelow-Grade Flr" = FLOOR
Y = 82
Z = -12
AZIMUTH = 360
POLYGON = "BseFloor Polygon"
SHAPE = POLYGON
FLOOR-HEIGHT = 12
SPACE-HEIGHT = 12
C-DIAGRAM-DATA = *Basement Diag Data*
..
"BseNorth" = SPACE
SHAPE = POLYGON
ZONE-TYPE = UNCONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "Lighting Low occ year" )
EQUIP-SCHEDULE = ( "Elevator sch" )
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 27.55 )
AREA/PERSON = 10000
POLYGON = "BseSpace Polygon 1"
LOCATION = FLOOR-V12
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"BseFlr (B.N1.U1)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Floor Assembly"
LOCATION = BOTTOM
..
"BseWest Wall (B.N1.U2)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V1
..
"BseEast Wall (B.N1.U3)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V3
..
"BseNorth Wall (B.N1.U4)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V4
..
"BseSouth" = SPACE
SHAPE = POLYGON
ZONE-TYPE = UNCONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "Lighting Low occ year" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 1.2 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 10000
POLYGON = "BseSpace Polygon 2"
LOCATION = FLOOR-V1
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"BseNorth Wall (B.S2.I1)" = INTERIOR-WALL
NEXT-TO = "BseNorth"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V10
..
"BseFlr (B.S2.U5)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Floor Assembly"
LOCATION = BOTTOM
..
"BseWest Wall (B.S2.U6)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V1
..
"BseSouth Wall (B.S2.U7)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V2
..
"BseEast Wall (B.S2.U8)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V3
..
"BseSouth Wall (B.S2.U9)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V4
..
"BseEast Wall (B.S2.U10)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V5
..
"BseSouth Wall (B.S2.U11)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V6
..
"BseEast Wall (B.S2.U12)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V7
..
"BseNorth Wall (B.S2.U13)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V8
..
"BseEast Wall (B.S2.U14)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V9
..
$ *********************************************************
$ ** **
$ ** Electric & Fuel Meters **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Electric Meters
$ ---------------------------------------------------------
"EM1" = ELEC-METER
TYPE = UTILITY
EXTERIOR-POWER = ( 0.662 )
EXTERIOR-SCH = ( "Ext Lighting Sch" )
..
$ ---------------------------------------------------------
$ Fuel Meters
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Master Meters
$ ---------------------------------------------------------
"MASTER-METERS 1" = MASTER-METERS
MSTR-ELEC-METER = "EM1"
MSTR-FUEL-METER = "FM1"
..
$ *********************************************************
$ ** **
$ ** HVAC Circulation Loops / Plant Equipment **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Pumps
$ ---------------------------------------------------------
"HW Loop Pump" = PUMP
NUMBER = 1
MOTOR-CLASS = HI-EFF
CAP-CTRL = VAR-SPEED-PUMP
..
$ ---------------------------------------------------------
$ Heat Exchangers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Circulation Loops
$ ---------------------------------------------------------
"Hot Water Loop" = CIRCULATION-LOOP
TYPE = HW
LOOP-DESIGN-DT = 50
PIPE-HEAD = 21.6
LOOP-OPERATION = STANDBY
DESIGN-HEAT-T = 180
HEAT-SETPT-CTRL = OA-RESET
HEAT-RESET-SCH = "Schedule RESET-TEMP"
LOOP-PUMP = "HW Loop Pump"
..
"DHW Plant 1 Loop (1)" = CIRCULATION-LOOP
TYPE = DHW
DESIGN-HEAT-T = 135
PROCESS-FLOW = ( 0.05 )
PROCESS-SCH = ( "DHW Eqp NRes Sch" )
PROCESS-T = ( 135 )
..
$ ---------------------------------------------------------
$ Chillers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Boilers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Domestic Water Heaters
$ ---------------------------------------------------------
"DHW Plant 1 Wtr Htr (1)" = DW-HEATER
TYPE = ELEC
TANK-VOLUME = 66.8934
CAPACITY = 0.0297183
TANK-UA = 2.78723
LOCATION = ZONE
ZONE-NAME = "BseSouth Th"
DHW-LOOP = "DHW Plant 1 Loop (1)"
C-ENERGY-FACTOR = 0.841701
C-TANK-EXT-RVAL = 12
..
$ ---------------------------------------------------------
$ Heat Rejection
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Tower Free Cooling
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Photovoltaic Modules
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Electric Generators
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Thermal Storage
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Ground Loop Heat Exchangers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Compliance DHW (residential dwelling units)
$ ---------------------------------------------------------
$ *********************************************************
$ ** **
$ ** Steam & Chilled Water Meters **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Steam Meters
$ ---------------------------------------------------------
"Steam Meter 1" = STEAM-METER
ENERGY/UNIT = 1.16e+006
CIRCULATION-LOOP = "Hot Water Loop"
..
$ ---------------------------------------------------------
$ Chilled Water Meters
$ ---------------------------------------------------------
$ *********************************************************
$ ** **
$ ** HVAC Systems / Zones **
$ ** **
$ *********************************************************
"Entry 103 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Enrty 103 Th"
..
"Enrty 103 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Entry 103"
OA-FLOW/AREA = 0.63
..
"Mech 106 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Mech 106 Th"
..
"Mech 106 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Mech 106"
OA-FLOW/AREA = 0.63
..
"Elev 104 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Elev 104 Th"
..
"Elev 104 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Elev 104"
OA-FLOW/AREA = 0.63
..
"Lobby 101 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Lobby 101 Th"
..
"Lobby 101 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Lobby 101"
OA-FLOW/AREA = 0.63
..
"1stSouth 107 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "1stSouth 107 Th"
..
"1stSouth 107 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Office South 107"
OA-FLOW/AREA = 0.63
..
"Vestabule 201 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Vestabule 201 Th"
..
"Vestabule 201 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Vestabule 201"
OA-FLOW/AREA = 0.63
..
"Elev 200 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Elev 200 Th"
..
"Elev 200 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.4
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Elev 200"
OA-FLOW/AREA = 0.63
..
"Mech 203 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Mech 203 Th"
..
"Mech 203 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Mech 203"
OA-FLOW/AREA = 0.63
..
"Study 212 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Study 212 Th"
..
"Study 212 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Study 212"
OA-FLOW/AREA = 0.63
..
"Lounge 204 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.0008348
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.258
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Lounge 204 Th"
..
"Lounge 204 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Study Lounge 204"
OA-FLOW/AREA = 0.63
..
"IT Elec 205 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "IT Elec 205 Th"
..
"IT Elec 205 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.4
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "IT Elec 205"
OA-FLOW/AREA = 0.63
..
"RestR 206-7 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "RestR 206-7 Th"
..
"RestR 206-7 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "RestR 206-7"
OA-FLOW/AREA = 0.63
..
"Office 208-16 Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
HEAT-SIZING-RATI = 1.25
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 90
MIN-SUPPLY-T = 55
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = CONSTANT-VOLUME
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.00085
RETURN-EFF = 0.53
REHEAT-DELTA-T = 30
HW-VALVE-TYPE = TWO-WAY
HW-LOOP = "Hot Water Loop"
COOLING-EIR = 0.2507
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
CONTROL-ZONE = "Office 208-16 Th"
..
"Office 208-16 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
DESIGN-HEAT-T = 72
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 75
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Office 208-16"
OA-FLOW/AREA = 0.63
..
"BseNorth SUM sys" = SYSTEM
TYPE = SUM
HEAT-SOURCE = NONE
SYSTEM-REPORTS = NO
..
"BseNorth Th" = ZONE
TYPE = UNCONDITIONED
DESIGN-HEAT-T = 72
DESIGN-COOL-T = 75
SIZING-OPTION = ADJUST-LOADS
SPACE = "BseNorth"
..
"BseSouth SUM sys" = SYSTEM
TYPE = SUM
HEAT-SOURCE = NONE
SYSTEM-REPORTS = NO
..
"BseSouth Th" = ZONE
TYPE = UNCONDITIONED
DESIGN-HEAT-T = 72
DESIGN-COOL-T = 75
SIZING-OPTION = ADJUST-LOADS
SPACE = "BseSouth"
..
$ *********************************************************
$ ** **
$ ** Metering & Misc HVAC **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Equipment Controls
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Load Management
$ ---------------------------------------------------------
$ *********************************************************
$ ** **
$ ** Utility Rates **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Ratchets
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Block Charges
$ ---------------------------------------------------------
"Cust 1 Elec Uniform Blk1" = BLOCK-CHARGE
BLOCK-SCH = "Cust 1 Elec Season Sched"
SCH-FLAG = 1
BLOCK1-TYPE = ENERGY
BLOCKS-1 = ( 1 )
COSTS-1 = ( 0.085 )
..
"Steam Block" = BLOCK-CHARGE
BLOCKS-1 = ( 1e+007 )
COSTS-1 = ( 6.71 )
..
$ ---------------------------------------------------------
$ Utility Rates
$ ---------------------------------------------------------
"UofM elec" = UTILITY-RATE
TYPE = ELECTRICITY
BLOCK-CHARGES = ( "Cust 1 Elec Uniform Blk1" )
..
"Steam Rate" = UTILITY-RATE
TYPE = STEAM
BLOCK-CHARGES = ( "Steam Block" )
..
$ *********************************************************
$ ** **
$ ** Output Reporting **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Loads Non-Hourly Reporting
$ ---------------------------------------------------------
LOADS-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Systems Non-Hourly Reporting
$ ---------------------------------------------------------
SYSTEMS-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Plant Non-Hourly Reporting
$ ---------------------------------------------------------
PLANT-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Economics Non-Hourly Reporting
$ ---------------------------------------------------------
ECONOMICS-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Hourly Reporting
$ ---------------------------------------------------------
"Hourly Report" = HOURLY-REPORT
LIBRARY-ENTRY "Hourly Report"
..
$ ---------------------------------------------------------
$ THE END
$ ---------------------------------------------------------
END ..
COMPUTE ..
STOP ..
-------------- next part --------------
Proj "UofM Athletic Addition baseline "
ProgramVersion = "eQUEST 3.65.7163"
BDBaseVersion = 25
ProductCode = "eQUEST"
WeatherFile = "TMY2\MISSOUMT.bin"
CreateDate = 1401221951
ModDate = 1408032376
RunDate = 1408031109
LibraryFile = "eQ_Lib.dat"
ActiveMode = 0
InputModule = 3
Owner = "University Of Montana"
UseCameraData = 1
ClippingRange = ( 109.477, 311.932 )
FocalPoint = ( 57.025, 245.9, 6.52929 )
Position = ( -96.6388, 142.252, 78.6626 )
ViewUpVector = ( 0, 0, 1 )
ViewAngle = 30
InterfaceMode = 1
AllowWizard = 1
NotProjFile = "UofM Athletic Addition baseline"
InputUnitsType = "English"
OutputUnitsType = "English"
PreviousName = "UofM Athletic Addition baseline "
DetailedModelEdits = 1
ProjTreeType = ( 0, 1, 1, 1, 1, 1 )
ProjTreeID = ( 10000, 10010000, 10080000, 10030063, 10480002,
10760000 )
ProjTreeLabel = ( "Project: 'UofM Athletic Addition baseline '",
"1stBldg Occup Sch", "Entry 103",
"Day Schedule RESET-TEMP", "Elev 104 Sys", "FM1" )
..
MainWiz "UofM Athletic Addition baseline "
ProductCode = "eQUEST"
WizardType = "Design Development"
DebugID = 0
AllowCustWinDoor = 1
ScreenIDArrIdx = 2
ScreenIDArrID = 18
Coverage = "All eQUEST Locations"
State = "Montana"
Location = "Missoula"
ElecUtility = "- custom -"
GasUtility = "- none -"
UserElecRate[1] = "UofM elec"
UserFuelRate = "Custom Gas Rate"
BldgType = "School, College/University"
HVACDefaulted = 1
..
ShellWiz "First Floor"
NamePrefix = "1st"
ModelEnduse[3] = 0
ModelEnduse[4] = 0
ModelEnduse[5] = 0
ModelEnduse[12] = 0
ScreenIDArrIdx = 13
ScreenIDArrID = 132
BldgType = "School, College/University"
GrossArea = 2851
FlrsAboveGrade = 1
Footprint = "- custom -"
FlrToFlr = 12
FlrToCeiling = 12
ZoningPattern = "- custom -"
NumMCZnGrps = 0
DiagLink = "Bldg Envelope & Loads 1 Diag Data"
RoofConsType = "No Exterior Exposure (adiabatic)"
ZoningCurrent = 1
NumFloorVertices = 15
FloorVertX[1] = 32.4
FloorVertX[2] = 32.4
FloorVertX[3] = 32.4
FloorVertX[4] = 32.4
FloorVertX[5] = 81.65
FloorVertX[6] = 81.65
FloorVertX[7] = 61.65
FloorVertX[8] = 61.65
FloorVertX[9] = 61.85
FloorVertX[10] = 46.35
FloorVertX[11] = 46.35
FloorVertX[12] = 55.15
FloorVertX[13] = 62.6
FloorVertX[14] = 62.6
FloorVertX[15] = 55.4
FloorVertY[1] = 290.3
FloorVertY[2] = 271.1
FloorVertY[3] = 228.9
FloorVertY[4] = 201.65
FloorVertY[5] = 201.5
FloorVertY[6] = 221.4
FloorVertY[7] = 221.4
FloorVertY[8] = 228.95
FloorVertY[9] = 271.1
FloorVertY[10] = 271.1
FloorVertY[11] = 281.15
FloorVertY[12] = 281.15
FloorVertY[13] = 281.15
FloorVertY[14] = 290.3
FloorVertY[15] = 290.3
AdiabaticCurrent = 1
ZoneGroupsOK = 1
DfltZnGrpName[1] = "GrndUnderground Areas"
DfltZnGrpName[2] = "GrndGround Floor"
DfltZnGrpName[3] = "GrndGround Floor"
DfltZnGrpName[4] = "GrndTypical Floor(s)"
DfltZnGrpName[5] = "GrndTypical Floor(s)"
DfltZnGrpName[6] = "GrndTop Floor"
DfltZnGrpName[7] = "GrndTop Floor"
DfltZnGrpName[8] = "GrndData Center"
CustomFootprint = 1
CustomZoning = 1
ActiveZoneIndex = 5
CustomRoofZoning = -1
ActiveRoofZoneIdx = 1
FloorArea = 2850.85
FloorPerimLen = 308.651
LastFootprint = 1
OverhangOption = "None"
GTCCategory[2] = "- select another -"
WindowHeight[1] = 8
WinSillHeight[1] = 0.5
PercentGlass2[1] = 40
PercentGlass3[1] = 0
DoorType[1] = "Opaque"
NumExtDoors1[1] = 0
NumExtDoors2[1] = 1
NumExtDoors3[1] = 0
NumExtDoors4[1] = 0
TypWindowWidth[1] = 4
SkyZonesCurrent = 1
SkyltZones[1] = 1
SkyltZones[2] = 1
SkyltZones[3] = 1
SkyltZones[4] = 1
SkyltZones[5] = 1
SkyPosCurrent = 1
DayZonesCurrent[3] = 1
DayltZones[1] = 1
DayltZones[2] = 1
DayltZones[3] = 1
DayltZones[4] = 1
DayltZones[5] = 0
DayltZones[201] = 1
DayltZones[202] = 1
DayltZones[203] = 1
DayltZones[204] = 1
DayltZones[205] = 0
DayltZones[401] = 1
DayltZones[402] = 1
DayltZones[403] = 1
DayltZones[404] = 1
DayltZones[405] = 1
WinDoorCurrent = 1
DetailsCurrent = ( 1, 1, 1 )
BDLNumDayltCtrls[1] = 0
BDLNumDayltCtrls[2] = 0
BDLNumDayltCtrls[3] = 0
BDLNumDayltCtrls[4] = 0
BDLNumDayltCtrls[5] = 0
BDLNumDayltCtrls[201] = 0
BDLNumDayltCtrls[202] = 0
BDLNumDayltCtrls[203] = 0
BDLNumDayltCtrls[204] = 0
BDLNumDayltCtrls[205] = 0
BDLNumDayltCtrls[401] = 0
BDLNumDayltCtrls[402] = 0
BDLNumDayltCtrls[403] = 0
BDLNumDayltCtrls[404] = 0
BDLNumDayltCtrls[405] = 0
OccShape = ( "EL1 Occup Profile (S1)", "EL1 Occup Profile (S2)",
"EL1 Occup Profile (S3)" )
ILShape = ( "EL1 InsLtg Profile (S1)", "EL1 InsLtg Profile (S2)",
"EL1 InsLtg Profile (S3)" )
ELDayShapes = ( "EL1 ExtLtg DayShape (Jan)",
"EL1 ExtLtg DayShape (Feb)",
"EL1 ExtLtg DayShape (Mar)",
"EL1 ExtLtg DayShape (Apr)",
"EL1 ExtLtg DayShape (May)",
"EL1 ExtLtg DayShape (Jun)",
"EL1 ExtLtg DayShape (Jul)",
"EL1 ExtLtg DayShape (Aug)",
"EL1 ExtLtg DayShape (Sep)",
"EL1 ExtLtg DayShape (Oct)",
"EL1 ExtLtg DayShape (Nov)",
"EL1 ExtLtg DayShape (Dec)" )
OEShape = ( "EL1 OffEq Profile (S1)", "EL1 OffEq Profile (S2)",
"EL1 OffEq Profile (S3)" )
CEShape = ( "EL1 CookEq Profile (S1)", "EL1 CookEq Profile (S2)",
"EL1 CookEq Profile (S3)" )
MiscShape = ( "EL1 Misc Profile (S1)", "EL1 Misc Profile (S2)",
"EL1 Misc Profile (S3)" )
RFDayShapes = ( "EL1 Refrig DayShape (Jan)",
"EL1 Refrig DayShape (Feb)",
"EL1 Refrig DayShape (Mar)",
"EL1 Refrig DayShape (Apr)",
"EL1 Refrig DayShape (May)",
"EL1 Refrig DayShape (Jun)",
"EL1 Refrig DayShape (Jul)",
"EL1 Refrig DayShape (Aug)",
"EL1 Refrig DayShape (Sep)",
"EL1 Refrig DayShape (Oct)",
"EL1 Refrig DayShape (Nov)",
"EL1 Refrig DayShape (Dec)" )
DHWShape = ( "EL1 DHW Profile (S1)", "EL1 DHW Profile (S2)",
"EL1 DHW Profile (S3)" )
SCRShape = ( "EL1 S-C Refrig Profile (S1)",
"EL1 S-C Refrig Profile (S2)",
"EL1 S-C Refrig Profile (S3)" )
GroundExtFacets[1] = "Facet-0-0"
GroundExtFacets[2] = "Facet-0-7"
GroundExtFacets[3] = "Facet-0-10"
DaylitAreaCurrent[3] = 1
RoofZoneErrorCode = 4
..
ShapeWiz "EL1 InsLtg Profile (S1)"
..
DayShape "EL1 ExtLtg DayShape (Jan)"
..
DayShape "EL1 ExtLtg DayShape (Feb)"
..
DayShape "EL1 ExtLtg DayShape (Mar)"
..
DayShape "EL1 ExtLtg DayShape (Apr)"
..
DayShape "EL1 ExtLtg DayShape (May)"
..
DayShape "EL1 ExtLtg DayShape (Jun)"
..
DayShape "EL1 ExtLtg DayShape (Jul)"
..
DayShape "EL1 ExtLtg DayShape (Aug)"
..
DayShape "EL1 ExtLtg DayShape (Sep)"
..
DayShape "EL1 ExtLtg DayShape (Oct)"
..
