[Equest-users] Gross vs. Conditioned Square Footage
David Eldridge
DEldridge at grummanbutkus.com
Fri Aug 22 15:29:40 PDT 2014
If the facility had to be benchmarked in that way, there might be justification to use the midpoint of the walls.
However this facility may not be a great fit for using area at all, if the whole occupied area is the imaging suite.
The client will have a better idea if the facility is area dominated or process donated after they have operated for a few months.
If they figure out that area is appropriate, then there still may not be a useful peer group, so the main issue will be tracking against their own facility over time.
Net or gross in this case is only important if a comparison is made to a similar facility.
Let us know how it turns out. This building could be a useful case study for energy use by a standalone imaging facility.
DSE Mobile
On Aug 22, 2014, at 4:42 PM, "Jim Paulino" <Jim.Paulino at hesm.com<mailto:Jim.Paulino at hesm.com>> wrote:
The definition of conditioned square footage is interesting and I wonder how it would apply to a medical facility that I performed some HVAC commissioning for.
The building housed some sort of MRI or CAT scan type machine that needed some intense shielding. The exterior walls and roof were a minimum of 3 feet reinforced concrete (some of the walls were 5 feet thick!). Additionally, there were interior walls with concrete 2 to 3 feet thick. If you took the net habitable area, it was somewhere in the neighborhood of 60% net.
Jim
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Wednesday, August 13, 2014 9:51 AM
To: David Eldridge; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Gross vs. Conditioned Square Footage
David makes a good point about elevator shafts being conditioned spaces. Per the space definition in 90.1, an indirectly conditioned space is considered conditioned. It doesn’t have to be served by an HVAC system, or heated or cooled. It just needs to be “enclosed” and have greater heat transfer to the interior of the building than to the exterior, based on wall area and U-factor. I generally interpret this as meaning that everything within the building envelope is conditioned space, except crawlspaces, attics and parking garages (per the definition for unconditioned space), and non-heated/cooled spaces along the exterior of the building that have insulated interior walls (like unheated storage and garages). Indirectly conditioned spaces are easy to model in eQUEST. Just define the space/zone as “conditioned” but don’t assign thermostat schedules, and zero out the air flow.
I don’t see an allowance for interior wall thickness in 90.1, so I think that should be included in “total conditioned floor area” as well. There is no definition for floor area, net in 90.1, only floor area, gross.
Regards,
Bill
<image001.jpg>
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
<image002.jpg> <image003.jpg>
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
<image004.png>Sustainability – the forest AND the trees.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Eldridge
Sent: Tuesday, August 12, 2014 7:26 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Gross vs. Conditioned Square Footage
Just to further clarify, you’ll need to explain to the reviewer why SV-A has a larger area than LS-C. You may want to include a corresponding conditioned area total as noted in the architectural plan as supporting documentation – after all, it isn’t really what the area is in model space that is the determinant, it is the actual conditioned area of the proposed design.
Although the LEED reviewers tend to take some flak from time to time, I don’t think they were necessarily off-base to ask you about the area when they saw the larger value in SV-A. If the conditioned area as designed was included in the other credit uploads, you can probably point the reviewer to that document. (Hopefully it is equal/close to 144,475 sf.)
There might be some debate about whether elevator shafts are conditioned or not, as these receive cooling indirectly from the rest of the building, and the area of the elevator cab takes the air directly from the rooms it opens up towards, if not having a small packaged A/C unit mounted on the cab.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Morteza Kasmai
Sent: Tuesday, August 12, 2014 6:04 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Gross vs. Conditioned Square Footage
Bernie,
Following paragraph is from page G-22 of the ASHRAE 90.1-2007 User’s Manual.
“For nonresidential buildings, the baseline system type depends not only on the heating source for the proposed building, but also on the number of floors and the total conditioned floor area of the building.”
Base on the ASHRAE language I think your system selection for the baseline is correct.
Thanks,
Morteza
<image005.jpg>
---------- Forwarded message ----------
From: Bernie Hont <bhont at girard.com<mailto:bhont at girard.com>>
To: "equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>" <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Cc:
Date: Mon, 11 Aug 2014 21:09:54 +0000
Subject: [Equest-users] Gross vs. Conditioned Square Footage
Per 90.1, G3.1.1 the baseline system shall be based on… number of floors, conditioned floor area… etc.
I have a 5 story building with a total gross square footage of ~153,172 square feet. I received a LEED review comment (LEED 2009) that states the baseline system should be system 8 rather than system 6 (as I have modeled). The SVA report indicates the floor area as 153172 square feet, but the LSC report indicates the conditioned area as 144775 square feet for calculations. Supply/return shafts, elevator shafts, etc are excluded from conditioned floor area as well as wall thicknesses. Is the use of system type 6 appropriate since the conditioned floor area is less than 150,000 square feet or, as the comment suggests, should the baseline system be changed to system 8 since the gross area exceeds 150,000 square feet? Changing the system type will substantially impact the savings as the proposed system is a packaged rooftop unit rather than a chilled water plant.
Thanks
<image006.png>
Bernie Hont, PE, LEED AP
Girard Engineering, P.C.
7600 Leesburg Pike
West Suite 310
Falls Church. Virginia 22043
703.442.8787<tel:703.442.8787> (T)
703.734.3946<tel:703.734.3946> (D)
703.356.0169<tel:703.356.0169> (F)
www.girard.com<http://www.girard.com/>
<image007.png><http://www.linkedin.com/in/berniehont>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4816 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1822 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1909 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 4600 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 823 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 37655 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 1038 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140822/63de7eb3/attachment-0002.png>
More information about the Equest-users
mailing list