[Equest-users] How to model a DOAS serving corridors with a Chilled Water Coil
Julien Marrec
julien.marrec at gmail.com
Mon Dec 8 06:57:37 PST 2014
Thanks for your message Nick.
I now have a 2-pipe loop with the SNAP-T, thanks for pointing it out.
David Elridge also wrote that I could just subsitute PSZ for a 2pipe FC.
I've got something working right now that is based on VAVS.
I have read the help file before posting.I understand there are many ways
to skin a cat in eQuest, but I'm still confused what fundamental difference
it would make between using a VAVS or using a 2pipe FC with a dummy zone.
Aside from the fact that the dummy zone setup is easier to implement I
guess... Is there a wrong way to do this? Or just a better way?
Thanks,
Julien
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
<http://www.linkedin.com/in/julienmarrec>
2014-12-08 13:20 GMT+01:00 Nicholas Caton <ncaton at catonenergy.com>:
> Hi Julien,
>
>
>
> I think there are multiple options that could fit the criteria you’ve
> provided, more than one could work depending on circumstances of your
> project…
>
>
>
> *General* advice for “what system should I use” queries follows.
>
> 1. Ask a few questions of the system equipment/design:
>
> - How the actual system is controlled – is it constant volume
> with heating/cooling triggered via one space/duct thermostat only, or
> something more complex?
>
> - Do you have just one central fan or additional fans in each
> zone for independent circulation?
>
> - One set of central heating/cooling coils or are there separate
> reheat / cooling coils occurring at individual zones?
>
> 2. QC your work:
>
> - Answer for yourself how the system’s fans/cooling/heating
> should operate, and when/to what degree ventilation OA is delivered
>
> - After initially setting up your systems/zones (or perhaps the
> first set of many), perform some test runs to QC your efforts
>
> - Verify each intended behavior/output via hourly reporting
>
>
>
> Considering you can generally force 100% OA and constant volume with
> system and/or zonal minimum OA/flow ratio inputs, as appropriate, peruse
> the help file diagrams for systems of interest that include features of
> interest. You probably want to consider/review the articles for FC, VAVS,
> and PIU.
>
>
>
> From your coil description, you may further consider an airside system
> type to leverage a 2-pipe loop set to an outdoor snap temperature (or
> perhaps a seasonal schedule) – see the operation tab under the loop in
> detailed edits.
>
>
>
> Hope that helps get you started!
>
>
>
> ~Nick
>
>
>
> *NICK CATON, P.E.*
> *Owner*
>
>
>
> *Caton Energy Consulting*
> 1150 N. 192nd St., #4-202
>
> Shoreline, WA 98133
> office: 785.410.3317
>
> www.catonenergy.com
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Julien Marrec
> *Sent:* Monday, December 08, 2014 3:29 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] How to model a DOAS serving corridors with a
> Chilled Water Coil
>
>
>
> Hi,
>
> I've got a building with a DOAS (AHU with 100% outside air) serving
> corridors (no reheat, no fan in there, just ventilation grilles). The DOAS
> has one coil, served by hot water in winter and cold water in summer.
>
> There is no economizer, and the supply temperature is simply set by a
> thermostat set as 70°F year round.
>
> I have modeled DOAS before but I was using a PSZ or a PVVT. Those have DX
> cooling coils, so it's not an option.
>
> Seems like I could use MSZ or VAV for example, but I'm not sure which
> would be more appropriate.
>
>
> What type of system do you recommend using in my case?
>
> How would you control it in order to get the proper supply temperature
> (70°F) and avoid simultaneous heating and cooling (Is using an availability
> schedule the only option?)?
>
>
>
>
>
> Also, if you have an .inp snippet I could use to set it up correctly, I'll
> greatly appreciate it!
>
>
>
>
>
> Thanks,
> Julien
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Energy&Sustainability Engineer
> T: +33 6 95 14 42 13
>
> LinkedIn (en) : www.linkedin.com/in/julienmarrec
> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141208/cb35898b/attachment-0001.htm>
More information about the Equest-users
mailing list