DayShape "EL1 ExtLtg DayShape (Nov)"
..
DayShape "EL1 ExtLtg DayShape (Dec)"
..
ShapeWiz "EL1 OffEq Profile (S1)"
..
ShapeWiz "EL1 Misc Profile (S1)"
..
ShapeWiz "EL1 DHW Profile (S1)"
..
ShapeWiz "EL1 Occup Profile (S1)"
..
ShapeWiz "EL1 InsLtg Profile (S2)"
..
ShapeWiz "EL1 InsLtg Profile (S3)"
..
ShapeWiz "EL1 OffEq Profile (S2)"
..
ShapeWiz "EL1 OffEq Profile (S3)"
..
ShapeWiz "EL1 CookEq Profile (S1)"
..
ShapeWiz "EL1 CookEq Profile (S2)"
..
ShapeWiz "EL1 CookEq Profile (S3)"
..
DayShape "EL1 Refrig DayShape (Jan)"
..
DayShape "EL1 Refrig DayShape (Feb)"
..
DayShape "EL1 Refrig DayShape (Mar)"
..
DayShape "EL1 Refrig DayShape (Apr)"
..
DayShape "EL1 Refrig DayShape (May)"
..
DayShape "EL1 Refrig DayShape (Jun)"
..
DayShape "EL1 Refrig DayShape (Jul)"
..
DayShape "EL1 Refrig DayShape (Aug)"
..
DayShape "EL1 Refrig DayShape (Sep)"
..
DayShape "EL1 Refrig DayShape (Oct)"
..
DayShape "EL1 Refrig DayShape (Nov)"
..
DayShape "EL1 Refrig DayShape (Dec)"
..
ShapeWiz "EL1 Misc Profile (S2)"
..
ShapeWiz "EL1 Misc Profile (S3)"
..
ShapeWiz "EL1 DHW Profile (S2)"
..
ShapeWiz "EL1 DHW Profile (S3)"
..
ShapeWiz "EL1 Occup Profile (S2)"
..
ShapeWiz "EL1 Occup Profile (S3)"
..
ShapeWiz "EL1 S-C Refrig Profile (S1)"
..
ShapeWiz "EL1 S-C Refrig Profile (S2)"
..
ShapeWiz "EL1 S-C Refrig Profile (S3)"
..
CustomZone "Custom Zone 1"
NumVerts = 7
X[1] = 32.4
X[2] = 32.4
X[3] = 39.55
X[4] = 39.55
X[5] = 46.35
X[6] = 55.15
X[7] = 55.4
Y[1] = 290.3
Y[2] = 271.1
Y[3] = 271.1
Y[4] = 281.15
Y[5] = 281.15
Y[6] = 281.15
Y[7] = 290.3
..
CustomZone "Custom Zone 2"
NumVerts = 4
X[1] = 55.15
X[2] = 62.6
X[3] = 62.6
X[4] = 55.4
Y[1] = 281.15
Y[2] = 281.15
Y[3] = 290.3
Y[4] = 290.3
..
CustomZone "Custom Zone 3"
NumVerts = 4
X[1] = 39.55
X[2] = 46.35
X[3] = 46.35
X[4] = 39.55
Y[1] = 271.1
Y[2] = 271.1
Y[3] = 281.15
Y[4] = 281.15
..
CustomZone "Custom Zone 4"
NumVerts = 6
X[1] = 32.4
X[2] = 32.4
X[3] = 61.65
X[4] = 61.85
X[5] = 46.35
X[6] = 39.55
Y[1] = 271.1
Y[2] = 228.9
Y[3] = 228.95
Y[4] = 271.1
Y[5] = 271.1
Y[6] = 271.1
..
CustomZone "Custom Zone 5"
NumVerts = 6
X[1] = 32.4
X[2] = 32.4
X[3] = 81.65
X[4] = 81.65
X[5] = 61.65
X[6] = 61.65
Y[1] = 228.9
Y[2] = 201.65
Y[3] = 201.5
Y[4] = 221.4
Y[5] = 221.4
Y[6] = 228.95
..
ZnGrpWiz "GrndGround Floor"
ShortName = "GndFlr"
..
FacetWiz "Facet-0-0"
ParentZoneIdx = 0
SegmentNumber = 0
..
WinWiz "Custom Window 36"
X = 11.03
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 37"
X = 15.2
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
DoorWiz "Custom Door 1"
X = 1.9
Y = 0
Width = 3
Height = 7
FrameWidth = 0
DoorTypeIdx = 0
..
FacetWiz "Facet-0-7"
ParentZoneIdx = 3
SegmentNumber = 0
..
WinWiz "Custom Window 38"
X = 13.95
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 39"
X = 18.12
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 40"
X = 22.29
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 41"
X = 26.46
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 42"
X = 33.83
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 43"
X = 38
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 44"
X = 4.27166
Y = 0.379723
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 45"
X = 0
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-10"
ParentZoneIdx = 4
SegmentNumber = 0
..
WinWiz "Custom Window 46"
X = 10.57
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 47"
X = 14.79
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 48"
X = 19.01
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 49"
X = 23.13
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 50"
X = 4.17
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 51"
X = 0
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
ShellWiz "Second floor"
NamePrefix = "2nd"
ModelEnduse[3] = 0
ModelEnduse[4] = 0
ModelEnduse[5] = 0
ModelEnduse[12] = 0
ScreenIDArrIdx = 7
ScreenIDArrID = 61
BldgType = "School, College/University"
GrossArea = 4766
FlrsAboveGrade = 1
ShellPos_Dir = "Immediately Above"
ShellPos_Specify = 1
BldgX = 0
Footprint = "- custom -"
FlrToFlr = 12
FlrToCeiling = 12
ZoningPattern = "- custom -"
NumMCZnGrps = 0
DiagLink = "EL2 Bldg Envelope & Loads 1 Diag Data"
RoofConsType = "Wood Advanced Frame, 24 in. o.c."
GrndFlrExposure = "Over Conditioned Space (adiabatic)"
GrndFlrInsType = "- no batt or board insulation -"
ZoningCurrent = 1
NumFloorVertices = 12
FloorVertX[1] = 25.85
FloorVertX[2] = 25.85
FloorVertX[3] = 25.85
FloorVertX[4] = 46.9
FloorVertX[5] = 80.3
FloorVertX[6] = 80.3
FloorVertX[7] = 80.3
FloorVertX[8] = 62.1
FloorVertX[9] = 55.2
FloorVertX[10] = 32.4
FloorVertX[11] = 32.4
FloorVertX[12] = 25.85
FloorVertX[13] = 81.15
FloorVertX[14] = 81.15
FloorVertX[15] = 62.1
FloorVertX[16] = 55.2
FloorVertX[17] = 32.4
FloorVertX[18] = 32.4
FloorVertX[19] = 25.85
FloorVertY[1] = 276.6
FloorVertY[2] = 222.6
FloorVertY[3] = 207.35
FloorVertY[4] = 207.35
FloorVertY[5] = 207.35
FloorVertY[6] = 282
FloorVertY[7] = 295.95
FloorVertY[8] = 295.95
FloorVertY[9] = 295.95
FloorVertY[10] = 295.95
FloorVertY[11] = 287.1
FloorVertY[12] = 287.1
FloorVertY[13] = 206.15
FloorVertY[14] = 295.95
FloorVertY[15] = 295.95
FloorVertY[16] = 295.95
FloorVertY[17] = 295.95
FloorVertY[18] = 287.1
FloorVertY[19] = 287.1
AdiabaticCurrent = 1
ZoneGroupsOK = 1
DfltZnGrpName[1] = "GrndUnderground Areas"
DfltZnGrpName[2] = "GrndGround Floor-2"
DfltZnGrpName[3] = "GrndGround Floor-2"
DfltZnGrpName[4] = "GrndTypical Floor(s)"
DfltZnGrpName[5] = "GrndTypical Floor(s)"
DfltZnGrpName[6] = "GrndTop Floor"
DfltZnGrpName[7] = "GrndTop Floor"
DfltZnGrpName[8] = "GrndData Center"
CustomFootprint = 1
CustomZoning = 1
ActiveZoneIndex = 4
CustomRoofZoning = -1
ActiveRoofZoneIdx = 1
FloorArea = 4766.3
FloorPerimLen = 286.1
LastFootprint = 9
OverhangOption = "None"
OverhangDepth[2] = 6
GTCCategory[2] = "- select another -"
PercentGlass2[1] = 40
PercentGlass3[1] = 0
PercentGlass4[1] = 0
DoorType[1] = "- select another -"
NumExtDoors1[1] = 0
NumExtDoors2[1] = 4
NumExtDoors3[1] = 0
NumExtDoors4[1] = 0
SkyZonesCurrent = 1
SkyltZones[1] = 1
SkyltZones[2] = 1
SkyltZones[3] = 1
SkyltZones[4] = 1
SkyltZones[5] = 1
SkyltZones[6] = 1
SkyltZones[7] = 1
SkyltZones[8] = 1
SkyltZones[9] = 1
SkyltZones[10] = 1
SkyltZones[11] = 1
SkyPosCurrent = 1
DayZonesCurrent[3] = 1
DayltZones[1] = 1
DayltZones[2] = 1
DayltZones[3] = 1
DayltZones[4] = 1
DayltZones[5] = 0
DayltZones[201] = 1
DayltZones[202] = 1
DayltZones[203] = 1
DayltZones[204] = 1
DayltZones[205] = 0
DayltZones[401] = 1
DayltZones[402] = 0
DayltZones[403] = 1
DayltZones[404] = 1
DayltZones[405] = 1
DayltZones[406] = 0
DayltZones[407] = 1
DayltZones[408] = 1
DayltZones[409] = 1
DayltZones[410] = 1
DayltZones[411] = 0
WinDoorCurrent = 1
DetailsCurrent = ( 1, 1, 1 )
BDLNumDayltCtrls[1] = 0
BDLNumDayltCtrls[2] = 0
BDLNumDayltCtrls[3] = 0
BDLNumDayltCtrls[4] = 0
BDLNumDayltCtrls[5] = 0
BDLNumDayltCtrls[201] = 0
BDLNumDayltCtrls[202] = 0
BDLNumDayltCtrls[203] = 0
BDLNumDayltCtrls[204] = 0
BDLNumDayltCtrls[205] = 0
BDLNumDayltCtrls[401] = 0
BDLNumDayltCtrls[402] = 0
BDLNumDayltCtrls[403] = 0
BDLNumDayltCtrls[404] = 0
BDLNumDayltCtrls[405] = 0
BDLNumDayltCtrls[406] = 0
BDLNumDayltCtrls[407] = 0
BDLNumDayltCtrls[408] = 0
BDLNumDayltCtrls[409] = 0
BDLNumDayltCtrls[410] = 0
BDLNumDayltCtrls[411] = 0
OccShape = ( "EL2 Occup Profile (S1)", "EL2 Occup Profile (S2)",
"EL2 Occup Profile (S3)" )
ILShape = ( "EL2 InsLtg Profile (S1)", "EL2 InsLtg Profile (S2)",
"EL2 InsLtg Profile (S3)" )
ELDayShapes = ( "EL2 ExtLtg DayShape (Jan)",
"EL2 ExtLtg DayShape (Feb)",
"EL2 ExtLtg DayShape (Mar)",
"EL2 ExtLtg DayShape (Apr)",
"EL2 ExtLtg DayShape (May)",
"EL2 ExtLtg DayShape (Jun)",
"EL2 ExtLtg DayShape (Jul)",
"EL2 ExtLtg DayShape (Aug)",
"EL2 ExtLtg DayShape (Sep)",
"EL2 ExtLtg DayShape (Oct)",
"EL2 ExtLtg DayShape (Nov)",
"EL2 ExtLtg DayShape (Dec)" )
OEShape = ( "EL2 OffEq Profile (S1)", "EL2 OffEq Profile (S2)",
"EL2 OffEq Profile (S3)" )
CEShape = ( "EL2 CookEq Profile (S1)", "EL2 CookEq Profile (S2)",
"EL2 CookEq Profile (S3)" )
MiscShape = ( "EL2 Misc Profile (S1)", "EL2 Misc Profile (S2)",
"EL2 Misc Profile (S3)" )
RFDayShapes = ( "EL2 Refrig DayShape (Jan)",
"EL2 Refrig DayShape (Feb)",
"EL2 Refrig DayShape (Mar)",
"EL2 Refrig DayShape (Apr)",
"EL2 Refrig DayShape (May)",
"EL2 Refrig DayShape (Jun)",
"EL2 Refrig DayShape (Jul)",
"EL2 Refrig DayShape (Aug)",
"EL2 Refrig DayShape (Sep)",
"EL2 Refrig DayShape (Oct)",
"EL2 Refrig DayShape (Nov)",
"EL2 Refrig DayShape (Dec)" )
DHWShape = ( "EL2 DHW Profile (S1)", "EL2 DHW Profile (S2)",
"EL2 DHW Profile (S3)" )
SCRShape = ( "EL2 S-C Refrig Profile (S1)",
"EL2 S-C Refrig Profile (S2)",
"EL2 S-C Refrig Profile (S3)" )
GroundExtFacets[1] = "Facet-0-0 4"
GroundExtFacets[2] = "Facet-0-1"
GroundExtFacets[3] = "Facet-0-2"
GroundExtFacets[4] = "Facet-0-5"
GroundExtFacets[5] = "Facet-0-7 8"
DaylitAreaCurrent[3] = 1
RoofZoneErrorCode = 4
..
ShapeWiz "EL2 InsLtg Profile (S1)"
..
DayShape "EL2 ExtLtg DayShape (Jan)"
..
DayShape "EL2 ExtLtg DayShape (Feb)"
..
DayShape "EL2 ExtLtg DayShape (Mar)"
..
DayShape "EL2 ExtLtg DayShape (Apr)"
..
DayShape "EL2 ExtLtg DayShape (May)"
..
DayShape "EL2 ExtLtg DayShape (Jun)"
..
DayShape "EL2 ExtLtg DayShape (Jul)"
..
DayShape "EL2 ExtLtg DayShape (Aug)"
..
DayShape "EL2 ExtLtg DayShape (Sep)"
..
DayShape "EL2 ExtLtg DayShape (Oct)"
..
DayShape "EL2 ExtLtg DayShape (Nov)"
..
DayShape "EL2 ExtLtg DayShape (Dec)"
..
ShapeWiz "EL2 OffEq Profile (S1)"
..
ShapeWiz "EL2 Misc Profile (S1)"
..
ShapeWiz "EL2 DHW Profile (S1)"
..
ShapeWiz "EL2 Occup Profile (S1)"
..
ShapeWiz "EL2 InsLtg Profile (S2)"
..
ShapeWiz "EL2 InsLtg Profile (S3)"
..
ShapeWiz "EL2 OffEq Profile (S2)"
..
ShapeWiz "EL2 OffEq Profile (S3)"
..
ShapeWiz "EL2 CookEq Profile (S1)"
..
ShapeWiz "EL2 CookEq Profile (S2)"
..
ShapeWiz "EL2 CookEq Profile (S3)"
..
DayShape "EL2 Refrig DayShape (Jan)"
..
DayShape "EL2 Refrig DayShape (Feb)"
..
DayShape "EL2 Refrig DayShape (Mar)"
..
DayShape "EL2 Refrig DayShape (Apr)"
..
DayShape "EL2 Refrig DayShape (May)"
..
DayShape "EL2 Refrig DayShape (Jun)"
..
DayShape "EL2 Refrig DayShape (Jul)"
..
DayShape "EL2 Refrig DayShape (Aug)"
..
DayShape "EL2 Refrig DayShape (Sep)"
..
DayShape "EL2 Refrig DayShape (Oct)"
..
DayShape "EL2 Refrig DayShape (Nov)"
..
DayShape "EL2 Refrig DayShape (Dec)"
..
ShapeWiz "EL2 Misc Profile (S2)"
..
ShapeWiz "EL2 Misc Profile (S3)"
..
ShapeWiz "EL2 DHW Profile (S2)"
..
ShapeWiz "EL2 DHW Profile (S3)"
..
ShapeWiz "EL2 Occup Profile (S2)"
..
ShapeWiz "EL2 Occup Profile (S3)"
..
ShapeWiz "EL2 S-C Refrig Profile (S1)"
..
ShapeWiz "EL2 S-C Refrig Profile (S2)"
..
ShapeWiz "EL2 S-C Refrig Profile (S3)"
..
ZnGrpWiz "GrndGround Floor-2"
ShortName = "GndFlr"
..
CustomZone "Custom Zone 6"
NumVerts = 9
X[1] = 32.4
X[2] = 32.4
X[3] = 25.85
X[4] = 25.85
X[5] = 40.05
X[6] = 40.05
X[7] = 46.35
X[8] = 55.2
X[9] = 55.2
Y[1] = 295.95
Y[2] = 287.1
Y[3] = 287.1
Y[4] = 276.6
Y[5] = 276.9
Y[6] = 286.9
Y[7] = 286.8
Y[8] = 287.3
Y[9] = 295.95
..
CustomZone "Custom Zone 7"
NumVerts = 4
X[1] = 40.05
X[2] = 46.35
X[3] = 46.35
X[4] = 40.05
Y[1] = 276.9
Y[2] = 276.9
Y[3] = 286.8
Y[4] = 286.9
..
CustomZone "Custom Zone 8"
NumVerts = 4
X[1] = 55.2
X[2] = 62.6
X[3] = 62.6
X[4] = 55.2
Y[1] = 287.3
Y[2] = 287.3
Y[3] = 295.95
Y[4] = 295.95
..
CustomZone "Custom Zone 10"
NumVerts = 4
X[1] = 25.85
X[2] = 25.85
X[3] = 46.9
X[4] = 46.9
Y[1] = 222.6
Y[2] = 207.35
Y[3] = 207.35
Y[4] = 222.45
..
CustomZone "Custom Zone 14"
NumVerts = 7
X[1] = 25.85
X[2] = 25.85
X[3] = 46.9
X[4] = 67
X[5] = 67
X[6] = 46.35
X[7] = 40.05
Y[1] = 276.6
Y[2] = 222.6
Y[3] = 222.45
Y[4] = 222.45
Y[5] = 276.6
Y[6] = 276.9
Y[7] = 276.9
..
CustomZone "Custom Zone 15"
NumVerts = 7
X[1] = 46.35
X[2] = 67
X[3] = 67
X[4] = 67
X[5] = 62.6
X[6] = 55.2
X[7] = 46.35
Y[1] = 276.9
Y[2] = 276.6
Y[3] = 282
Y[4] = 287.3
Y[5] = 287.3
Y[6] = 287.3
Y[7] = 286.8
..
CustomZone "Custom Zone 16"
NumVerts = 6
X[1] = 62.6
X[2] = 62.6
X[3] = 67
X[4] = 67
X[5] = 80.3
X[6] = 80.3
Y[1] = 295.95
Y[2] = 287.3
Y[3] = 287.3
Y[4] = 282
Y[5] = 282
Y[6] = 295.95
..
CustomZone "Custom Zone 17"
NumVerts = 7
X[1] = 67
X[2] = 67
X[3] = 67
X[4] = 46.9
X[5] = 46.9
X[6] = 80.3
X[7] = 80.3
Y[1] = 282
Y[2] = 276.6
Y[3] = 222.45
Y[4] = 222.45
Y[5] = 207.35
Y[6] = 207.35
Y[7] = 282
..
FacetWiz "Facet-0-0 4"
ParentZoneIdx = 0
SegmentNumber = 0
..
FacetWiz "Facet-0-1"
ParentZoneIdx = 0
SegmentNumber = 1
..
WinWiz "Custom Window 17"
X = 0.237154
Y = 0.237154
Width = 6
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-2"
ParentZoneIdx = 0
SegmentNumber = 2
..
