One curve ball you need to consider. If you only just put in multiple chillers, all chillers will rise and fall the same, as they will share the load. You need to use Equipment-Quad to fire the chillers in the sequnces you want.
But as far as i know, what ever chillers are running at a particular time share the load.
Make sure this is how your intended operation goes.
John R. Aulbach, PE 

     On Wednesday, December 17, 2014 10:31 AM, "Jones, Christopher" <cjones at halsall.com> wrote:
   

 #yiv7360993904 #yiv7360993904 -- _filtered #yiv7360993904 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv7360993904 {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;} _filtered #yiv7360993904 {panose-1:2 11 5 3 2 1 2 2 2 4;} _filtered #yiv7360993904 {panose-1:2 11 6 3 2 2 2 2 2 4;}#yiv7360993904 #yiv7360993904 p.yiv7360993904MsoNormal, #yiv7360993904 li.yiv7360993904MsoNormal, #yiv7360993904 div.yiv7360993904MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;}#yiv7360993904 a:link, #yiv7360993904 span.yiv7360993904MsoHyperlink {color:blue;text-decoration:underline;}#yiv7360993904 a:visited, #yiv7360993904 span.yiv7360993904MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv7360993904 span.yiv7360993904EmailStyle17 {color:#1F497D;}#yiv7360993904 .yiv7360993904MsoChpDefault {} _filtered #yiv7360993904 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv7360993904 div.yiv7360993904WordSection1 {}#yiv7360993904 Create a new hourly report. Enter a unique name. For Variable Type, select the chiller you are concerned with.       Christopher Jones,P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527    From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of Javed Iqbal
Sent: Wednesday, December 17, 2014 12:52 PM
To: equest-users
Subject: [Equest-users] Chiller hourly profile    Hello,    Is there way to generate chiller hourly profile in eQuest. I am able to get cooling load profile for CHW circulation loop. however, i am specifically looking for individual chiller serving the loads. Any insight would be highly appreciated.    Thanks in advance.    --        Javed Iqbal, LEED AP, CEA Sr. Energy Analyst                 
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141217/da7dc1dc/attachment-0001.htm>


More information about the Equest-users mailing list