WinWiz "Custom Window 18"
X = 0.372569
Y = 0.284585
Width = 9.66
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-5"
ParentZoneIdx = 3
SegmentNumber = 0
..
WinWiz "Custom Window 19"
X = 0.375415
Y = 0.25
Width = 14.5
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-7 8"
ParentZoneIdx = 4
SegmentNumber = 0
..
WinWiz "Custom Window 20"
X = 0.19
Y = 0.24
Width = 53.5
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
ShellWiz "Basement"
NamePrefix = "Bse"
ScreenIDArrIdx = 13
ScreenIDArrID = 132
GrossArea = 2800
FlrsAboveGrade = 0
FlrsBelowGrade = 1
ShellPos_Ref = "First Floor"
ShellPos_Dir = "Immediately Below"
ShellPos_Specify = 1
BldgX = 0
BldgY = 82
Footprint = "- custom -"
FlrToFlr = 12
FlrToCeiling = 12
ZoningPattern = "- custom -"
NumMCZnGrps = 0
DiagLink = "Basement Diag Data"
ZoningCurrent = 1
NumFloorVertices = 12
FloorVertX[1] = 32.4
FloorVertX[2] = 32.4
FloorVertX[3] = 76.75
FloorVertX[4] = 76.75
FloorVertX[5] = 80.9
FloorVertX[6] = 80.9
FloorVertX[7] = 89.9
FloorVertX[8] = 89.9
FloorVertX[9] = 60.9
FloorVertX[10] = 60.9
FloorVertX[11] = 60.9
FloorVertX[12] = 32.4
FloorVertY[1] = 178.75
FloorVertY[2] = 129.75
FloorVertY[3] = 129.75
FloorVertY[4] = 148.55
FloorVertY[5] = 148.55
FloorVertY[6] = 157.45
FloorVertY[7] = 157.45
FloorVertY[8] = 175.6
FloorVertY[9] = 175.6
FloorVertY[10] = 179.15
FloorVertY[11] = 207.6
FloorVertY[12] = 207.6
AdiabaticCurrent = 1
ZoneGroupsOK = 1
DfltZnGrpName[1] = "BseUnderground Areas"
DfltZnGrpName[2] = "BseGround Floor"
DfltZnGrpName[3] = "BseGround Floor"
DfltZnGrpName[4] = "BseTypical Floor(s)"
DfltZnGrpName[5] = "BseTypical Floor(s)"
DfltZnGrpName[6] = "BseTop Floor"
DfltZnGrpName[7] = "BseTop Floor"
DfltZnGrpName[8] = "BseData Center"
CustomFootprint = 1
CustomZoning = 1
ActiveZoneIndex = 2
CustomRoofZoning = -1
ActiveRoofZoneIdx = 1
FloorArea = 3221.06
FloorPerimLen = 270.7
LastFootprint = 1
SkyZonesCurrent = 1
SkyltZones[1] = 1
SkyltZones[2] = 1
SkyltZones[3] = 1
SkyltZones[4] = 1
SkyltZones[5] = 1
SkyPosCurrent = 1
DayltZones[1] = 1
DayltZones[2] = 1
DayltZones[3] = 1
DayltZones[4] = 1
DayltZones[5] = 0
DayltZones[201] = 1
DayltZones[202] = 1
DayltZones[203] = 1
DayltZones[204] = 1
DayltZones[205] = 0
DayltZones[401] = 1
DayltZones[402] = 1
DayltZones[403] = 1
DayltZones[404] = 1
DayltZones[405] = 0
WinDoorCurrent = 1
DetailsCurrent = ( 1, 1, 1 )
BDLNumDayltCtrls[1] = 0
BDLNumDayltCtrls[2] = 0
BDLNumDayltCtrls[3] = 0
BDLNumDayltCtrls[4] = 0
BDLNumDayltCtrls[5] = 0
BDLNumDayltCtrls[201] = 0
BDLNumDayltCtrls[202] = 0
BDLNumDayltCtrls[203] = 0
BDLNumDayltCtrls[204] = 0
BDLNumDayltCtrls[205] = 0
BDLNumDayltCtrls[401] = 0
BDLNumDayltCtrls[402] = 0
BDLNumDayltCtrls[403] = 0
BDLNumDayltCtrls[404] = 0
BDLNumDayltCtrls[405] = 0
OccShape = ( "EL3 Occup Profile (S1)", "EL3 Occup Profile (S2)",
"EL3 Occup Profile (S3)" )
ILShape = ( "EL3 InsLtg Profile (S1)", "EL3 InsLtg Profile (S2)",
"EL3 InsLtg Profile (S3)" )
ELDayShapes = ( "EL3 ExtLtg DayShape (Jan)",
"EL3 ExtLtg DayShape (Feb)",
"EL3 ExtLtg DayShape (Mar)",
"EL3 ExtLtg DayShape (Apr)",
"EL3 ExtLtg DayShape (May)",
"EL3 ExtLtg DayShape (Jun)",
"EL3 ExtLtg DayShape (Jul)",
"EL3 ExtLtg DayShape (Aug)",
"EL3 ExtLtg DayShape (Sep)",
"EL3 ExtLtg DayShape (Oct)",
"EL3 ExtLtg DayShape (Nov)",
"EL3 ExtLtg DayShape (Dec)" )
OEShape = ( "EL3 OffEq Profile (S1)", "EL3 OffEq Profile (S2)",
"EL3 OffEq Profile (S3)" )
CEShape = ( "EL3 CookEq Profile (S1)", "EL3 CookEq Profile (S2)",
"EL3 CookEq Profile (S3)" )
MiscShape = ( "EL3 Misc Profile (S1)", "EL3 Misc Profile (S2)",
"EL3 Misc Profile (S3)" )
RFDayShapes = ( "EL3 Refrig DayShape (Jan)",
"EL3 Refrig DayShape (Feb)",
"EL3 Refrig DayShape (Mar)",
"EL3 Refrig DayShape (Apr)",
"EL3 Refrig DayShape (May)",
"EL3 Refrig DayShape (Jun)",
"EL3 Refrig DayShape (Jul)",
"EL3 Refrig DayShape (Aug)",
"EL3 Refrig DayShape (Sep)",
"EL3 Refrig DayShape (Oct)",
"EL3 Refrig DayShape (Nov)",
"EL3 Refrig DayShape (Dec)" )
DHWShape = ( "EL3 DHW Profile (S1)", "EL3 DHW Profile (S2)",
"EL3 DHW Profile (S3)" )
SCRShape = ( "EL3 S-C Refrig Profile (S1)",
"EL3 S-C Refrig Profile (S2)",
"EL3 S-C Refrig Profile (S3)" )
RoofZoneErrorCode = 4
..
ShapeWiz "EL3 InsLtg Profile (S1)"
..
ShapeWiz "EL3 InsLtg Profile (S2)"
..
ShapeWiz "EL3 InsLtg Profile (S3)"
..
DayShape "EL3 ExtLtg DayShape (Jan)"
..
DayShape "EL3 ExtLtg DayShape (Feb)"
..
DayShape "EL3 ExtLtg DayShape (Mar)"
..
DayShape "EL3 ExtLtg DayShape (Apr)"
..
DayShape "EL3 ExtLtg DayShape (May)"
..
DayShape "EL3 ExtLtg DayShape (Jun)"
..
DayShape "EL3 ExtLtg DayShape (Jul)"
..
DayShape "EL3 ExtLtg DayShape (Aug)"
..
DayShape "EL3 ExtLtg DayShape (Sep)"
..
DayShape "EL3 ExtLtg DayShape (Oct)"
..
DayShape "EL3 ExtLtg DayShape (Nov)"
..
DayShape "EL3 ExtLtg DayShape (Dec)"
..
ShapeWiz "EL3 OffEq Profile (S1)"
..
ShapeWiz "EL3 OffEq Profile (S2)"
..
ShapeWiz "EL3 OffEq Profile (S3)"
..
ShapeWiz "EL3 CookEq Profile (S1)"
..
ShapeWiz "EL3 CookEq Profile (S2)"
..
ShapeWiz "EL3 CookEq Profile (S3)"
..
DayShape "EL3 Refrig DayShape (Jan)"
..
DayShape "EL3 Refrig DayShape (Feb)"
..
DayShape "EL3 Refrig DayShape (Mar)"
..
DayShape "EL3 Refrig DayShape (Apr)"
..
DayShape "EL3 Refrig DayShape (May)"
..
DayShape "EL3 Refrig DayShape (Jun)"
..
DayShape "EL3 Refrig DayShape (Jul)"
..
DayShape "EL3 Refrig DayShape (Aug)"
..
DayShape "EL3 Refrig DayShape (Sep)"
..
DayShape "EL3 Refrig DayShape (Oct)"
..
DayShape "EL3 Refrig DayShape (Nov)"
..
DayShape "EL3 Refrig DayShape (Dec)"
..
ShapeWiz "EL3 Misc Profile (S1)"
..
ShapeWiz "EL3 Misc Profile (S2)"
..
ShapeWiz "EL3 Misc Profile (S3)"
..
ShapeWiz "EL3 DHW Profile (S1)"
..
ShapeWiz "EL3 DHW Profile (S2)"
..
ShapeWiz "EL3 DHW Profile (S3)"
..
ShapeWiz "EL3 Occup Profile (S1)"
..
ShapeWiz "EL3 Occup Profile (S2)"
..
ShapeWiz "EL3 Occup Profile (S3)"
..
ShapeWiz "EL3 S-C Refrig Profile (S1)"
..
ShapeWiz "EL3 S-C Refrig Profile (S2)"
..
ShapeWiz "EL3 S-C Refrig Profile (S3)"
..
ZnGrpWiz "BseUnderground Areas"
ShortName = "Undgnd"
IsConditioned = 0
..
CustomZone "Custom Zone 12"
NumVerts = 4
X[1] = 32.4
X[2] = 32.4
X[3] = 60.9
X[4] = 60.9
Y[1] = 207.6
Y[2] = 178.75
Y[3] = 179.15
Y[4] = 207.6
..
CustomZone "Custom Zone 13"
NumVerts = 10
X[1] = 32.4
X[2] = 32.4
X[3] = 76.75
X[4] = 76.75
X[5] = 80.9
X[6] = 80.9
X[7] = 89.9
X[8] = 89.9
X[9] = 60.9
X[10] = 60.9
Y[1] = 178.75
Y[2] = 129.75
Y[3] = 129.75
Y[4] = 148.55
Y[5] = 148.55
Y[6] = 157.45
Y[7] = 157.45
Y[8] = 175.6
Y[9] = 175.6
Y[10] = 179.15
..
DiagData "Bldg Envelope & Loads 1 Diag Data"
PolyWndGridRes = 3
PolyWndLwrLeftX = -50.6
PolyWndLwrLeftY = 190.5
PolyWndWidth = 215.4
ShowCADLayer[1] = 1
ShowCADLayer[2] = 1
ShowCADLayer[3] = 1
ShowCADLayer[4] = 1
ShowCADLayer[5] = 1
ShowCADLayer[6] = 1
ShowCADLayer[7] = 1
ShowCADLayer[8] = 1
ShowCADLayer[9] = 1
ShowCADLayer[10] = 1
ShowCADLayer[11] = 1
ShowCADLayer[12] = 1
ShowCADLayer[13] = 1
ShowCADLayer[14] = 1
ShowCADLayer[15] = 1
ShowCADLayer[16] = 1
ShowCADLayer[17] = 1
CADFileComp = "UofM model First Floor - DWG"
..
DiagData "EL2 Bldg Envelope & Loads 1 Diag Data"
PolyWndGridRes = 3
PolyWndLwrLeftX = -54.15
PolyWndLwrLeftY = 196.25
PolyWndWidth = 215.4
ShowCADLayer[1] = 1
ShowCADLayer[2] = 1
ShowCADLayer[3] = 1
ShowCADLayer[4] = 1
ShowCADLayer[5] = 1
ShowCADLayer[6] = 1
ShowCADLayer[7] = 1
ShowCADLayer[8] = 1
ShowCADLayer[9] = 1
ShowCADLayer[10] = 1
ShowCADLayer[11] = 1
ShowCADLayer[12] = 1
ShowCADLayer[13] = 1
ShowCADLayer[14] = 1
ShowCADLayer[15] = 1
ShowCADLayer[16] = 1
CADFileComp = "UofM model Second Floor - DWG"
..
DiagData "Basement Diag Data"
PolyWndGridRes = 4
PolyWndLwrLeftX = -46.6
PolyWndLwrLeftY = 113.275
PolyWndWidth = 215.4
ShowCADLayer[1] = 1
ShowCADLayer[2] = 1
ShowCADLayer[3] = 1
ShowCADLayer[4] = 1
ShowCADLayer[5] = 1
ShowCADLayer[6] = 1
CADFileComp = "UofM model Basement - DWG"
..
CADFile "UofM model First Floor - DWG"
ScaleUnits = 0
ScaleValue = 1
OriginX = -2360.29
OriginY = -1622.08
Azimuth = 0
..
CADFile "UofM model Second Floor - DWG"
ScaleUnits = 0
ScaleValue = 1
OriginX = -2360.29
OriginY = -1690.07
Azimuth = 0
..
CADFile "UofM model Basement - DWG"
ScaleUnits = 0
ScaleValue = 1
OriginX = -2350.91
OriginY = -630.331
Azimuth = 0
..
HVACWiz "HVAC System 1"
ScreenIDArrIdx = 0
HeatSource[1] = "Hot Water Coils"
SystemPerWhat[1] = "System per Zone"
..
DXCWWiz "Water-Cooled DX System"
..
WSECWWiz "Wtr-Side Econo System"
..
WLHPWiz "WSHP System"
..
GSHPWiz "GSHP System"
..
PrimWiz "Primary HVAC Plant"
HWScrnIDArrIdx = 0
HWSysLoopFlow = "Variable"
HWSysPumpCtrl = "VSD"
BoilerType[1] = "Steam Boiler (Natural Draft)"
..
DHWWiz "DHW Plant 1"
ScreenIDArrIdx = 0
DHWFuel = "Electricity"
..
FacetColor "By Wall Type"
FacetType = "Walls"
ColorOption = "By Wall Type"
..
FacetColor "By Construction"
FacetType = "Walls"
ColorOption = "By Construction"
..
FacetColor "Uniform"
FacetType = "Windows"
ColorOption = "Uniform"
..
FacetColor "By Glass Type"
FacetType = "Windows"
ColorOption = "By Glass Type"
..
Light3D "Light3D - Default"
Type = "Default"
..
Light3D "Light3D - User1"
Type = "User Defined 1"
..
Light3D "Light3D - User2"
Type = "User Defined 2"
..
Light3D "Light3D - User3"
Type = "User Defined 3"
..
Light3D "Light3D - User4"
Type = "User Defined 4"
..
Light3D "Light3D - User5"
Type = "User Defined 5"
..
ERateWiz "UofM elec"
Version = 1
CustChargeAmt[1] = 0
UniformChargeKW[1] = 0
UniformChargeKWH[1] = 0.085
TOUPeriodsChecked = 1
TOUPeriodErrSeas1 = " "
TOUPeriodErrS1b = " "
..
FRateWiz "Custom Gas Rate"
Version = 1
CustChargeAmt[1] = 10
UniformChargeUse[1] = 0.95
..
END_OF_FILE
-------------- next part --------------
INPUT ..
$ ---------------------------------------------------------
$ Abort, Diagnostics
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Global Parameters
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Title, Run Periods, Design Days, Holidays
$ ---------------------------------------------------------
TITLE
LINE-1 = *UofM Athletic Addition proposed*
..
"Entire Year" = RUN-PERIOD-PD
BEGIN-MONTH = 1
BEGIN-DAY = 1
BEGIN-YEAR = 2014
END-MONTH = 12
END-DAY = 31
END-YEAR = 2014
..
"Standard US Holidays" = HOLIDAYS
LIBRARY-ENTRY "US"
..
$ ---------------------------------------------------------
$ Compliance Data
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Site and Building Data
$ ---------------------------------------------------------
"Site Data" = SITE-PARAMETERS
ALTITUDE = 0
..
"Building Data" = BUILD-PARAMETERS
HOLIDAYS = "Standard US Holidays"
..
PROJECT-DATA
..
$ ---------------------------------------------------------
$ Materials / Layers / Constructions
$ ---------------------------------------------------------
"1stEWall Cons Mat 2 (16.34)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 16.34
..
"2ndRoof Cons Mat 4 (31.45)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 31.45
..
"1stUFMat (G.NW1.U2.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 1.25183
..
"1stUFMat (G.E2.U3.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 0.1
..
"1stUFMat (G.E3.U4.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 2.42182
..
"1stUFMat (G.N4.U5.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 7.50989
..
"1stUFMat (G.S5.U6.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 5.01542
..
"BseUFMat (B.N1.U2.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 100
..
"BseUWMat (B.N1.U2.M1)" = MATERIAL
TYPE = RESISTANCE
RESISTANCE = 3.00557
..
"1stEWall Cons Layers" = LAYERS
MATERIAL = ( "Stucco 1in (SC01)", "Insul Bd 3/4in (IN62)",
"1stEWall Cons Mat 2 (16.34)", "GypBd 1/2in (GP01)" )
..
"1stCeilg Cons Layers" = LAYERS
MATERIAL = ( "AcousTile 1/2in (AC02)" )
..
"1stIFlr Cons Layers" = LAYERS
MATERIAL = ( "Conc HW 140lb 6in (HF-C13)" )
..
"2ndRoof Cons Layers" = LAYERS
MATERIAL = ( "Blt-Up Roof 3/8in (BR01)", "Bldg Paper Felt (BP01)",
"Plywd 5/8in (PW04)", "2ndRoof Cons Mat 4 (31.45)",
"AcousTile 1/2in (AC02)" )
..
"1stUFLyrs (G.NW1.U2)" = LAYERS
MATERIAL = ( "1stUFMat (G.NW1.U2.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.E2.U3)" = LAYERS
MATERIAL = ( "1stUFMat (G.E2.U3.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.E3.U4)" = LAYERS
MATERIAL = ( "1stUFMat (G.E3.U4.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.N4.U5)" = LAYERS
MATERIAL = ( "1stUFMat (G.N4.U5.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"1stUFLyrs (G.S5.U6)" = LAYERS
MATERIAL = ( "1stUFMat (G.S5.U6.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"BseUFLyrs (B.N1.U2)" = LAYERS
MATERIAL = ( "BseUFMat (B.N1.U2.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 12in (HF-C11)" )
..
"BseUWLyrs (B.N1.U2)" = LAYERS
MATERIAL = ( "BseUWMat (B.N1.U2.M1)", "Light Soil, Damp 12in",
"Conc HW 140lb 6in (HF-C13)" )
..
"Exterior Wall Assembly" = CONSTRUCTION
TYPE = U-VALUE
ABSORPTANCE = 0.6
ROUGHNESS = 1
U-VALUE = 0.041
..
"1stCeilg Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stCeilg Cons Layers"
..
"1stIWall Construction" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.05
..
"1stIFlr Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"1stIFlSP Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"Roof Assembly" = CONSTRUCTION
TYPE = U-VALUE
ABSORPTANCE = 0.7
ROUGHNESS = 1
U-VALUE = 0.018
..
"2ndGFlr Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"2ndGFlSP Construction" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stIFlr Cons Layers"
..
"1stUFCons (G.NW1.U2)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.NW1.U2)"
..
"1stUFCons (G.E2.U3)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.E2.U3)"
..
"1stUFCons (G.E3.U4)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.E3.U4)"
..
"1stUFCons (G.N4.U5)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.N4.U5)"
..
"1stUFCons (G.S5.U6)" = CONSTRUCTION
TYPE = LAYERS
LAYERS = "1stUFLyrs (G.S5.U6)"
..
"Below Grade Floor Assembly" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.54
..
"Below Grade Wall Assembly" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.119
..
"Dbl Lyr Unins Mtl Door" = CONSTRUCTION
TYPE = U-VALUE
U-VALUE = 0.7
..
$ ---------------------------------------------------------
$ Glass Type Codes
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Glass Types
$ ---------------------------------------------------------
"Prop Windows" = GLASS-TYPE
TYPE = SHADING-COEF
SHADING-COEF = 0.29
GLASS-CONDUCT = 0.39
VIS-TRANS = 0.43
..
$ ---------------------------------------------------------
$ Window Layers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Lamps / Luminaries / Lighting Systems
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Day Schedules
$ ---------------------------------------------------------
"1stBldg Occup S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, 0.0005, 0.0039, 0.005, &D, &D,
0.0028, &D, 0.005, &D, &D, 0.0039, 0.0016, 0.0005, &D, &D, &D, 0 )
..
"1stBldg Occup S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, 0.054, 0.225, 0.9, &D, &D,
0.783, &D, 0.801, &D, 0.711, 0.414, 0.207, 0.387, &D, 0.288, 0.099,
0.045, 0 )
..
"1stBldg Occup S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"1stBldg InsLt S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.0512, 0.0535, 0.054, &D,
&D, &D, &D, &D, &D, &D, 0.0535, 0.0521, 0.0512, &D, 0.0502, &D,
0.05 )
..
"1stBldg InsLt S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.1605, 0.424, 0.9, &D, &D,
&D, &D, &D, 1, 0.713, 0.611, 0.5005, 0.679, &D, 0.6705, 0.288,
0.101, 0.05 )
..
"1stBldg InsLt S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"1stBldg Misc S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.051, &D, &D, &D, &D, &D, 0.0514, 0.0536, 0.054, &D,
&D, &D, &D, &D, &D, &D, &D, 0.0523, 0.0514, &D, 0.051 )
..
"1stBldg Misc S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.058, &D, &D, &D, &D, &D, 0.1085, 0.4201, 0.9, &D,
&D, &D, &D, &D, &D, 0.7063, 0.6137, 0.5043, 0.6811, &D, 0.6727,
0.2938, 0.1085, 0.058 )
..
"1stBldg Misc S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"BseBldg OffEq S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05 )
..
"BseBldg OffEq S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.1355, 0.6143, 0.905, &D,
&D, 0.5886, &D, 0.8879, &D, 0.8622, 0.6571, 0.3151, 0.2039, &D,
0.1868, 0.144, 0.0586, 0.05 )
..
"BseBldg OffEq S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"BseBldg SCRfg S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6636, &D, 0.656, &D, &D, 0.6636, 0.6723, 0.6887,
0.705, 0.7301, 0.7465, 0.7563, 0.765, &D, &D, &D, 0.7563, 0.7465,
0.7377, 0.729, 0.7127, 0.6876, 0.6723, 0.6636 )
..
"BseBldg SCRfg S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.64, &D, &D, &D, &D, 0.6556, 0.6712, 0.731, 0.7908,
0.8558, &D, 0.8818, 0.9, &D, &D, &D, 0.8818, 0.874, 0.8454, 0.8168,
0.7726, 0.7206, 0.6972, 0.6556 )
..
"BseBldg SCRfg S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"BseBldg Cook S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, 0.0011, &D, 0.0005, &D, 0.0016,
0.0032, 0.004, 0.0024, 0.0011, 0.0005, &D, &D, &D, 0.0003, 0 )
..
"BseBldg Cook S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, 0.1407, 0.2881, 0.1541, 0.1072, 0.0536,
0.0134, 0.0603, 0.1407, 0.2278, 0.1206, 0.0268, 0.1474, 0.3819,
0.67, 0.3819, 0.1474, 0.0603, 0 )
..
"BseBldg Cook S2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"Ext Lighting W1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, &D, &D, &D, 0.3, 0.1, 0, &D, &D, &D,
&D, &D, 0.1, 0.55, 0.9, &D, &D, &D, &D, 0.8, 0.7 )
..
"Ext Lighting W2 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, &D, 0.45, 0.15, 0, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 0.25, 0.7, 0.9, &D, &D, 0.8, 0.7 )
..
"Ext Lighting W5 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, 0.3, 0, &D, &D, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, &D, &D, 0.25, 0.8, &D, 0.7 )
..
"Ext Lighting W8 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.6, &D, &D, &D, &D, 0.45, 0.25, 0, &D, &D, &D, &D,
&D, &D, &D, &D, 0.1, 0.5, 0.9, &D, &D, &D, 0.8, 0.7 )
..
"DHW Eqp NRes W1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.03 )
..
"DHW Eqp NRes W2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.2, 0.5975, 0.7025, 0.8,
&D, &D, &D, &D, &D, &D, 0.7025, 0.5, &D, &D, 0.4025, 0.2, 0.1025,
0.05 )
..
"DHW Eqp NRes W2 HDD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"ZG0-S1 (PVAVS) P-Inf S1 All" = DAY-SCHEDULE-PD
TYPE = MULTIPLIER
VALUES = ( 1 )
..
"ZG0-S1 (PVAVS) P-Inf S2 WD" = DAY-SCHEDULE-PD
TYPE = MULTIPLIER
VALUES = ( 1, &D, &D, &D, &D, 1.004, 1.175, 1.25, &D, 0.5, 0.701,
&D, 0.5, &D, 0.62, 1.25, &D, 0.971, 1.13, 1.049, 1.238, 1.193,
1.049, 1 )
..
"ZG0-S1 (PVAVS) P-Inf S2 HDD" = DAY-SCHEDULE-PD
TYPE = MULTIPLIER
VALUES = ( 1, &D, &D, &D, &D, &D, &D, 0.5, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 1 )
..
"ZG0-S1 (PVAVS) C-Inf S1 All" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 1 )
..
"ZG0-S1 (PVAVS) C-Inf S2 WD" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 1, &D, &D, &D, &D, &D, &D, 0.5, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 1 )
..
"S1 Sys1 (PVAVS) Fan S1 All" = DAY-SCHEDULE-PD
TYPE = ON/OFF/FLAG
VALUES = ( 0 )
..
"S1 Sys1 (PVAVS) Fan S2 WD" = DAY-SCHEDULE-PD
TYPE = ON/OFF/FLAG
VALUES = ( 0, &D, &D, &D, &D, &D, &D, 1, &D, &D, &D, &D, &D, &D,
&D, &D, &D, &D, 0 )
..
"S1 Sys1 (PVAVS) Cool S1 All" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 82 )
..
"S1 Sys1 (PVAVS) Cool S2 WD" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 82, &D, &D, &D, &D, &D, &D, 76, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 82 )
..
"S1 Sys1 (PVAVS) Heat S1 All" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64 )
..
"S1 Sys1 (PVAVS) Heat S2 WD" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64, &D, &D, &D, &D, &D, &D, 70, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 64 )
..
"S1 1stSys1 (PVAVS) (G.NW1) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.E2) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.E3) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.N4) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 1stSys1 (PVAVS) (G.S5) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S12ndSys1 (PVAVS) (G.NNW1) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.C2) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.N3) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.SW4) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.W5) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.C6) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S1 2ndSys1 (PVAVS) (G.NE7) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"S12ndSys1 (PVAVS) (G.ESE8) CRS-D" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 80
OUTSIDE-LO = 60
SUPPLY-HI = 65
SUPPLY-LO = 55
..
"Cust 1 Elec Seas1 Day" = DAY-SCHEDULE-PD
TYPE = FLAG
VALUES = ( 1 )
..
"Day Schedule 50" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D, &D,
&D, 1, 0 )
..
"Day Schedule 51" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0.05, &D, &D, &D, &D, &D, 0.1605, 0.424, 0.9, &D, &D,
&D, &D, &D, &D, 0.713, 0.611, 0.5005, 0.679, &D, 0.6705, 0.288,
0.101, 0.05 )
..
"Day Schedule 52" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
"Day Schedule 53" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64 )
..
"Day Schedule 54" = DAY-SCHEDULE-PD
TYPE = TEMPERATURE
VALUES = ( 64, &D, &D, &D, &D, &D, &D, 70, &D, &D, &D, &D, &D,
&D, &D, &D, &D, &D, 64 )
..
"Elevator sch week day" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0, &D, &D, &D, &D, &D, &D, &D, &D, 1, 0 )
..
"Elevator sch weekend" = DAY-SCHEDULE-PD
TYPE = FRACTION
VALUES = ( 0 )
..
$ ---------------------------------------------------------
$ Week Schedules
$ ---------------------------------------------------------
"1stBldg Occup S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Occup S1 All" )
..
"1stBldg Occup S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Occup S2 WD", &D, &D, &D, &D,
"1stBldg Occup S1 All", &D, &D, "1stBldg Occup S2 HDD" )
..
"1stBldg InsLt S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg InsLt S1 All" )
..
"1stBldg InsLt S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg InsLt S2 WD", &D, &D, &D, &D,
"1stBldg InsLt S1 All", &D, &D, "1stBldg InsLt S2 HDD" )
..
"1stBldg Misc S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Misc S1 All" )
..
"1stBldg Misc S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "1stBldg Misc S2 WD", &D, &D, &D, &D,
"1stBldg Misc S1 All", &D, &D, "1stBldg Misc S2 HDD" )
..
"BseBldg OffEq S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg OffEq S1 All" )
..
"BseBldg OffEq S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg OffEq S2 WD", &D, &D, &D, &D,
"BseBldg OffEq S1 All", &D, &D, "BseBldg OffEq S2 HDD" )
..
"BseBldg SCRfg S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg SCRfg S1 All" )
..
"BseBldg SCRfg S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg SCRfg S2 WD", &D, &D, &D, &D,
"BseBldg SCRfg S1 All", &D, &D, "BseBldg SCRfg S2 HDD" )
..
"BseBldg Cook S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg Cook S1 All" )
..
"BseBldg Cook S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "BseBldg Cook S2 WD", &D, &D, &D, &D,
"BseBldg Cook S1 All", &D, &D, "BseBldg Cook S2 HDD" )
..
"Ext Lighting Wk1" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W1 All" )
..
"Ext Lighting Wk2" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W2 All" )
..
"Ext Lighting Wk5" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W5 All" )
..
"Ext Lighting Wk8" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Ext Lighting W8 All" )
..
"DHW Eqp NRes Wk1" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "DHW Eqp NRes W1 All" )
..
"DHW Eqp NRes Wk2" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "DHW Eqp NRes W2 WD", &D, &D, &D, &D,
"DHW Eqp NRes W1 All", &D, &D, "DHW Eqp NRes W2 HDD" )
..
"ZG0-S1 (PVAVS) P-Inf S1 Wk" = WEEK-SCHEDULE-PD
TYPE = MULTIPLIER
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) P-Inf S1 All" )
..
"ZG0-S1 (PVAVS) P-Inf S2 Wk" = WEEK-SCHEDULE-PD
TYPE = MULTIPLIER
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) P-Inf S2 WD", &D, &D, &D, &D,
"ZG0-S1 (PVAVS) P-Inf S1 All", &D, &D,
"ZG0-S1 (PVAVS) P-Inf S2 HDD" )
..
"ZG0-S1 (PVAVS) C-Inf S1 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) C-Inf S1 All" )
..
"ZG0-S1 (PVAVS) C-Inf S2 Wk" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "ZG0-S1 (PVAVS) C-Inf S2 WD", &D, &D, &D, &D,
"ZG0-S1 (PVAVS) C-Inf S1 All" )
..
"S1 Sys1 (PVAVS) Fan S1 Wk" = WEEK-SCHEDULE-PD
TYPE = ON/OFF/FLAG
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Fan S1 All" )
..
"S1 Sys1 (PVAVS) Fan S2 Wk" = WEEK-SCHEDULE-PD
TYPE = ON/OFF/FLAG
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Fan S2 WD", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Fan S1 All" )
..
"S1 Sys1 (PVAVS) Cool S1 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Cool S1 All" )
..
"S1 Sys1 (PVAVS) Cool S2 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Cool S2 WD", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Cool S1 All" )
..
"S1 Sys1 (PVAVS) Heat S1 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S1 All" )
..
"S1 Sys1 (PVAVS) Heat S2 Wk" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S2 WD", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Heat S1 All" )
..
"S1 1stSys1 (PVAVS) (G.NW1) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.NW1) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.E2) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E2) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.E3) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E3) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.N4) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.N4) CRS-D" )
..
"S1 1stSys1 (PVAVS) (G.S5) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.S5) CRS-D" )
..
"S12ndSys1 (PVAVS) (G.NNW1) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.NNW1) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.C2) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C2) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.N3) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.N3) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.SW4) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.SW4) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.W5) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.W5) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.C6) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C6) CRS-D" )
..
"S1 2ndSys1 (PVAVS) (G.NE7) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.NE7) CRS-D" )
..
"S12ndSys1 (PVAVS) (G.ESE8) CRS-W" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.ESE8) CRS-D" )
..
"Cust 1 Elec Seas1 Week" = WEEK-SCHEDULE-PD
TYPE = FLAG
DAY-SCHEDULES = ( "Cust 1 Elec Seas1 Day" )
..
"Week Schedule 41" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Day Schedule 50", &D, &D, &D, &D,
"1stBldg InsLt S2 HDD" )
..
"Week Schedule 42" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Day Schedule 51", &D, &D, &D, &D,
"1stBldg InsLt S1 All", &D, &D, "Day Schedule 52" )
..
"Week Schedule 43" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "Day Schedule 53" )
..
"Week Schedule 44" = WEEK-SCHEDULE-PD
TYPE = TEMPERATURE
DAY-SCHEDULES = ( "Day Schedule 54", &D, &D, &D, &D,
"S1 Sys1 (PVAVS) Heat S1 All" )
..
"Elevator sch Week" = WEEK-SCHEDULE-PD
TYPE = FRACTION
DAY-SCHEDULES = ( "Elevator sch week day", "Elevator sch weekend",
"Elevator sch weekend", &D, "Elevator sch weekend",
"Elevator sch weekend" )
..
$ ---------------------------------------------------------
$ Annual Schedules
$ ---------------------------------------------------------
"1stBldg Occup Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "1stBldg Occup S1 Wk", "1stBldg Occup S2 Wk",
"1stBldg Occup S1 Wk", "1stBldg Occup S2 Wk", "1stBldg Occup S1 Wk",
"1stBldg Occup S2 Wk", "1stBldg Occup S1 Wk", "1stBldg Occup S2 Wk",
"1stBldg Occup S1 Wk" )
..
"1stBldg InsLt Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "1stBldg InsLt S1 Wk", "1stBldg InsLt S2 Wk",
"1stBldg InsLt S1 Wk", "1stBldg InsLt S2 Wk", "1stBldg InsLt S1 Wk",
"1stBldg InsLt S2 Wk", "1stBldg InsLt S1 Wk", "1stBldg InsLt S2 Wk",
"1stBldg InsLt S1 Wk" )
..
"1stBldg Misc Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "1stBldg Misc S1 Wk", "1stBldg Misc S2 Wk",
"1stBldg Misc S1 Wk", "1stBldg Misc S2 Wk", "1stBldg Misc S1 Wk",
"1stBldg Misc S2 Wk", "1stBldg Misc S1 Wk", "1stBldg Misc S2 Wk",
"1stBldg Misc S1 Wk" )
..
"BseBldg OffEq Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "BseBldg OffEq S1 Wk", "BseBldg OffEq S2 Wk",
"BseBldg OffEq S1 Wk", "BseBldg OffEq S2 Wk", "BseBldg OffEq S1 Wk",
"BseBldg OffEq S2 Wk", "BseBldg OffEq S1 Wk", "BseBldg OffEq S2 Wk",
"BseBldg OffEq S1 Wk" )
..
"BseBldg SCRfg Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "BseBldg SCRfg S1 Wk", "BseBldg SCRfg S2 Wk",
"BseBldg SCRfg S1 Wk", "BseBldg SCRfg S2 Wk", "BseBldg SCRfg S1 Wk",
"BseBldg SCRfg S2 Wk", "BseBldg SCRfg S1 Wk", "BseBldg SCRfg S2 Wk",
"BseBldg SCRfg S1 Wk" )
..
"BseBldg Cook Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "BseBldg Cook S1 Wk", "BseBldg Cook S2 Wk",
"BseBldg Cook S1 Wk", "BseBldg Cook S2 Wk", "BseBldg Cook S1 Wk",
"BseBldg Cook S2 Wk", "BseBldg Cook S1 Wk", "BseBldg Cook S2 Wk",
"BseBldg Cook S1 Wk" )
..
"Ext Lighting Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12 )
DAY = ( 31, 28, 31, 30, 31, 30, 31, 31, 30, 31, 30, 31 )
WEEK-SCHEDULES = ( "Ext Lighting Wk1", "Ext Lighting Wk2",
"Ext Lighting Wk2", "Ext Lighting Wk2", "Ext Lighting Wk5",
"Ext Lighting Wk5", "Ext Lighting Wk5", "Ext Lighting Wk8",
"Ext Lighting Wk8", "Ext Lighting Wk8", "Ext Lighting Wk1",
"Ext Lighting Wk1" )
..
"DHW Eqp NRes Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "DHW Eqp NRes Wk1", "DHW Eqp NRes Wk2",
"DHW Eqp NRes Wk1", "DHW Eqp NRes Wk2", "DHW Eqp NRes Wk1",
"DHW Eqp NRes Wk2", "DHW Eqp NRes Wk1", "DHW Eqp NRes Wk2",
"DHW Eqp NRes Wk1" )
..
"ZG0-S1 (PVAVS) P-Inf Sch" = SCHEDULE-PD
TYPE = MULTIPLIER
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk",
"ZG0-S1 (PVAVS) P-Inf S2 Wk", "ZG0-S1 (PVAVS) P-Inf S1 Wk" )
..
"ZG0-S1 (PVAVS) C-Inf Sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk",
"ZG0-S1 (PVAVS) C-Inf S2 Wk", "ZG0-S1 (PVAVS) C-Inf S1 Wk" )
..
"S1 Sys1 (PVAVS) Fan Sch" = SCHEDULE-PD
TYPE = ON/OFF/FLAG
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk",
"S1 Sys1 (PVAVS) Fan S2 Wk", "S1 Sys1 (PVAVS) Fan S1 Wk" )
..
"S1 Sys1 (PVAVS) Cool Sch" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk",
"S1 Sys1 (PVAVS) Cool S2 Wk", "S1 Sys1 (PVAVS) Cool S1 Wk" )
..
"S1 Sys1 (PVAVS) Heat Sch" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S2 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk" )
..
"S1 1stSys1 (PVAVS) (G.NW1) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.NW1) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.E2) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E2) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.E3) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.E3) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.N4) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.N4) CRS-W" )
..
"S1 1stSys1 (PVAVS) (G.S5) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 1stSys1 (PVAVS) (G.S5) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.NNW1) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.NNW1) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.C2) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C2) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.N3) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.N3) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.SW4) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.SW4) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.W5) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.W5) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.C6) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.C6) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.NE7) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S1 2ndSys1 (PVAVS) (G.NE7) CRS-W" )
..
"S1 2ndSys1 (PVAVS) (G.ESE8) CRS" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "S12ndSys1 (PVAVS) (G.ESE8) CRS-W" )
..
"Cust 1 Elec Season Sched" = SCHEDULE-PD
TYPE = FLAG
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "Cust 1 Elec Seas1 Week" )
..
"Lighting Low occ year" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "Week Schedule 41", "Week Schedule 41",
"Week Schedule 41", "Week Schedule 41", "Week Schedule 41",
"Week Schedule 41", "Week Schedule 41", "Week Schedule 41",
"Week Schedule 41" )
..
"Unocc Heat Shc" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 3, 4, 6, 7, 9, 10, 12, 12 )
DAY = ( 6, 22, 7, 14, 14, 20, 6, 13, 31 )
WEEK-SCHEDULES = ( "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk",
"S1 Sys1 (PVAVS) Heat S1 Wk", "S1 Sys1 (PVAVS) Heat S1 Wk" )
..
"GYMNASIUM LTG" = SCHEDULE-PD
LIBRARY-ENTRY "GYMNASIUM LTG"
..
"Elevator sch" = SCHEDULE-PD
TYPE = FRACTION
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "Elevator sch Week" )
..
$ ---------------------------------------------------------
$ Polygons
$ ---------------------------------------------------------
"1stFloor Polygon" = POLYGON
V1 = ( 32.4, 290.3 )
V2 = ( 32.4, 271.1 )
V3 = ( 32.4, 228.9 )
V4 = ( 32.4, 201.65 )
V5 = ( 81.65, 201.5 )
V6 = ( 81.65, 221.4 )
V7 = ( 61.65, 221.4 )
V8 = ( 61.65, 228.95 )
V9 = ( 61.85, 271.1 )
V10 = ( 46.35, 271.1 )
V11 = ( 46.35, 281.15 )
V12 = ( 55.15, 281.15 )
V13 = ( 62.6, 281.15 )
V14 = ( 62.6, 290.3 )
V15 = ( 55.4, 290.3 )
..
"1stSpace Polygon 1" = POLYGON
V1 = ( 0, 0 )
V2 = ( 19.2, 0 )
V3 = ( 19.2, 7.15 )
V4 = ( 9.15, 7.15 )
V5 = ( 9.15, 13.95 )
V6 = ( 9.15, 22.75 )
V7 = ( 0, 23 )
..
"1stSpace Polygon 2" = POLYGON
V1 = ( 0, 0 )
V2 = ( 7.45, 0 )
V3 = ( 7.45, 9.15 )
V4 = ( 0.25, 9.15 )
..
"1stSpace Polygon 3" = POLYGON
V1 = ( 0, 0 )
V2 = ( 10.05, 0 )
V3 = ( 10.05, 6.8 )
V4 = ( 0, 6.8 )
..
"1stSpace Polygon 4" = POLYGON
V1 = ( 0, 0 )
V2 = ( 42.2, 0 )
V3 = ( 42.15, 29.25 )
V4 = ( 0, 29.45 )
V5 = ( 0, 13.95 )
V6 = ( 0, 7.15 )
..
"1stSpace Polygon 5" = POLYGON
V1 = ( 0, 0 )
V2 = ( 27.25, 0 )
V3 = ( 27.4, 49.25 )
V4 = ( 7.5, 49.25 )
V5 = ( 7.5, 29.25 )
V6 = ( -0.05, 29.25 )
..
"2ndFloor Polygon" = POLYGON
V1 = ( 25.85, 276.6 )
V2 = ( 25.85, 222.6 )
V3 = ( 25.85, 207.35 )
V4 = ( 46.9, 207.35 )
V5 = ( 80.3, 207.35 )
V6 = ( 80.3, 282 )
V7 = ( 80.3, 295.95 )
V8 = ( 62.1, 295.95 )
V9 = ( 55.2, 295.95 )
V10 = ( 32.4, 295.95 )
V11 = ( 32.4, 287.1 )
V12 = ( 25.85, 287.1 )
..
"2ndSpace Polygon 1" = POLYGON
V1 = ( 0, 0 )
V2 = ( 8.85, 0 )
V3 = ( 8.85, -6.55 )
V4 = ( 19.35, -6.55 )
V5 = ( 19.05, 7.65 )
V6 = ( 9.05, 7.65 )
V7 = ( 9.15, 13.95 )
V8 = ( 8.65, 22.8 )
V9 = ( 0, 22.8 )
..
"2ndSpace Polygon 2" = POLYGON
V1 = ( 0, 0 )
V2 = ( 6.3, 0 )
V3 = ( 6.3, 9.9 )
V4 = ( 0, 10 )
..
"2ndSpace Polygon 3" = POLYGON
V1 = ( 0, 0 )
V2 = ( 8.65, 0 )
V3 = ( 8.65, 7.4 )
V4 = ( 0, 7.4 )
..
"2ndSpace Polygon 4" = POLYGON
V1 = ( 0, 0 )
V2 = ( 15.25, 0 )
V3 = ( 15.25, 21.05 )
V4 = ( 0.15, 21.05 )
..
"2ndSpace Polygon 5" = POLYGON
V1 = ( 0, 0 )
V2 = ( 54, 0 )
V3 = ( 54.15, 21.05 )
V4 = ( 54.15, 41.15 )
V5 = ( -0, 41.15 )
V6 = ( -0.3, 20.5 )
V7 = ( -0.3, 14.2 )
..
"2ndSpace Polygon 6" = POLYGON
V1 = ( 0, 0 )
V2 = ( 20.65, -0.3 )
V3 = ( 20.65, 5.1 )
V4 = ( 20.65, 10.4 )
V5 = ( 16.25, 10.4 )
V6 = ( 8.85, 10.4 )
V7 = ( 0, 9.9 )
..
"2ndSpace Polygon 7" = POLYGON
V1 = ( 0, 0 )
V2 = ( 13.95, 0 )
V3 = ( 13.95, 17.7 )
V4 = ( 5.3, 17.7 )
V5 = ( 5.3, 13.3 )
V6 = ( 0, 13.3 )
..
"2ndSpace Polygon 8" = POLYGON
V1 = ( 0, 0 )
V2 = ( 33.4, 0 )
V3 = ( 33.4, 74.65 )
V4 = ( 20.1, 74.65 )
V5 = ( 20.1, 15.1 )
V6 = ( 0, 15.1 )
..
"BseFloor Polygon" = POLYGON
V1 = ( 32.4, 178.75 )
V2 = ( 32.4, 129.75 )
V3 = ( 76.75, 129.75 )
V4 = ( 76.75, 148.55 )
V5 = ( 80.9, 148.55 )
V6 = ( 80.9, 157.45 )
V7 = ( 89.9, 157.45 )
V8 = ( 89.9, 175.6 )
V9 = ( 60.9, 175.6 )
V10 = ( 60.9, 179.15 )
V11 = ( 60.9, 207.6 )
V12 = ( 32.4, 207.6 )
..
"BseSpace Polygon 1" = POLYGON
V1 = ( 0, 0 )
V2 = ( 28.85, 0 )
V3 = ( 28.45, 28.5 )
V4 = ( 0, 28.5 )
..
"BseSpace Polygon 2" = POLYGON
V1 = ( 0, 0 )
V2 = ( 49, 0 )
V3 = ( 49, 44.35 )
V4 = ( 30.2, 44.35 )
V5 = ( 30.2, 48.5 )
V6 = ( 21.3, 48.5 )
V7 = ( 21.3, 57.5 )
V8 = ( 3.15, 57.5 )
V9 = ( 3.15, 28.5 )
V10 = ( -0.4, 28.5 )
..
"1stSpace Polygon 1 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 23, 0 )
V3 = ( 22.75, 9.15 )
V4 = ( 13.95, 9.15 )
V5 = ( 7.15, 9.15 )
V6 = ( 7.15, 19.2 )
V7 = ( 0, 19.2 )
..
"1stSpace Polygon 2 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 9.15, 0.25 )
V3 = ( 9.15, 7.45 )
V4 = ( 0, 7.45 )
..
"1stSpace Polygon 3 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 6.8, 0 )
V3 = ( 6.8, 10.05 )
V4 = ( 0, 10.05 )
..
"1stSpace Polygon 4 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 7.15, 0 )
V3 = ( 13.95, 0 )
V4 = ( 29.45, 0 )
V5 = ( 29.25, 42.15 )
V6 = ( 0, 42.2 )
..
"1stSpace Polygon 5 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 29.25, -0.05 )
V3 = ( 29.25, 7.5 )
V4 = ( 49.25, 7.5 )
V5 = ( 49.25, 27.4 )
V6 = ( 0, 27.25 )
..
"2ndSpace Polygon 1 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 22.8, 0 )
V3 = ( 22.8, 8.65 )
V4 = ( 13.95, 9.15 )
V5 = ( 7.65, 9.05 )
V6 = ( 7.65, 19.05 )
V7 = ( -6.55, 19.35 )
V8 = ( -6.55, 8.85 )
V9 = ( 0, 8.85 )
..
"2ndSpace Polygon 2 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 10, 0 )
V3 = ( 9.9, 6.3 )
V4 = ( 0, 6.3 )
..
"2ndSpace Polygon 3 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 7.4, 0 )
V3 = ( 7.4, 8.65 )
V4 = ( 0, 8.65 )
..
"2ndSpace Polygon 4 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 21.05, 0.15 )
V3 = ( 21.05, 15.25 )
V4 = ( 0, 15.25 )
..
"2ndSpace Polygon 5 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 14.2, -0.3 )
V3 = ( 20.5, -0.3 )
V4 = ( 41.15, -0 )
V5 = ( 41.15, 54.15 )
V6 = ( 21.05, 54.15 )
V7 = ( 0, 54 )
..
"2ndSpace Polygon 6 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 9.9, 0 )
V3 = ( 10.4, 8.85 )
V4 = ( 10.4, 16.25 )
V5 = ( 10.4, 20.65 )
V6 = ( 5.1, 20.65 )
V7 = ( -0.3, 20.65 )
..
"2ndSpace Polygon 7 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 13.3, 0 )
V3 = ( 13.3, 5.3 )
V4 = ( 17.7, 5.3 )
V5 = ( 17.7, 13.95 )
V6 = ( 0, 13.95 )
..
"2ndSpace Polygon 8 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 15.1, 0 )
V3 = ( 15.1, 20.1 )
V4 = ( 74.65, 20.1 )
V5 = ( 74.65, 33.4 )
V6 = ( 0, 33.4 )
..
"BseSpace Polygon 1 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 28.5, 0 )
V3 = ( 28.5, 28.45 )
V4 = ( 0, 28.85 )
..
"BseSpace Polygon 2 - SMirro" = POLYGON
V1 = ( 0, 0 )
V2 = ( 28.5, -0.4 )
V3 = ( 28.5, 3.15 )
V4 = ( 57.5, 3.15 )
V5 = ( 57.5, 21.3 )
V6 = ( 48.5, 21.3 )
V7 = ( 48.5, 30.2 )
V8 = ( 44.35, 30.2 )
V9 = ( 44.35, 49 )
V10 = ( 0, 49 )
..
$ ---------------------------------------------------------
$ Wall Parameters
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Fixed and Building Shades
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Misc Cost Related Objects
$ ---------------------------------------------------------
"Baseline Data" = BASELINE
..
$ *********************************************************
$ ** **
$ ** Performance Curves **
$ ** **
$ *********************************************************
$ *********************************************************
$ ** **
$ ** Floors / Spaces / Walls / Windows / Doors **
$ ** **
$ *********************************************************
"1stGround Flr" = FLOOR
AZIMUTH = 360
POLYGON = "1stFloor Polygon"
SHAPE = POLYGON
FLOOR-HEIGHT = 12
SPACE-HEIGHT = 12
C-DIAGRAM-DATA = *Bldg Envelope & Loads 1 Diag Data*
..
"Entry 103" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0827134
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.631 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 1"
LOCATION = FLOOR-V1
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stWest Wall (G.NW1.E1)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stWest Win (G.NW1.E1.W1)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 11.1383
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.NW1.E1.W2)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 15.3083
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78332
FRAME-CONDUCT = 2.781
..
"1stWest Door (G.NW1.E1.D1)" = DOOR
CONSTRUCTION = "Dbl Lyr Unins Mtl Door"
X = 1.9
HEIGHT = 7
WIDTH = 3
..
"1stSouth Wall (G.NW1.E2)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V5
SHADING-SURFACE = YES
..
"1stNorth Wall (G.NW1.E3)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V7
SHADING-SURFACE = YES
..
"1stSouth Wall (G.NW1.I1)" = INTERIOR-WALL
NEXT-TO = "Lobby 101"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"1stEast Wall (G.NW1.I2)" = INTERIOR-WALL
NEXT-TO = "Elev 104"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"1stSouth Wall (G.NW1.I3)" = INTERIOR-WALL
NEXT-TO = "Elev 104"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"1stEast Wall (G.NW1.I4)" = INTERIOR-WALL
NEXT-TO = "Mech 106"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"1stFlr (G.NW1.U1)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.NW1.U2)"
LOCATION = BOTTOM
..
"Mech 106" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.161925
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 2"
LOCATION = FLOOR-V12
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stSouth Wall (G.E2.E4)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stEast Wall (G.E2.E5)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"1stNorth Wall (G.E2.E6)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"1stFlr (G.E2.U2)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.E2.U3)"
LOCATION = BOTTOM
..
"Elev 104" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0670588
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 3"
LOCATION = FLOOR-V10
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stEast Wall (G.E3.E7)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stFlr (G.E3.U3)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.E3.U4)"
LOCATION = BOTTOM
..
"Lobby 101" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0367835
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 4"
LOCATION = FLOOR-V2
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stWest Wall (G.N4.E8)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stWest Win (G.N4.E8.W1)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 14.0583
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W2)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 18.2283
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W3)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 22.3983
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W4)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 26.5683
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W5)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 33.9383
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W6)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 38.1083
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W7)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 4.37999
Y = 0.488056
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.N4.E8.W8)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 0.108333
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stEast Wall (G.N4.E9)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"1stNorth Wall (G.N4.E10)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V4
SHADING-SURFACE = YES
..
"1stSouth Wall (G.N4.I5)" = INTERIOR-WALL
NEXT-TO = "Office South 107"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"1stNorth Wall (G.N4.I6)" = INTERIOR-WALL
NEXT-TO = "Elev 104"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"1stFlr (G.N4.U4)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.N4.U5)"
LOCATION = BOTTOM
..
"Office South 107" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0472394
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "1stSpace Polygon 5"
LOCATION = FLOOR-V3
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"1stWest Wall (G.S5.E11)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"1stWest Win (G.S5.E11.W1)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 10.6783
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W2)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 14.8983
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W3)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 19.1183
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W4)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 23.2383
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W5)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 4.27833
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stWest Win (G.S5.E11.W6)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 0.108333
Y = 0.558333
HEIGHT = 7.78333
WIDTH = 3.78333
FRAME-CONDUCT = 2.781
..
"1stSouth Wall (G.S5.E12)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"1stEast Wall (G.S5.E13)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"1stNorth Wall (G.S5.E14)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V4
SHADING-SURFACE = YES
..
"1stEast Wall (G.S5.E15)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V5
SHADING-SURFACE = YES
..
"1stFlr (G.S5.U5)" = UNDERGROUND-WALL
CONSTRUCTION = "1stUFCons (G.S5.U6)"
LOCATION = BOTTOM
..
"2ndGround Flr" = FLOOR
Y = -5.75
Z = 12
AZIMUTH = 360
POLYGON = "2ndFloor Polygon"
SHAPE = POLYGON
FLOOR-HEIGHT = 12
SPACE-HEIGHT = 12
C-DIAGRAM-DATA = *EL2 Bldg Envelope & Loads 1 Diag Data*
..
"Vestabule 201" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0633102
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 1"
LOCATION = FLOOR-V10
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndWest Wall (G.NNW1.E1)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndNorth Wall (G.NNW1.E2)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndNorth Win (G.NNW1.E2.W1)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 0.345487
Y = 0.345487
HEIGHT = 11.2833
WIDTH = 5.78333
FRAME-CONDUCT = 2.781
..
"2ndWest Wall (G.NNW1.E3)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V3
SHADING-SURFACE = YES
..
"2ndWest Win (G.NNW1.E3.W1)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 0.480902
Y = 0.392918
HEIGHT = 11.2833
WIDTH = 9.44333
FRAME-CONDUCT = 2.781
..
"2ndNorth Wall (G.NNW1.E4)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V9
SHADING-SURFACE = YES
..
"2ndRoof (G.NNW1.E5)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.NNW1.I1)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndSouth Wall (G.NNW1.I2)" = INTERIOR-WALL
NEXT-TO = "Study Lounge 204"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"2ndEast Wall (G.NNW1.I3)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"2ndSouth Wall (G.NNW1.I4)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"2ndSouth Wall (G.NNW1.I5)" = INTERIOR-WALL
NEXT-TO = "IT Elec 205"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V7
..
"2ndEast Wall (G.NNW1.I6)" = INTERIOR-WALL
NEXT-TO = "Mech 203"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V8
..
"Elev 200" = SPACE
X = 40.05
Y = 276.9
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) C-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.001
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 2"
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndRoof (G.C2.E6)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.C2.I7)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"Mech 203" = SPACE
X = 55.2
Y = 295.95
AZIMUTH = 90
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0527166
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 3"
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndNorth Wall (G.N3.E7)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V4
SHADING-SURFACE = YES
..
"2ndRoof (G.N3.E8)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.N3.I8)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"Study 212" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0518192
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 4"
LOCATION = FLOOR-V2
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndWest Wall (G.SW4.E9)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndWest Win (G.SW4.E9.W1)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 0.483748
Y = 0.358333
HEIGHT = 11.2833
WIDTH = 14.2833
FRAME-CONDUCT = 2.781
..
"2ndSouth Wall (G.SW4.E10)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndRoof (G.SW4.E11)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.SW4.I9)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"Study Lounge 204" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0110233
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 5"
LOCATION = FLOOR-V1
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndWest Wall (G.W5.E12)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndWest Win (G.W5.E12.W1)" = WINDOW
GLASS-TYPE = "Prop Windows"
FRAME-WIDTH = 0
X = 0.298333
Y = 0.348333
HEIGHT = 11.2833
WIDTH = 53.2833
FRAME-CONDUCT = 2.781
..
"2ndRoof (G.W5.E13)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.W5.I10)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndSouth Wall (G.W5.I11)" = INTERIOR-WALL
NEXT-TO = "Study 212"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"2ndSouth Wall (G.W5.I12)" = INTERIOR-WALL
NEXT-TO = "Office 208-16"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"2ndEast Wall (G.W5.I13)" = INTERIOR-WALL
NEXT-TO = "Office 208-16"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"2ndNorth Wall (G.W5.I14)" = INTERIOR-WALL
NEXT-TO = "IT Elec 205"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"2ndNorth Wall (G.W5.I15)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"IT Elec 205" = SPACE
X = 46.35
Y = 276.9
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) C-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.001
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 6.5 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 6"
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndRoof (G.C6.E14)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.C6.I16)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndEast Wall (G.C6.I17)" = INTERIOR-WALL
NEXT-TO = "Office 208-16"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V2
..
"2ndEast Wall (G.C6.I18)" = INTERIOR-WALL
NEXT-TO = "RestR 206-7"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"2ndNorth Wall (G.C6.I19)" = INTERIOR-WALL
NEXT-TO = "RestR 206-7"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V4
..
"2ndNorth Wall (G.C6.I20)" = INTERIOR-WALL
NEXT-TO = "Mech 203"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V5
..
"2ndWest Wall (G.C6.I21)" = INTERIOR-WALL
NEXT-TO = "Elev 200"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V7
..
"RestR 206-7" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.064547
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 7"
LOCATION = FLOOR-V6
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndEast Wall (G.NE7.E15)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndNorth Wall (G.NE7.E16)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndRoof (G.NE7.E17)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.NE7.I22)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndWest Wall (G.NE7.I23)" = INTERIOR-WALL
NEXT-TO = "Mech 203"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"Office 208-16" = SPACE
SHAPE = POLYGON
ZONE-TYPE = CONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "1stBldg InsLt Sch" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
INF-SCHEDULE = "ZG0-S1 (PVAVS) P-Inf Sch"
INF-METHOD = AIR-CHANGE
INF-FLOW/AREA = 0.0380072
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 1 )
AREA/PERSON = 107
POLYGON = "2ndSpace Polygon 8"
LOCATION = FLOOR-V4
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"2ndSouth Wall (G.ESE8.E18)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V1
SHADING-SURFACE = YES
..
"2ndEast Wall (G.ESE8.E19)" = EXTERIOR-WALL
CONSTRUCTION = "Exterior Wall Assembly"
LOCATION = SPACE-V2
SHADING-SURFACE = YES
..
"2ndRoof (G.ESE8.E20)" = EXTERIOR-WALL
CONSTRUCTION = "Roof Assembly"
LOCATION = TOP
SHADING-SURFACE = YES
..
"2ndFlr (G.ESE8.I24)" = INTERIOR-WALL
CONSTRUCTION = "2ndGFlr Construction"
INT-WALL-TYPE = ADIABATIC
LOCATION = BOTTOM
..
"2ndNorth Wall (G.ESE8.I25)" = INTERIOR-WALL
NEXT-TO = "RestR 206-7"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V3
..
"2ndWest Wall (G.ESE8.I26)" = INTERIOR-WALL
NEXT-TO = "Study 212"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V6
..
"BseBelow-Grade Flr" = FLOOR
Y = 82
Z = -12
AZIMUTH = 360
POLYGON = "BseFloor Polygon"
SHAPE = POLYGON
FLOOR-HEIGHT = 12
SPACE-HEIGHT = 12
C-DIAGRAM-DATA = *Basement Diag Data*
..
"BseNorth" = SPACE
SHAPE = POLYGON
ZONE-TYPE = UNCONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "Lighting Low occ year" )
EQUIP-SCHEDULE = ( "Elevator sch" )
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 27.55 )
AREA/PERSON = 10000
POLYGON = "BseSpace Polygon 1"
LOCATION = FLOOR-V12
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"BseFlr (B.N1.U1)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Floor Assembly"
LOCATION = BOTTOM
..
"BseWest Wall (B.N1.U2)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V1
..
"BseEast Wall (B.N1.U3)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V3
..
"BseNorth Wall (B.N1.U4)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V4
..
"BseSouth" = SPACE
SHAPE = POLYGON
ZONE-TYPE = UNCONDITIONED
PEOPLE-SCHEDULE = "1stBldg Occup Sch"
LIGHTING-SCHEDUL = ( "Lighting Low occ year" )
EQUIP-SCHEDULE = ( "1stBldg Misc Sch" )
PEOPLE-HG-LAT = 308.004
PEOPLE-HG-SENS = 248.704
EQUIP-LATENT = ( 0 )
EQUIP-SENSIBLE = ( 1 )
LIGHTING-W/AREA = ( 0.63 )
EQUIPMENT-W/AREA = ( 0 )
AREA/PERSON = 10000
POLYGON = "BseSpace Polygon 2"
LOCATION = FLOOR-V1
C-SUB-SRC-BTUH = ( 0, 0, 0 )
C-SUB-SRC-KW = ( 0, 0, 0 )
C-ACTIVITY-DESC = *Classroom / Lecture (50%)*
..
"BseNorth Wall (B.S2.I1)" = INTERIOR-WALL
NEXT-TO = "BseNorth"
CONSTRUCTION = "1stIWall Construction"
LOCATION = SPACE-V10
..
"BseFlr (B.S2.U5)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Floor Assembly"
LOCATION = BOTTOM
..
"BseWest Wall (B.S2.U6)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V1
..
"BseSouth Wall (B.S2.U7)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V2
..
"BseEast Wall (B.S2.U8)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V3
..
"BseSouth Wall (B.S2.U9)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V4
..
"BseEast Wall (B.S2.U10)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V5
..
"BseSouth Wall (B.S2.U11)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V6
..
"BseEast Wall (B.S2.U12)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V7
..
"BseNorth Wall (B.S2.U13)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V8
..
"BseEast Wall (B.S2.U14)" = UNDERGROUND-WALL
CONSTRUCTION = "Below Grade Wall Assembly"
LOCATION = SPACE-V9
..
$ *********************************************************
$ ** **
$ ** Electric & Fuel Meters **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Electric Meters
$ ---------------------------------------------------------
"EM1" = ELEC-METER
TYPE = UTILITY
EXTERIOR-POWER = ( 0.452 )
EXTERIOR-SCH = ( "Ext Lighting Sch" )
..
$ ---------------------------------------------------------
$ Fuel Meters
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Master Meters
$ ---------------------------------------------------------
"MASTER-METERS 1" = MASTER-METERS
MSTR-ELEC-METER = "EM1"
MSTR-FUEL-METER = "FM1"
..
$ *********************************************************
$ ** **
$ ** HVAC Circulation Loops / Plant Equipment **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Pumps
$ ---------------------------------------------------------
"HW Loop Pump" = PUMP
NUMBER = 1
MOTOR-CLASS = HI-EFF
CAP-CTRL = VAR-SPEED-PUMP
..
$ ---------------------------------------------------------
$ Heat Exchangers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Circulation Loops
$ ---------------------------------------------------------
"Hot Water Loop" = CIRCULATION-LOOP
TYPE = HW
LOOP-DESIGN-DT = 22
PIPE-HEAD = 21.6
LOOP-OPERATION = STANDBY
DESIGN-HEAT-T = 180
HEAT-SETPT-CTRL = FIXED
LOOP-PUMP = "HW Loop Pump"
..
"DHW Plant 1 Loop (1)" = CIRCULATION-LOOP
TYPE = DHW
DESIGN-HEAT-T = 135
PROCESS-FLOW = ( 0.05 )
PROCESS-SCH = ( "DHW Eqp NRes Sch" )
PROCESS-T = ( 135 )
..
$ ---------------------------------------------------------
$ Chillers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Boilers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Domestic Water Heaters
$ ---------------------------------------------------------
"DHW Plant 1 Wtr Htr (1)" = DW-HEATER
TYPE = ELEC
TANK-VOLUME = 66.8934
CAPACITY = 0.0297183
TANK-UA = 2.78723
LOCATION = ZONE
ZONE-NAME = "BseSouth Th"
DHW-LOOP = "DHW Plant 1 Loop (1)"
C-ENERGY-FACTOR = 0.841701
C-TANK-EXT-RVAL = 12
..
$ ---------------------------------------------------------
$ Heat Rejection
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Tower Free Cooling
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Photovoltaic Modules
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Electric Generators
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Thermal Storage
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Ground Loop Heat Exchangers
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Compliance DHW (residential dwelling units)
$ ---------------------------------------------------------
$ *********************************************************
$ ** **
$ ** Steam & Chilled Water Meters **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Steam Meters
$ ---------------------------------------------------------
"Steam Meter 1" = STEAM-METER
ENERGY/UNIT = 1.16e+006
CIRCULATION-LOOP = "Hot Water Loop"
..
$ ---------------------------------------------------------
$ Chilled Water Meters
$ ---------------------------------------------------------
$ *********************************************************
$ ** **
$ ** HVAC Systems / Zones **
$ ** **
$ *********************************************************
"AHU-1 Sys" = SYSTEM
TYPE = PVAVS
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = HOT-WATER
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1
COOL-SIZING-RATI = 1.15
HUMIDIFIER-TYPE = NONE
MAX-SUPPLY-T = 105
MIN-SUPPLY-T = 55
COOL-CONTROL = CONSTANT
MAX-HUMIDITY = 100
MIN-HUMIDITY = 0
ECONO-LIMIT-T = 65
ENTHALPY-LIMIT = 30
ECONO-LOCKOUT = YES
SUPPLY-FLOW = 7900
RETURN-FLOW = 7525
OA-CONTROL = OA-TEMP
FAN-SCHEDULE = "S1 Sys1 (PVAVS) Fan Sch"
FAN-CONTROL = FAN-EIR-FPLR
SUPPLY-EFF = 0.53
SUPPLY-KW/FLOW = 0.0007079
RETURN-EFF = 0.53
RETURN-KW/FLOW = 0.0004955
FAN-EIR-FPLR = "Variable Speed Drive FPLR"
REHEAT-DELTA-T = 65
HW-VALVE-TYPE = TWO-WAY
HW-COIL-DT = 50
HW-LOOP = "Hot Water Loop"
COOLING-CAPACITY = 234000
COOLING-EIR = 0.2182
COOL-SH-CAP = 217000
COOL-CTRL-RANGE = 5
CRANKCASE-HEAT = 0
HEATING-CAPACITY = -172300
FURNACE-HIR = 1.24067
ZONE-HW-LOOP = "Hot Water Loop"
HUMIDIFIER-LOC = IN-AIR-HANDLER
..
"Enrty 103 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Entry 103"
OA-FLOW/AREA = 0.63
..
"Mech 106 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Mech 106"
OA-FLOW/AREA = 0.63
..
"Elev 104 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Elev 104"
OA-FLOW/AREA = 0.63
..
"Lobby 101 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Lobby 101"
OA-FLOW/AREA = 0.63
..
"1stSouth 107 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Office South 107"
OA-FLOW/AREA = 0.63
..
"Vestabule 201 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Vestabule 201"
OA-FLOW/AREA = 0.63
..
"Elev 200 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Elev 200"
OA-FLOW/AREA = 0.63
..
"Mech 203 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Mech 203"
OA-FLOW/AREA = 0.63
..
"Study 212 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Study 212"
OA-FLOW/AREA = 0.63
..
"Lounge 204 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Study Lounge 204"
OA-FLOW/AREA = 0.63
..
"RestR 206-7 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "RestR 206-7"
OA-FLOW/AREA = 0.63
..
"Office 208-16 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "S1 Sys1 (PVAVS) Heat Sch"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "Office 208-16"
OA-FLOW/AREA = 0.63
..
"BseSys1 (PVAVS) (B.C1)" = SYSTEM
TYPE = SUM
HEAT-SOURCE = NONE
SYSTEM-REPORTS = NO
..
"BseNorth Th" = ZONE
TYPE = UNCONDITIONED
DESIGN-HEAT-T = 72
DESIGN-COOL-T = 75
SIZING-OPTION = ADJUST-LOADS
SPACE = "BseNorth"
..
"BseSys1 (PVAVS) (B.C2)" = SYSTEM
TYPE = SUM
HEAT-SOURCE = NONE
SYSTEM-REPORTS = NO
..
"BseSouth Th" = ZONE
TYPE = UNCONDITIONED
DESIGN-HEAT-T = 72
DESIGN-COOL-T = 75
SIZING-OPTION = ADJUST-LOADS
SPACE = "BseSouth"
..
"IT Elec Sys" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HOT-WATER
ZONE-HEAT-SOURCE = NONE
HEAT-SIZING-RATI = 1.25
MAX-SUPPLY-T = 90
SUPPLY-FLOW = 450
SUPPLY-KW/FLOW = 0.0007
HW-LOOP = "Hot Water Loop"
COOLING-CAPACITY = 12000
COOLING-EIR = 0.17
COOL-SH-CAP = 8200
CRANKCASE-HEAT = 0
ZONE-HW-LOOP = "Hot Water Loop"
CONTROL-ZONE = "IT Elec 205 Th"
..
"IT Elec 205 Th" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.3
DESIGN-HEAT-T = 75
HEAT-TEMP-SCH = "Unocc Heat Shc"
DESIGN-COOL-T = 72
COOL-TEMP-SCH = "S1 Sys1 (PVAVS) Cool Sch"
THROTTLING-RANGE = 5
SIZING-OPTION = ADJUST-LOADS
HW-COIL-DT = 40
SPACE = "IT Elec 205"
OA-FLOW/AREA = 0.63
..
$ *********************************************************
$ ** **
$ ** Metering & Misc HVAC **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Equipment Controls
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Load Management
$ ---------------------------------------------------------
$ *********************************************************
$ ** **
$ ** Utility Rates **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Ratchets
$ ---------------------------------------------------------
$ ---------------------------------------------------------
$ Block Charges
$ ---------------------------------------------------------
"Cust 1 Elec Uniform Blk1" = BLOCK-CHARGE
BLOCK-SCH = "Cust 1 Elec Season Sched"
SCH-FLAG = 1
BLOCK1-TYPE = ENERGY
BLOCKS-1 = ( 1 )
COSTS-1 = ( 0.085 )
..
"Steam Block" = BLOCK-CHARGE
BLOCKS-1 = ( 1e+007 )
COSTS-1 = ( 6.71 )
..
$ ---------------------------------------------------------
$ Utility Rates
$ ---------------------------------------------------------
"UofM elec" = UTILITY-RATE
TYPE = ELECTRICITY
BLOCK-CHARGES = ( "Cust 1 Elec Uniform Blk1" )
..
"Steam Rate" = UTILITY-RATE
TYPE = STEAM
BLOCK-CHARGES = ( "Steam Block" )
..
$ *********************************************************
$ ** **
$ ** Output Reporting **
$ ** **
$ *********************************************************
$ ---------------------------------------------------------
$ Loads Non-Hourly Reporting
$ ---------------------------------------------------------
LOADS-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Systems Non-Hourly Reporting
$ ---------------------------------------------------------
SYSTEMS-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Plant Non-Hourly Reporting
$ ---------------------------------------------------------
PLANT-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Economics Non-Hourly Reporting
$ ---------------------------------------------------------
ECONOMICS-REPORT
VERIFICATION = ( ALL-VERIFICATION )
SUMMARY = ( ALL-SUMMARY )
..
$ ---------------------------------------------------------
$ Hourly Reporting
$ ---------------------------------------------------------
"Hourly Report" = HOURLY-REPORT
LIBRARY-ENTRY "Hourly Report"
..
$ ---------------------------------------------------------
$ THE END
$ ---------------------------------------------------------
END ..
COMPUTE ..
STOP ..
-------------- next part --------------
Proj "UofM Athletic Addition proposed "
ProgramVersion = "eQUEST 3.65.7163"
BDBaseVersion = 25
ProductCode = "eQUEST"
WeatherFile = "TMY2\MISSOUMT.bin"
CreateDate = 1401221951
ModDate = 1408031642
RunDate = 1408031251
LibraryFile = "eQ_Lib.dat"
ActiveMode = 0
InputModule = 3
Owner = "University Of Montana"
UseCameraData = 1
ClippingRange = ( 109.477, 311.932 )
FocalPoint = ( 57.025, 245.9, 6.52929 )
Position = ( -138.007, 242.496, 45.3806 )
ViewUpVector = ( 0, 0, 1 )
ViewAngle = 30
InterfaceMode = 1
AllowWizard = 1
NotProjFile = "UofM Athletic Addition proposed"
InputUnitsType = "English"
OutputUnitsType = "English"
PreviousName = "UofM Athletic Addition proposed "
DetailedModelEdits = 1
ProjTreeType = ( 1, 1, 1, 1, 1, 1 )
ProjTreeID = ( 10010002, 10410000, 10020049, 10640000, 10480003,
10750000 )
ProjTreeLabel = ( "1stBldg Misc Sch", "1stGround Flr",
"Elevator sch Week", "Hot Water Loop",
"IT Elec Sys", "EM1" )
..
MainWiz "UofM Athletic Addition proposed "
ProductCode = "eQUEST"
WizardType = "Design Development"
DebugID = 0
AllowCustWinDoor = 1
ScreenIDArrIdx = 2
ScreenIDArrID = 18
Coverage = "All eQUEST Locations"
State = "Montana"
Location = "Missoula"
ElecUtility = "- custom -"
GasUtility = "- none -"
UserElecRate[1] = "UofM elec"
UserFuelRate = "Custom Gas Rate"
BldgType = "School, College/University"
HVACDefaulted = 1
..
ShellWiz "First Floor"
NamePrefix = "1st"
ModelEnduse[3] = 0
ModelEnduse[4] = 0
ModelEnduse[5] = 0
ModelEnduse[12] = 0
ScreenIDArrIdx = 13
ScreenIDArrID = 132
BldgType = "School, College/University"
GrossArea = 2851
FlrsAboveGrade = 1
Footprint = "- custom -"
FlrToFlr = 12
FlrToCeiling = 12
ZoningPattern = "- custom -"
NumMCZnGrps = 0
DiagLink = "Bldg Envelope & Loads 1 Diag Data"
RoofConsType = "No Exterior Exposure (adiabatic)"
ZoningCurrent = 1
NumFloorVertices = 15
FloorVertX[1] = 32.4
FloorVertX[2] = 32.4
FloorVertX[3] = 32.4
FloorVertX[4] = 32.4
FloorVertX[5] = 81.65
FloorVertX[6] = 81.65
FloorVertX[7] = 61.65
FloorVertX[8] = 61.65
FloorVertX[9] = 61.85
FloorVertX[10] = 46.35
FloorVertX[11] = 46.35
FloorVertX[12] = 55.15
FloorVertX[13] = 62.6
FloorVertX[14] = 62.6
FloorVertX[15] = 55.4
FloorVertY[1] = 290.3
FloorVertY[2] = 271.1
FloorVertY[3] = 228.9
FloorVertY[4] = 201.65
FloorVertY[5] = 201.5
FloorVertY[6] = 221.4
FloorVertY[7] = 221.4
FloorVertY[8] = 228.95
FloorVertY[9] = 271.1
FloorVertY[10] = 271.1
FloorVertY[11] = 281.15
FloorVertY[12] = 281.15
FloorVertY[13] = 281.15
FloorVertY[14] = 290.3
FloorVertY[15] = 290.3
AdiabaticCurrent = 1
ZoneGroupsOK = 1
DfltZnGrpName[1] = "GrndUnderground Areas"
DfltZnGrpName[2] = "GrndGround Floor"
DfltZnGrpName[3] = "GrndGround Floor"
DfltZnGrpName[4] = "GrndTypical Floor(s)"
DfltZnGrpName[5] = "GrndTypical Floor(s)"
DfltZnGrpName[6] = "GrndTop Floor"
DfltZnGrpName[7] = "GrndTop Floor"
DfltZnGrpName[8] = "GrndData Center"
CustomFootprint = 1
CustomZoning = 1
ActiveZoneIndex = 5
CustomRoofZoning = -1
ActiveRoofZoneIdx = 1
FloorArea = 2850.85
FloorPerimLen = 308.651
LastFootprint = 1
OverhangOption = "None"
GTCCategory[2] = "- select another -"
WindowHeight[1] = 8
WinSillHeight[1] = 0.5
PercentGlass2[1] = 40
PercentGlass3[1] = 0
DoorType[1] = "Opaque"
NumExtDoors1[1] = 0
NumExtDoors2[1] = 1
NumExtDoors3[1] = 0
NumExtDoors4[1] = 0
TypWindowWidth[1] = 4
SkyZonesCurrent = 1
SkyltZones[1] = 1
SkyltZones[2] = 1
SkyltZones[3] = 1
SkyltZones[4] = 1
SkyltZones[5] = 1
SkyPosCurrent = 1
DayZonesCurrent[3] = 1
DayltZones[1] = 1
DayltZones[2] = 1
DayltZones[3] = 1
DayltZones[4] = 1
DayltZones[5] = 0
DayltZones[201] = 1
DayltZones[202] = 1
DayltZones[203] = 1
DayltZones[204] = 1
DayltZones[205] = 0
DayltZones[401] = 1
DayltZones[402] = 1
DayltZones[403] = 1
DayltZones[404] = 1
DayltZones[405] = 1
WinDoorCurrent = 1
DetailsCurrent = ( 1, 1, 1 )
BDLNumDayltCtrls[1] = 0
BDLNumDayltCtrls[2] = 0
BDLNumDayltCtrls[3] = 0
BDLNumDayltCtrls[4] = 0
BDLNumDayltCtrls[5] = 0
BDLNumDayltCtrls[201] = 0
BDLNumDayltCtrls[202] = 0
BDLNumDayltCtrls[203] = 0
BDLNumDayltCtrls[204] = 0
BDLNumDayltCtrls[205] = 0
BDLNumDayltCtrls[401] = 0
BDLNumDayltCtrls[402] = 0
BDLNumDayltCtrls[403] = 0
BDLNumDayltCtrls[404] = 0
BDLNumDayltCtrls[405] = 0
OccShape = ( "EL1 Occup Profile (S1)", "EL1 Occup Profile (S2)",
"EL1 Occup Profile (S3)" )
ILShape = ( "EL1 InsLtg Profile (S1)", "EL1 InsLtg Profile (S2)",
"EL1 InsLtg Profile (S3)" )
ELDayShapes = ( "EL1 ExtLtg DayShape (Jan)",
"EL1 ExtLtg DayShape (Feb)",
"EL1 ExtLtg DayShape (Mar)",
"EL1 ExtLtg DayShape (Apr)",
"EL1 ExtLtg DayShape (May)",
"EL1 ExtLtg DayShape (Jun)",
"EL1 ExtLtg DayShape (Jul)",
"EL1 ExtLtg DayShape (Aug)",
"EL1 ExtLtg DayShape (Sep)",
"EL1 ExtLtg DayShape (Oct)",
"EL1 ExtLtg DayShape (Nov)",
"EL1 ExtLtg DayShape (Dec)" )
OEShape = ( "EL1 OffEq Profile (S1)", "EL1 OffEq Profile (S2)",
"EL1 OffEq Profile (S3)" )
CEShape = ( "EL1 CookEq Profile (S1)", "EL1 CookEq Profile (S2)",
"EL1 CookEq Profile (S3)" )
MiscShape = ( "EL1 Misc Profile (S1)", "EL1 Misc Profile (S2)",
"EL1 Misc Profile (S3)" )
RFDayShapes = ( "EL1 Refrig DayShape (Jan)",
"EL1 Refrig DayShape (Feb)",
"EL1 Refrig DayShape (Mar)",
"EL1 Refrig DayShape (Apr)",
"EL1 Refrig DayShape (May)",
"EL1 Refrig DayShape (Jun)",
"EL1 Refrig DayShape (Jul)",
"EL1 Refrig DayShape (Aug)",
"EL1 Refrig DayShape (Sep)",
"EL1 Refrig DayShape (Oct)",
"EL1 Refrig DayShape (Nov)",
"EL1 Refrig DayShape (Dec)" )
DHWShape = ( "EL1 DHW Profile (S1)", "EL1 DHW Profile (S2)",
"EL1 DHW Profile (S3)" )
SCRShape = ( "EL1 S-C Refrig Profile (S1)",
"EL1 S-C Refrig Profile (S2)",
"EL1 S-C Refrig Profile (S3)" )
GroundExtFacets[1] = "Facet-0-0"
GroundExtFacets[2] = "Facet-0-7"
GroundExtFacets[3] = "Facet-0-10"
DaylitAreaCurrent[3] = 1
RoofZoneErrorCode = 4
..
ShapeWiz "EL1 InsLtg Profile (S1)"
..
DayShape "EL1 ExtLtg DayShape (Jan)"
..
DayShape "EL1 ExtLtg DayShape (Feb)"
..
DayShape "EL1 ExtLtg DayShape (Mar)"
..
DayShape "EL1 ExtLtg DayShape (Apr)"
..
DayShape "EL1 ExtLtg DayShape (May)"
..
DayShape "EL1 ExtLtg DayShape (Jun)"
..
DayShape "EL1 ExtLtg DayShape (Jul)"
..
DayShape "EL1 ExtLtg DayShape (Aug)"
..
DayShape "EL1 ExtLtg DayShape (Sep)"
..
DayShape "EL1 ExtLtg DayShape (Oct)"
..
DayShape "EL1 ExtLtg DayShape (Nov)"
..
DayShape "EL1 ExtLtg DayShape (Dec)"
..
ShapeWiz "EL1 OffEq Profile (S1)"
..
ShapeWiz "EL1 Misc Profile (S1)"
..
ShapeWiz "EL1 DHW Profile (S1)"
..
ShapeWiz "EL1 Occup Profile (S1)"
..
ShapeWiz "EL1 InsLtg Profile (S2)"
..
ShapeWiz "EL1 InsLtg Profile (S3)"
..
ShapeWiz "EL1 OffEq Profile (S2)"
..
ShapeWiz "EL1 OffEq Profile (S3)"
..
ShapeWiz "EL1 CookEq Profile (S1)"
..
ShapeWiz "EL1 CookEq Profile (S2)"
..
ShapeWiz "EL1 CookEq Profile (S3)"
..
DayShape "EL1 Refrig DayShape (Jan)"
..
DayShape "EL1 Refrig DayShape (Feb)"
..
DayShape "EL1 Refrig DayShape (Mar)"
..
DayShape "EL1 Refrig DayShape (Apr)"
..
DayShape "EL1 Refrig DayShape (May)"
..
DayShape "EL1 Refrig DayShape (Jun)"
..
DayShape "EL1 Refrig DayShape (Jul)"
..
DayShape "EL1 Refrig DayShape (Aug)"
..
DayShape "EL1 Refrig DayShape (Sep)"
..
DayShape "EL1 Refrig DayShape (Oct)"
..
DayShape "EL1 Refrig DayShape (Nov)"
..
DayShape "EL1 Refrig DayShape (Dec)"
..
ShapeWiz "EL1 Misc Profile (S2)"
..
ShapeWiz "EL1 Misc Profile (S3)"
..
ShapeWiz "EL1 DHW Profile (S2)"
..
ShapeWiz "EL1 DHW Profile (S3)"
..
ShapeWiz "EL1 Occup Profile (S2)"
..
ShapeWiz "EL1 Occup Profile (S3)"
..
ShapeWiz "EL1 S-C Refrig Profile (S1)"
..
ShapeWiz "EL1 S-C Refrig Profile (S2)"
..
ShapeWiz "EL1 S-C Refrig Profile (S3)"
..
CustomZone "Custom Zone 1"
NumVerts = 7
X[1] = 32.4
X[2] = 32.4
X[3] = 39.55
X[4] = 39.55
X[5] = 46.35
X[6] = 55.15
X[7] = 55.4
Y[1] = 290.3
Y[2] = 271.1
Y[3] = 271.1
Y[4] = 281.15
Y[5] = 281.15
Y[6] = 281.15
Y[7] = 290.3
..
CustomZone "Custom Zone 2"
NumVerts = 4
X[1] = 55.15
X[2] = 62.6
X[3] = 62.6
X[4] = 55.4
Y[1] = 281.15
Y[2] = 281.15
Y[3] = 290.3
Y[4] = 290.3
..
CustomZone "Custom Zone 3"
NumVerts = 4
X[1] = 39.55
X[2] = 46.35
X[3] = 46.35
X[4] = 39.55
Y[1] = 271.1
Y[2] = 271.1
Y[3] = 281.15
Y[4] = 281.15
..
CustomZone "Custom Zone 4"
NumVerts = 6
X[1] = 32.4
X[2] = 32.4
X[3] = 61.65
X[4] = 61.85
X[5] = 46.35
X[6] = 39.55
Y[1] = 271.1
Y[2] = 228.9
Y[3] = 228.95
Y[4] = 271.1
Y[5] = 271.1
Y[6] = 271.1
..
CustomZone "Custom Zone 5"
NumVerts = 6
X[1] = 32.4
X[2] = 32.4
X[3] = 81.65
X[4] = 81.65
X[5] = 61.65
X[6] = 61.65
Y[1] = 228.9
Y[2] = 201.65
Y[3] = 201.5
Y[4] = 221.4
Y[5] = 221.4
Y[6] = 228.95
..
ZnGrpWiz "GrndGround Floor"
ShortName = "GndFlr"
..
FacetWiz "Facet-0-0"
ParentZoneIdx = 0
SegmentNumber = 0
..
WinWiz "Custom Window 36"
X = 11.03
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 37"
X = 15.2
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
DoorWiz "Custom Door 1"
X = 1.9
Y = 0
Width = 3
Height = 7
FrameWidth = 0
DoorTypeIdx = 0
..
FacetWiz "Facet-0-7"
ParentZoneIdx = 3
SegmentNumber = 0
..
WinWiz "Custom Window 38"
X = 13.95
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 39"
X = 18.12
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 40"
X = 22.29
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 41"
X = 26.46
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 42"
X = 33.83
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 43"
X = 38
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 44"
X = 4.27166
Y = 0.379723
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 45"
X = 0
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-10"
ParentZoneIdx = 4
SegmentNumber = 0
..
WinWiz "Custom Window 46"
X = 10.57
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 47"
X = 14.79
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 48"
X = 19.01
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 49"
X = 23.13
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 50"
X = 4.17
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
WinWiz "Custom Window 51"
X = 0
Y = 0.45
Width = 4
Height = 8
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
ShellWiz "Second floor"
NamePrefix = "2nd"
ModelEnduse[3] = 0
ModelEnduse[4] = 0
ModelEnduse[5] = 0
ModelEnduse[12] = 0
ScreenIDArrIdx = 7
ScreenIDArrID = 61
BldgType = "School, College/University"
GrossArea = 4766
FlrsAboveGrade = 1
ShellPos_Dir = "Immediately Above"
ShellPos_Specify = 1
BldgX = 0
Footprint = "- custom -"
FlrToFlr = 12
FlrToCeiling = 12
ZoningPattern = "- custom -"
NumMCZnGrps = 0
DiagLink = "EL2 Bldg Envelope & Loads 1 Diag Data"
RoofConsType = "Wood Advanced Frame, 24 in. o.c."
GrndFlrExposure = "Over Conditioned Space (adiabatic)"
GrndFlrInsType = "- no batt or board insulation -"
ZoningCurrent = 1
NumFloorVertices = 12
FloorVertX[1] = 25.85
FloorVertX[2] = 25.85
FloorVertX[3] = 25.85
FloorVertX[4] = 46.9
FloorVertX[5] = 80.3
FloorVertX[6] = 80.3
FloorVertX[7] = 80.3
FloorVertX[8] = 62.1
FloorVertX[9] = 55.2
FloorVertX[10] = 32.4
FloorVertX[11] = 32.4
FloorVertX[12] = 25.85
FloorVertX[13] = 81.15
FloorVertX[14] = 81.15
FloorVertX[15] = 62.1
FloorVertX[16] = 55.2
FloorVertX[17] = 32.4
FloorVertX[18] = 32.4
FloorVertX[19] = 25.85
FloorVertY[1] = 276.6
FloorVertY[2] = 222.6
FloorVertY[3] = 207.35
FloorVertY[4] = 207.35
FloorVertY[5] = 207.35
FloorVertY[6] = 282
FloorVertY[7] = 295.95
FloorVertY[8] = 295.95
FloorVertY[9] = 295.95
FloorVertY[10] = 295.95
FloorVertY[11] = 287.1
FloorVertY[12] = 287.1
FloorVertY[13] = 206.15
FloorVertY[14] = 295.95
FloorVertY[15] = 295.95
FloorVertY[16] = 295.95
FloorVertY[17] = 295.95
FloorVertY[18] = 287.1
FloorVertY[19] = 287.1
AdiabaticCurrent = 1
ZoneGroupsOK = 1
DfltZnGrpName[1] = "GrndUnderground Areas"
DfltZnGrpName[2] = "GrndGround Floor-2"
DfltZnGrpName[3] = "GrndGround Floor-2"
DfltZnGrpName[4] = "GrndTypical Floor(s)"
DfltZnGrpName[5] = "GrndTypical Floor(s)"
DfltZnGrpName[6] = "GrndTop Floor"
DfltZnGrpName[7] = "GrndTop Floor"
DfltZnGrpName[8] = "GrndData Center"
CustomFootprint = 1
CustomZoning = 1
ActiveZoneIndex = 4
CustomRoofZoning = -1
ActiveRoofZoneIdx = 1
FloorArea = 4766.3
FloorPerimLen = 286.1
LastFootprint = 9
OverhangOption = "None"
OverhangDepth[2] = 6
GTCCategory[2] = "- select another -"
PercentGlass2[1] = 40
PercentGlass3[1] = 0
PercentGlass4[1] = 0
DoorType[1] = "- select another -"
NumExtDoors1[1] = 0
NumExtDoors2[1] = 4
NumExtDoors3[1] = 0
NumExtDoors4[1] = 0
SkyZonesCurrent = 1
SkyltZones[1] = 1
SkyltZones[2] = 1
SkyltZones[3] = 1
SkyltZones[4] = 1
SkyltZones[5] = 1
SkyltZones[6] = 1
SkyltZones[7] = 1
SkyltZones[8] = 1
SkyltZones[9] = 1
SkyltZones[10] = 1
SkyltZones[11] = 1
SkyPosCurrent = 1
DayZonesCurrent[3] = 1
DayltZones[1] = 1
DayltZones[2] = 1
DayltZones[3] = 1
DayltZones[4] = 1
DayltZones[5] = 0
DayltZones[201] = 1
DayltZones[202] = 1
DayltZones[203] = 1
DayltZones[204] = 1
DayltZones[205] = 0
DayltZones[401] = 1
DayltZones[402] = 0
DayltZones[403] = 1
DayltZones[404] = 1
DayltZones[405] = 1
DayltZones[406] = 0
DayltZones[407] = 1
DayltZones[408] = 1
DayltZones[409] = 1
DayltZones[410] = 1
DayltZones[411] = 0
WinDoorCurrent = 1
DetailsCurrent = ( 1, 1, 1 )
BDLNumDayltCtrls[1] = 0
BDLNumDayltCtrls[2] = 0
BDLNumDayltCtrls[3] = 0
BDLNumDayltCtrls[4] = 0
BDLNumDayltCtrls[5] = 0
BDLNumDayltCtrls[201] = 0
BDLNumDayltCtrls[202] = 0
BDLNumDayltCtrls[203] = 0
BDLNumDayltCtrls[204] = 0
BDLNumDayltCtrls[205] = 0
BDLNumDayltCtrls[401] = 0
BDLNumDayltCtrls[402] = 0
BDLNumDayltCtrls[403] = 0
BDLNumDayltCtrls[404] = 0
BDLNumDayltCtrls[405] = 0
BDLNumDayltCtrls[406] = 0
BDLNumDayltCtrls[407] = 0
BDLNumDayltCtrls[408] = 0
BDLNumDayltCtrls[409] = 0
BDLNumDayltCtrls[410] = 0
BDLNumDayltCtrls[411] = 0
OccShape = ( "EL2 Occup Profile (S1)", "EL2 Occup Profile (S2)",
"EL2 Occup Profile (S3)" )
ILShape = ( "EL2 InsLtg Profile (S1)", "EL2 InsLtg Profile (S2)",
"EL2 InsLtg Profile (S3)" )
ELDayShapes = ( "EL2 ExtLtg DayShape (Jan)",
"EL2 ExtLtg DayShape (Feb)",
"EL2 ExtLtg DayShape (Mar)",
"EL2 ExtLtg DayShape (Apr)",
"EL2 ExtLtg DayShape (May)",
"EL2 ExtLtg DayShape (Jun)",
"EL2 ExtLtg DayShape (Jul)",
"EL2 ExtLtg DayShape (Aug)",
"EL2 ExtLtg DayShape (Sep)",
"EL2 ExtLtg DayShape (Oct)",
"EL2 ExtLtg DayShape (Nov)",
"EL2 ExtLtg DayShape (Dec)" )
OEShape = ( "EL2 OffEq Profile (S1)", "EL2 OffEq Profile (S2)",
"EL2 OffEq Profile (S3)" )
CEShape = ( "EL2 CookEq Profile (S1)", "EL2 CookEq Profile (S2)",
"EL2 CookEq Profile (S3)" )
MiscShape = ( "EL2 Misc Profile (S1)", "EL2 Misc Profile (S2)",
"EL2 Misc Profile (S3)" )
RFDayShapes = ( "EL2 Refrig DayShape (Jan)",
"EL2 Refrig DayShape (Feb)",
"EL2 Refrig DayShape (Mar)",
"EL2 Refrig DayShape (Apr)",
"EL2 Refrig DayShape (May)",
"EL2 Refrig DayShape (Jun)",
"EL2 Refrig DayShape (Jul)",
"EL2 Refrig DayShape (Aug)",
"EL2 Refrig DayShape (Sep)",
"EL2 Refrig DayShape (Oct)",
"EL2 Refrig DayShape (Nov)",
"EL2 Refrig DayShape (Dec)" )
DHWShape = ( "EL2 DHW Profile (S1)", "EL2 DHW Profile (S2)",
"EL2 DHW Profile (S3)" )
SCRShape = ( "EL2 S-C Refrig Profile (S1)",
"EL2 S-C Refrig Profile (S2)",
"EL2 S-C Refrig Profile (S3)" )
GroundExtFacets[1] = "Facet-0-0 4"
GroundExtFacets[2] = "Facet-0-1"
GroundExtFacets[3] = "Facet-0-2"
GroundExtFacets[4] = "Facet-0-5"
GroundExtFacets[5] = "Facet-0-7 8"
DaylitAreaCurrent[3] = 1
RoofZoneErrorCode = 4
..
ShapeWiz "EL2 InsLtg Profile (S1)"
..
DayShape "EL2 ExtLtg DayShape (Jan)"
..
DayShape "EL2 ExtLtg DayShape (Feb)"
..
DayShape "EL2 ExtLtg DayShape (Mar)"
..
DayShape "EL2 ExtLtg DayShape (Apr)"
..
DayShape "EL2 ExtLtg DayShape (May)"
..
DayShape "EL2 ExtLtg DayShape (Jun)"
..
DayShape "EL2 ExtLtg DayShape (Jul)"
..
DayShape "EL2 ExtLtg DayShape (Aug)"
..
DayShape "EL2 ExtLtg DayShape (Sep)"
..
DayShape "EL2 ExtLtg DayShape (Oct)"
..
DayShape "EL2 ExtLtg DayShape (Nov)"
..
DayShape "EL2 ExtLtg DayShape (Dec)"
..
ShapeWiz "EL2 OffEq Profile (S1)"
..
ShapeWiz "EL2 Misc Profile (S1)"
..
ShapeWiz "EL2 DHW Profile (S1)"
..
ShapeWiz "EL2 Occup Profile (S1)"
..
ShapeWiz "EL2 InsLtg Profile (S2)"
..
ShapeWiz "EL2 InsLtg Profile (S3)"
..
ShapeWiz "EL2 OffEq Profile (S2)"
..
ShapeWiz "EL2 OffEq Profile (S3)"
..
ShapeWiz "EL2 CookEq Profile (S1)"
..
ShapeWiz "EL2 CookEq Profile (S2)"
..
ShapeWiz "EL2 CookEq Profile (S3)"
..
DayShape "EL2 Refrig DayShape (Jan)"
..
DayShape "EL2 Refrig DayShape (Feb)"
..
DayShape "EL2 Refrig DayShape (Mar)"
..
DayShape "EL2 Refrig DayShape (Apr)"
..
DayShape "EL2 Refrig DayShape (May)"
..
DayShape "EL2 Refrig DayShape (Jun)"
..
DayShape "EL2 Refrig DayShape (Jul)"
..
DayShape "EL2 Refrig DayShape (Aug)"
..
DayShape "EL2 Refrig DayShape (Sep)"
..
DayShape "EL2 Refrig DayShape (Oct)"
..
DayShape "EL2 Refrig DayShape (Nov)"
..
DayShape "EL2 Refrig DayShape (Dec)"
..
ShapeWiz "EL2 Misc Profile (S2)"
..
ShapeWiz "EL2 Misc Profile (S3)"
..
ShapeWiz "EL2 DHW Profile (S2)"
..
ShapeWiz "EL2 DHW Profile (S3)"
..
ShapeWiz "EL2 Occup Profile (S2)"
..
ShapeWiz "EL2 Occup Profile (S3)"
..
ShapeWiz "EL2 S-C Refrig Profile (S1)"
..
ShapeWiz "EL2 S-C Refrig Profile (S2)"
..
ShapeWiz "EL2 S-C Refrig Profile (S3)"
..
ZnGrpWiz "GrndGround Floor-2"
ShortName = "GndFlr"
..
CustomZone "Custom Zone 6"
NumVerts = 9
X[1] = 32.4
X[2] = 32.4
X[3] = 25.85
X[4] = 25.85
X[5] = 40.05
X[6] = 40.05
X[7] = 46.35
X[8] = 55.2
X[9] = 55.2
Y[1] = 295.95
Y[2] = 287.1
Y[3] = 287.1
Y[4] = 276.6
Y[5] = 276.9
Y[6] = 286.9
Y[7] = 286.8
Y[8] = 287.3
Y[9] = 295.95
..
CustomZone "Custom Zone 7"
NumVerts = 4
X[1] = 40.05
X[2] = 46.35
X[3] = 46.35
X[4] = 40.05
Y[1] = 276.9
Y[2] = 276.9
Y[3] = 286.8
Y[4] = 286.9
..
CustomZone "Custom Zone 8"
NumVerts = 4
X[1] = 55.2
X[2] = 62.6
X[3] = 62.6
X[4] = 55.2
Y[1] = 287.3
Y[2] = 287.3
Y[3] = 295.95
Y[4] = 295.95
..
CustomZone "Custom Zone 10"
NumVerts = 4
X[1] = 25.85
X[2] = 25.85
X[3] = 46.9
X[4] = 46.9
Y[1] = 222.6
Y[2] = 207.35
Y[3] = 207.35
Y[4] = 222.45
..
CustomZone "Custom Zone 14"
NumVerts = 7
X[1] = 25.85
X[2] = 25.85
X[3] = 46.9
X[4] = 67
X[5] = 67
X[6] = 46.35
X[7] = 40.05
Y[1] = 276.6
Y[2] = 222.6
Y[3] = 222.45
Y[4] = 222.45
Y[5] = 276.6
Y[6] = 276.9
Y[7] = 276.9
..
CustomZone "Custom Zone 15"
NumVerts = 7
X[1] = 46.35
X[2] = 67
X[3] = 67
X[4] = 67
X[5] = 62.6
X[6] = 55.2
X[7] = 46.35
Y[1] = 276.9
Y[2] = 276.6
Y[3] = 282
Y[4] = 287.3
Y[5] = 287.3
Y[6] = 287.3
Y[7] = 286.8
..
CustomZone "Custom Zone 16"
NumVerts = 6
X[1] = 62.6
X[2] = 62.6
X[3] = 67
X[4] = 67
X[5] = 80.3
X[6] = 80.3
Y[1] = 295.95
Y[2] = 287.3
Y[3] = 287.3
Y[4] = 282
Y[5] = 282
Y[6] = 295.95
..
CustomZone "Custom Zone 17"
NumVerts = 7
X[1] = 67
X[2] = 67
X[3] = 67
X[4] = 46.9
X[5] = 46.9
X[6] = 80.3
X[7] = 80.3
Y[1] = 282
Y[2] = 276.6
Y[3] = 222.45
Y[4] = 222.45
Y[5] = 207.35
Y[6] = 207.35
Y[7] = 282
..
FacetWiz "Facet-0-0 4"
ParentZoneIdx = 0
SegmentNumber = 0
..
FacetWiz "Facet-0-1"
ParentZoneIdx = 0
SegmentNumber = 1
..
WinWiz "Custom Window 17"
X = 0.237154
Y = 0.237154
Width = 6
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-2"
ParentZoneIdx = 0
SegmentNumber = 2
..
WinWiz "Custom Window 18"
X = 0.372569
Y = 0.284585
Width = 9.66
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-5"
ParentZoneIdx = 3
SegmentNumber = 0
..
WinWiz "Custom Window 19"
X = 0.375415
Y = 0.25
Width = 14.5
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
FacetWiz "Facet-0-7 8"
ParentZoneIdx = 4
SegmentNumber = 0
..
WinWiz "Custom Window 20"
X = 0.19
Y = 0.24
Width = 53.5
Height = 11.5
FramePercent = -1
FrameWidth = 1.3
IsDoor = 0
GlassTypeIdx = 0
..
ShellWiz "Basement"
NamePrefix = "Bse"
ScreenIDArrIdx = 13
ScreenIDArrID = 132
GrossArea = 2800
FlrsAboveGrade = 0
FlrsBelowGrade = 1
ShellPos_Ref = "First Floor"
ShellPos_Dir = "Immediately Below"
ShellPos_Specify = 1
BldgX = 0
BldgY = 82
Footprint = "- custom -"
FlrToFlr = 12
FlrToCeiling = 12
ZoningPattern = "- custom -"
NumMCZnGrps = 0
DiagLink = "Basement Diag Data"
ZoningCurrent = 1
NumFloorVertices = 12
FloorVertX[1] = 32.4
FloorVertX[2] = 32.4
FloorVertX[3] = 76.75
FloorVertX[4] = 76.75
FloorVertX[5] = 80.9
FloorVertX[6] = 80.9
FloorVertX[7] = 89.9
FloorVertX[8] = 89.9
FloorVertX[9] = 60.9
FloorVertX[10] = 60.9
FloorVertX[11] = 60.9
FloorVertX[12] = 32.4
FloorVertY[1] = 178.75
FloorVertY[2] = 129.75
FloorVertY[3] = 129.75
FloorVertY[4] = 148.55
FloorVertY[5] = 148.55
FloorVertY[6] = 157.45
FloorVertY[7] = 157.45
FloorVertY[8] = 175.6
FloorVertY[9] = 175.6
FloorVertY[10] = 179.15
FloorVertY[11] = 207.6
FloorVertY[12] = 207.6
AdiabaticCurrent = 1
ZoneGroupsOK = 1
DfltZnGrpName[1] = "BseUnderground Areas"
DfltZnGrpName[2] = "BseGround Floor"
DfltZnGrpName[3] = "BseGround Floor"
DfltZnGrpName[4] = "BseTypical Floor(s)"
DfltZnGrpName[5] = "BseTypical Floor(s)"
DfltZnGrpName[6] = "BseTop Floor"
DfltZnGrpName[7] = "BseTop Floor"
DfltZnGrpName[8] = "BseData Center"
CustomFootprint = 1
CustomZoning = 1
ActiveZoneIndex = 2
CustomRoofZoning = -1
ActiveRoofZoneIdx = 1
FloorArea = 3221.06
FloorPerimLen = 270.7
LastFootprint = 1
SkyZonesCurrent = 1
SkyltZones[1] = 1
SkyltZones[2] = 1
SkyltZones[3] = 1
SkyltZones[4] = 1
SkyltZones[5] = 1
SkyPosCurrent = 1
DayltZones[1] = 1
DayltZones[2] = 1
DayltZones[3] = 1
DayltZones[4] = 1
DayltZones[5] = 0
DayltZones[201] = 1
DayltZones[202] = 1
DayltZones[203] = 1
DayltZones[204] = 1
DayltZones[205] = 0
DayltZones[401] = 1
DayltZones[402] = 1
DayltZones[403] = 1
DayltZones[404] = 1
DayltZones[405] = 0
WinDoorCurrent = 1
DetailsCurrent = ( 1, 1, 1 )
BDLNumDayltCtrls[1] = 0
BDLNumDayltCtrls[2] = 0
BDLNumDayltCtrls[3] = 0
BDLNumDayltCtrls[4] = 0
BDLNumDayltCtrls[5] = 0
BDLNumDayltCtrls[201] = 0
BDLNumDayltCtrls[202] = 0
BDLNumDayltCtrls[203] = 0
BDLNumDayltCtrls[204] = 0
BDLNumDayltCtrls[205] = 0
BDLNumDayltCtrls[401] = 0
BDLNumDayltCtrls[402] = 0
BDLNumDayltCtrls[403] = 0
BDLNumDayltCtrls[404] = 0
BDLNumDayltCtrls[405] = 0
OccShape = ( "EL3 Occup Profile (S1)", "EL3 Occup Profile (S2)",
"EL3 Occup Profile (S3)" )
ILShape = ( "EL3 InsLtg Profile (S1)", "EL3 InsLtg Profile (S2)",
"EL3 InsLtg Profile (S3)" )
ELDayShapes = ( "EL3 ExtLtg DayShape (Jan)",
"EL3 ExtLtg DayShape (Feb)",
"EL3 ExtLtg DayShape (Mar)",
"EL3 ExtLtg DayShape (Apr)",
"EL3 ExtLtg DayShape (May)",
"EL3 ExtLtg DayShape (Jun)",
"EL3 ExtLtg DayShape (Jul)",
"EL3 ExtLtg DayShape (Aug)",
"EL3 ExtLtg DayShape (Sep)",
"EL3 ExtLtg DayShape (Oct)",
"EL3 ExtLtg DayShape (Nov)",
"EL3 ExtLtg DayShape (Dec)" )
OEShape = ( "EL3 OffEq Profile (S1)", "EL3 OffEq Profile (S2)",
"EL3 OffEq Profile (S3)" )
CEShape = ( "EL3 CookEq Profile (S1)", "EL3 CookEq Profile (S2)",
"EL3 CookEq Profile (S3)" )
MiscShape = ( "EL3 Misc Profile (S1)", "EL3 Misc Profile (S2)",
"EL3 Misc Profile (S3)" )
RFDayShapes = ( "EL3 Refrig DayShape (Jan)",
"EL3 Refrig DayShape (Feb)",
"EL3 Refrig DayShape (Mar)",
"EL3 Refrig DayShape (Apr)",
"EL3 Refrig DayShape (May)",
"EL3 Refrig DayShape (Jun)",
"EL3 Refrig DayShape (Jul)",
"EL3 Refrig DayShape (Aug)",
"EL3 Refrig DayShape (Sep)",
"EL3 Refrig DayShape (Oct)",
"EL3 Refrig DayShape (Nov)",
"EL3 Refrig DayShape (Dec)" )
DHWShape = ( "EL3 DHW Profile (S1)", "EL3 DHW Profile (S2)",
"EL3 DHW Profile (S3)" )
SCRShape = ( "EL3 S-C Refrig Profile (S1)",
"EL3 S-C Refrig Profile (S2)",
"EL3 S-C Refrig Profile (S3)" )
RoofZoneErrorCode = 4
..
ShapeWiz "EL3 InsLtg Profile (S1)"
..
ShapeWiz "EL3 InsLtg Profile (S2)"
..
ShapeWiz "EL3 InsLtg Profile (S3)"
..
DayShape "EL3 ExtLtg DayShape (Jan)"
..
DayShape "EL3 ExtLtg DayShape (Feb)"
..
DayShape "EL3 ExtLtg DayShape (Mar)"
..
DayShape "EL3 ExtLtg DayShape (Apr)"
..
DayShape "EL3 ExtLtg DayShape (May)"
..
DayShape "EL3 ExtLtg DayShape (Jun)"
..
DayShape "EL3 ExtLtg DayShape (Jul)"
..
DayShape "EL3 ExtLtg DayShape (Aug)"
..
DayShape "EL3 ExtLtg DayShape (Sep)"
..
DayShape "EL3 ExtLtg DayShape (Oct)"
..
DayShape "EL3 ExtLtg DayShape (Nov)"
..
DayShape "EL3 ExtLtg DayShape (Dec)"
..
ShapeWiz "EL3 OffEq Profile (S1)"
..
ShapeWiz "EL3 OffEq Profile (S2)"
..
ShapeWiz "EL3 OffEq Profile (S3)"
..
ShapeWiz "EL3 CookEq Profile (S1)"
..
ShapeWiz "EL3 CookEq Profile (S2)"
..
ShapeWiz "EL3 CookEq Profile (S3)"
..
DayShape "EL3 Refrig DayShape (Jan)"
..
DayShape "EL3 Refrig DayShape (Feb)"
..
DayShape "EL3 Refrig DayShape (Mar)"
..
DayShape "EL3 Refrig DayShape (Apr)"
..
DayShape "EL3 Refrig DayShape (May)"
..
DayShape "EL3 Refrig DayShape (Jun)"
..
DayShape "EL3 Refrig DayShape (Jul)"
..
DayShape "EL3 Refrig DayShape (Aug)"
..
DayShape "EL3 Refrig DayShape (Sep)"
..
DayShape "EL3 Refrig DayShape (Oct)"
..
DayShape "EL3 Refrig DayShape (Nov)"
..
DayShape "EL3 Refrig DayShape (Dec)"
..
ShapeWiz "EL3 Misc Profile (S1)"
..
ShapeWiz "EL3 Misc Profile (S2)"
..
ShapeWiz "EL3 Misc Profile (S3)"
..
ShapeWiz "EL3 DHW Profile (S1)"
..
ShapeWiz "EL3 DHW Profile (S2)"
..
ShapeWiz "EL3 DHW Profile (S3)"
..
ShapeWiz "EL3 Occup Profile (S1)"
..
ShapeWiz "EL3 Occup Profile (S2)"
..
ShapeWiz "EL3 Occup Profile (S3)"
..
ShapeWiz "EL3 S-C Refrig Profile (S1)"
..
ShapeWiz "EL3 S-C Refrig Profile (S2)"
..
ShapeWiz "EL3 S-C Refrig Profile (S3)"
..
ZnGrpWiz "BseUnderground Areas"
ShortName = "Undgnd"
IsConditioned = 0
..
CustomZone "Custom Zone 12"
NumVerts = 4
X[1] = 32.4
X[2] = 32.4
X[3] = 60.9
X[4] = 60.9
Y[1] = 207.6
Y[2] = 178.75
Y[3] = 179.15
Y[4] = 207.6
..
CustomZone "Custom Zone 13"
NumVerts = 10
X[1] = 32.4
X[2] = 32.4
X[3] = 76.75
X[4] = 76.75
X[5] = 80.9
X[6] = 80.9
X[7] = 89.9
X[8] = 89.9
X[9] = 60.9
X[10] = 60.9
Y[1] = 178.75
Y[2] = 129.75
Y[3] = 129.75
Y[4] = 148.55
Y[5] = 148.55
Y[6] = 157.45
Y[7] = 157.45
Y[8] = 175.6
Y[9] = 175.6
Y[10] = 179.15
..
DiagData "Bldg Envelope & Loads 1 Diag Data"
PolyWndGridRes = 3
PolyWndLwrLeftX = -50.6
PolyWndLwrLeftY = 190.5
PolyWndWidth = 215.4
ShowCADLayer[1] = 1
ShowCADLayer[2] = 1
ShowCADLayer[3] = 1
ShowCADLayer[4] = 1
ShowCADLayer[5] = 1
ShowCADLayer[6] = 1
ShowCADLayer[7] = 1
ShowCADLayer[8] = 1
ShowCADLayer[9] = 1
ShowCADLayer[10] = 1
ShowCADLayer[11] = 1
ShowCADLayer[12] = 1
ShowCADLayer[13] = 1
ShowCADLayer[14] = 1
ShowCADLayer[15] = 1
ShowCADLayer[16] = 1
ShowCADLayer[17] = 1
CADFileComp = "UofM model First Floor - DWG"
..
DiagData "EL2 Bldg Envelope & Loads 1 Diag Data"
PolyWndGridRes = 3
PolyWndLwrLeftX = -54.15
PolyWndLwrLeftY = 196.25
PolyWndWidth = 215.4
ShowCADLayer[1] = 1
ShowCADLayer[2] = 1
ShowCADLayer[3] = 1
ShowCADLayer[4] = 1
ShowCADLayer[5] = 1
ShowCADLayer[6] = 1
ShowCADLayer[7] = 1
ShowCADLayer[8] = 1
ShowCADLayer[9] = 1
ShowCADLayer[10] = 1
ShowCADLayer[11] = 1
ShowCADLayer[12] = 1
ShowCADLayer[13] = 1
ShowCADLayer[14] = 1
ShowCADLayer[15] = 1
ShowCADLayer[16] = 1
CADFileComp = "UofM model Second Floor - DWG"
..
DiagData "Basement Diag Data"
PolyWndGridRes = 4
PolyWndLwrLeftX = -46.6
PolyWndLwrLeftY = 113.275
PolyWndWidth = 215.4
ShowCADLayer[1] = 1
ShowCADLayer[2] = 1
ShowCADLayer[3] = 1
ShowCADLayer[4] = 1
ShowCADLayer[5] = 1
ShowCADLayer[6] = 1
CADFileComp = "UofM model Basement - DWG"
..
CADFile "UofM model First Floor - DWG"
ScaleUnits = 0
ScaleValue = 1
OriginX = -2360.29
OriginY = -1622.08
Azimuth = 0
..
CADFile "UofM model Second Floor - DWG"
ScaleUnits = 0
ScaleValue = 1
OriginX = -2360.29
OriginY = -1690.07
Azimuth = 0
..
CADFile "UofM model Basement - DWG"
ScaleUnits = 0
ScaleValue = 1
OriginX = -2350.91
OriginY = -630.331
Azimuth = 0
..
HVACWiz "HVAC System 1"
ScreenIDArrIdx = 0
HeatSource[1] = "Hot Water Coils"
SystemPerWhat[1] = "System per Zone"
..
DXCWWiz "Water-Cooled DX System"
..
WSECWWiz "Wtr-Side Econo System"
..
WLHPWiz "WSHP System"
..
GSHPWiz "GSHP System"
..
PrimWiz "Primary HVAC Plant"
HWScrnIDArrIdx = 0
HWSysLoopFlow = "Variable"
HWSysPumpCtrl = "VSD"
BoilerType[1] = "Steam Boiler (Natural Draft)"
..
DHWWiz "DHW Plant 1"
ScreenIDArrIdx = 0
DHWFuel = "Electricity"
..
FacetColor "By Wall Type"
FacetType = "Walls"
ColorOption = "By Wall Type"
..
FacetColor "By Construction"
FacetType = "Walls"
ColorOption = "By Construction"
..
FacetColor "Uniform"
FacetType = "Windows"
ColorOption = "Uniform"
..
FacetColor "By Glass Type"
FacetType = "Windows"
ColorOption = "By Glass Type"
..
Light3D "Light3D - Default"
Type = "Default"
..
Light3D "Light3D - User1"
Type = "User Defined 1"
..
Light3D "Light3D - User2"
Type = "User Defined 2"
..
Light3D "Light3D - User3"
Type = "User Defined 3"
..
Light3D "Light3D - User4"
Type = "User Defined 4"
..
Light3D "Light3D - User5"
Type = "User Defined 5"
..
ERateWiz "UofM elec"
Version = 1
CustChargeAmt[1] = 0
UniformChargeKW[1] = 0
UniformChargeKWH[1] = 0.085
TOUPeriodsChecked = 1
TOUPeriodErrSeas1 = " "
TOUPeriodErrS1b = " "
..
FRateWiz "Custom Gas Rate"
Version = 1
CustChargeAmt[1] = 10
UniformChargeUse[1] = 0.95
..
END_OF_FILE
More information about the Equest-users
mailing list